buickanddeere
Super Member
If the motor was 100% efficient and had a PF of 1. It would make 4.83HP with 15 amp and 240V. Probably running at approx 70% so 9.3amp would be doing work , 4 amps wasted as heat and 1.7 more amps of reactive power.
That makes sense to me, but I seem to recall numerous discussions about this not being acceptable in the NEC. Also in many discussions about proper grounding of generators. Can anyone elaborate?
This is what I intend on doing:
1. Pull the 220 out of the outlet it resides in now and terminate it into a sub panel box. Assuming I can do that with a three wire set up
2. Install a 50 amp and a 30 amp double throw breakers
3. Wire a new line from the 50 amp to the existing outlet - change outlet to proper 220v outlet
4. Replace welder plug to a matching 220 plug that mates with the new 220 outlet
5. Wire 12 ga from 30 amp breaker to new to me compressor.
Sound good?
This is what I intend on doing:
5. Wire 12 ga from 30 amp breaker to new to me compressor.
Sound good?
You need four (4) wires going to a 220 plug in.
This is what I intend on doing:
1. Pull the 220 out of the outlet it resides in now and terminate it into a sub panel box. Assuming I can do that with a three wire set up
2. Install a 50 amp and a 30 amp double throw breakers
3. Wire a new line from the 50 amp to the existing outlet - change outlet to proper 220v outlet
4. Replace welder plug to a matching 220 plug that mates with the new 220 outlet
5. Wire 10 ga from 30 amp breaker to new to me compressor.
Sound good?
You can't do this if the wire is part of the building. The breaker is there to protect the wire from overheating. With a 30 amp breaker you will need 10 ga wire. Someone may plug a 30 amp load in and overheat the 12 ga wire, causing a fire.