Generator Should I change my PTO generator from Bonded Neutral to Floating Neutral?

   / Should I change my PTO generator from Bonded Neutral to Floating Neutral? #41  
Howdy,

Here is a cut and paste from another PTO generator manufacturer
............................
GENERATOR AC NEUTRAL CONNECTIONS

The generator is shipped from the factory with the neutral ungrounded. (Neutral floating, i.e.; no electrical connection between neutral and ground connection).

The required status of the neutral depends on how the PTO generator is to be used. The NEC (National Electrical Code) requires the following.

*Emergency Supply for a Fixed Wiring System -This is the case when the PTO is used to provide emergency backup power for a fixed wiring system. This requires the output of the generator to be connected to electrical load though a double-throw transfer switch. The neutral is NOT to be connected to the ground terminal. This is how the PTO generator is supplied from the factory, no changes are required.

*Separately Derived Source --This is the case when the PTO generator is to supply only loads connected by cords plugged into the outlets or fuel capacity connector. This is the case when the load is not normally supplied by the Utility source or is not part of a fixed wiring system.

The neutral is to be connected to the ground terminal in the control panel.

1. Remove the control panel cover.
2. Locate the #4 AWG wire loop on the ground terminal.
3. Disconnect one end of the wire loop and attach it to the neutral connection terminal.
4. Tighten the retaining nuts on both terminals.
5. Replace the control panel cover and secure the fasteners.

GROUNDING THE GENERATOR

The National Electrical Code requires that the frame and external electrically conductive parts of this generator be properly connected to an approved earth ground. Local electrical codes may also require proper grounding of the unit. For that purpose, a GROUNDING LUG (Figure 13) is provided on the unit. Generally, connecting a No. 6 AWG (American Wire Gauge) stranded copper wire to the grounding lug and to an earth driven copper or brass grounding rod (electrode) provides adequate protection against electrical shock. However, local codes may vary widely. Consult with a local electrician for grounding requirements in your area.

DANGER Do not connect the grounding wire to any pipe that carries flammable or explosive substances fire or an explosion may result.

Proper grounding of the generator will help prevent electrical shock in the event of a ground fault condition in the generator or in connected electrical devices. Proper grounding also helps dissipate static electricity, which often builds up in ungrounded devices.
...............................
The emergency supply for a fixed wiring system is where you want to be. Unless you are hard wiring it in your system. What type of outlet does the PTO generator have?

I use the modular anderson connectors with mine, with all 4 wires in place. Known as a full power plug.
 
   / Should I change my PTO generator from Bonded Neutral to Floating Neutral?
  • Thread Starter
#42  
What type of outlet does the PTO generator have?

The generator has the following outlets: (1) 20A 120V 5-20R / (1) 30A 240V L14-30R Twist Lock / (1) 50A 5-50R Straight, and here is the Generator
Appears to be identical to this one as well and there is a manual for it on that site, but it's been of little help and the companies support hasn't been either.
I'll be using the NEMA 14-50R outlet which provides 50a at 240v with a 4 wire 6ga cord, the output of the cord is a 50a twist lock female plug and the inlet box on the house is a male 50a receptacle.
My generator cord and the run from the inlet box to the breaker will be under 30ft total.

I've installed a 50a double pole breaker in the upper right hand corner of my breaker box, and will be using it with an interlock kit to make sure the main and generator breakers can't be on at the same time.
The electric meter and a ground rod that my breaker box is connected to are within 30ft of where the generator would be operated.
Your thread here is what got me going on the interlock in the breaker panel.

If your attaching yours with an interlock, then your setup is like mine except for the higher current connectors.
How are you running yours, did your leave Neutral and Ground floating, do you attach the generator to a ground rod?
 

Attachments

  • NEMA 14-50R.jpg
    NEMA 14-50R.jpg
    15.5 KB · Views: 585
   / Should I change my PTO generator from Bonded Neutral to Floating Neutral? #43  
If your attaching yours with an interlock, then your setup is like mine except for the higher current connectors.
How are you running yours, did your leave Neutral and Ground floating, do you attach the generator to a ground rod?
Howdy,
I actually am using three different methods. The systems all have the generators using floating neutral. All of my generators methods of connection are all portable. I am tying into a fixed wired system. From my thread here you can see I use a meter panel with interlock, a generac exl6500 attached, then a generlink system with a ETQ 7250 attached with provided cordset. I then have the Tiger Power 30kw, which is connected via the anderson 350amp connectors and 2/0 wire to the transconnect TC-200M26W. This special connection was installed by my utility, and verified all was proper with floating neutral, and all 4 wires connected and grounded. If you look back at my generator-transfer-switch-connection-choices thread, you can see each of the panels. You can click on the pictures and zoom in for better views.

With all the comments here, I would say you are emergency use, fixed wiring system, and the ground is the panel, and you use all 4 wires from generator to interlock breaker. Just verify you do indeed have floating neutral configured.
 
   / Should I change my PTO generator from Bonded Neutral to Floating Neutral? #44  
This is very important because the generator in question has been designed, manufactured, and tested against certain safety standards. The generator can't just be rewired and assumed safe. It's not. It was not intended to operate that way and there may be associated hazards. One obvious hazard is electrocution, as with no system bonding jumper in place, the equipment ground (generator chassis) can become energized. The possible ways this can happen is limited only by one's imagination. Another hazard is that the fault current path is changed. The new connections/configuration should be tested to see if it will carry the fault current that the generator can supply. That and many other tests were conducted before the generator was available as a commercial product.
Many generators DO have as part of their instructions how to bond/unbond the neutral depending on how they are connected and they ARE tested that way.

The correct way to do the installation is to use a three pole transfer switch, if the generator will allow for a solid connection. If it doesn't allow for a solid connection, then there really is no safe way to connect this generator to the premises wiring system. The OP asked what is "for best safety". That's why I'm answering. There are many possible ways to connect the OP's generator to his premises wiring system, but for best safety, follow the NEC.
Have you looked at a small (30ish amp) "emergency transfer switch" recently? How about a "Generlink" (which is usually sold by a utility)? How about a Genrac ATS?

All use a 4 prong plug or 4 solidly connected wires with an unbonded neutral at the generator. In fact (from the generlink site):
http://www.generlink.com/generators_main.cfm said:
NOTE: Per the National Electric Code, all generators must have a "floating neutral " when used with the GenerLink Automatic Transfer Switch. Please refer to the generator operation manual for bonded neutral specifications.
Here is a Generac ATS picture as installed by "Robert Welborne - Master Electrician & State Electrical Inspector": http://www.rrelectriccompany.com/files/100_0654.JPG Note that the neutral is NOT switched and as such the generator has a unbonded neutral and a 4 wire connection to the ATS.

The short of it is:
IF you are using a 3 pole (hot, hot, neutral) transfer switch to disconnect things between the meter and the panel - Bond neutral to ground at the generator and use a 3 wire cord.
IF using a 2 pole transfer switch such as a generlink, an interlock, a/b switch panel, etc - Do NOT bond neutral to ground at the generator and use a 4 wire cord.

Aaron Z
 
   / Should I change my PTO generator from Bonded Neutral to Floating Neutral?
  • Thread Starter
#45  
With all the comments here, I would say you are emergency use, fixed wiring system, and the ground is the panel, and you use all 4 wires from generator to interlock breaker. Just verify you do indeed have floating neutral configured.

There is a ground lug on the receptacle panel of my PTO generator, should I run an additional wire from it to the ground rod at my service entrance?
Seems redundant to me, as one of the four wires in my generator cord is also attached to ground on the generator panel and connects to the bonded Neutral/Ground in the breaker panel then runs to the ground rod.

Are you running a separate ground wire on yours?
 
   / Should I change my PTO generator from Bonded Neutral to Floating Neutral? #46  
There is a ground lug on the receptacle panel of my PTO generator, should I run an additional wire from it to the ground rod at my service entrance?
Seems redundant to me, as one of the four wires in my generator cord is also attached to ground on the generator panel and connects to the bonded Neutral/Ground in the breaker panel then runs to the ground rod.
Are you running a separate ground wire on yours?
If close enough to the existing ground rods, I would use them. If not, I would drive a new one. Either way, I would ground the frame of the generator using the lug you mentioned.

Aaron Z
 
   / Should I change my PTO generator from Bonded Neutral to Floating Neutral? #47  
(Ignoring the issues that come with using a cord/plug instead of hardwired)

Ok, you are using a 4-wire connection between the panel & generator: (2 hots, 1 Neutral, 1 ground). This is good. You do NOT have a seperately derived system when the neutral is unswitched when you wire the neutral of the generator to the neutral of the panel. It is only at the panel where the neutral should be bonded to ground (rod).

The ground wire (green) in your cord should also connect the chasis of the generator to the ground bus in your panel (which is in turn connected to an existing ground rod). Think of this as the protection against the generator's frame developing a dangerous touch voltage. (Actually, it insures that a fault current to the frame will have a low resistant path to ground and therefore develop a fault current large enough to trip a fuse/breaker.) A ground rod at the generator is not required (but wouldn't hurt as long as the nuetral and ground are seperated at the gen.)

The term "floating neutral" is a misnomer, it will be connected to your panel's neutral through the cord, and thus pegged to ~0 volts (ground) by the neutral connection to ground at your panel. This insures that the 240V from the gen is divided into 2-120V circuits (and not 80V and 140 volts, for example, if the neutral was unconnected to anything (i.e. truely "floating")). (One can see that if the neutral was switched we would then need a connection of the generator's neutral to ground (rod) at the gen.)

What's important is: The neutral (white) and the chasis ground (green) should not be connected together, by any means, at the generator. System-wide, they should only be connected at one place (in your existing panel). Otherwise, you would have normal neutral current also running on the parallel chasis ground conductor (green). As per Ohm's Law, a current through this conductor (with some resistance) will cause a voltage to develop across that resistance, and the generator's chasis connected to this ground conductor with neutral current running through it would see that voltage above ground (O volts); that could be shocking if you then touch it.

(Caution if you ever use this generator (with it's non-fixed, quick detachable cords/plugs) to power something else, where the neutral & ground aren't bonded as they are in your panel, (and you have a seperately derived system), you may not trip off on a ground fault.)
 
   / Should I change my PTO generator from Bonded Neutral to Floating Neutral? #48  
OK ... not to confuse the discussion, but I have an additional question.

It has been stated that the Ground and Neutral should be un-bonded at the Generator but that they are bonded in the panel box.

Well, on my home we have a panel at the power pole where the neutral and ground are bonded. Then, due to distance from the pole to the house, we were required to have a panel just outside the house. This panel has un-bonded neutral. Then, there is the panel in the house that also has the neutral nu-bonded.

If I connect a generator to the panel outside the house, not the one that is further away at the pole, should the neutral of the generator be bonded or not since the neutral in the panel is un-bonded?
 
   / Should I change my PTO generator from Bonded Neutral to Floating Neutral? #49  
I hang my head and try to say this again for all to listen or ignore (Jpc gets it ) If you disconect the neutral to ground jumper on the jenny.... You loose the ground conductor from the genny to the house during a fault. It think it must be one of those abstract principles that somehow boggles smart minds. Draw it on paper.... The portable genny has a 240v secondary, with a center tap. Those three outputs only want to flow to each other- not to derived gnd. If a 120v whatever, in your house shorts to gnd, it's only motive force is back to the center tap of your genny if you remove the bond. This renders the ground conductor of your patch cable dead weight, it's only motive is back on the neutral conductor.
 
   / Should I change my PTO generator from Bonded Neutral to Floating Neutral? #50  
I hang my head and try to say this again for all to listen or ignore (Jpc gets it ) If you disconect the neutral to ground jumper on the jenny.... You loose the ground conductor from the genny to the house during a fault. QUOTE]

I don't think that is so, the neutral (aka "grounded conductor) and the (equipment) grounding conductor are bonded at the house panel, the fault current will re-enter the neutral back to the jenny's winding here.
 
 

Tractor & Equipment Auctions

2023 FOREST RIVER CONTINENTAL CARGO AUTO MASTER 44 FT TRAILER. (A47001)
2023 FOREST RIVER...
Case Cable Plow (A47809)
Case Cable Plow...
Tong De-Stoner Bucket Stand (A47369)
Tong De-Stoner...
132917 (A44391)
132917 (A44391)
2014 AMERITRAIL, INC. TUGGER TRAILER (A47001)
2014 AMERITRAIL...
1973 Timpte 40-Foot Hopper Bottom Grain Trailer - Leaf Spring Suspension and Well-Maintained Tarp (A46884)
1973 Timpte...
 
Top