MikeA57
Silver Member
You can never have too much Monkey ***!!!!
(Least, that's what we called it!)
(Least, that's what we called it!)
Came across this thread as I am preparing to build a home and need to get power back to my site which is about 800' back. The power company said I am responsible for the trench and conduit (4" Sched 40 with a 36" radius to 90 degree at each end) and they will pull the wire.
I have not yet asked them this question, but when I assemble the conduit, I assume I have to feed some type of rope or something in it so that they can pull, but what can I use that would stand up to an 800' pull of 200amp service wire?
Should I bury the conduit in spots so that is does not move while they are pulling?
Any advice would be appreciated.




I wonder if it would work to use a deep-sea fishing reel as a source for blowing in a line to get the pull rope?
BOB
Hi
Ideal Yellow 77 wire pulling lube is the best way to make pulling wire easy.
Charlie.
Depending on the length of the run, PVC glued together BEFORE it is put in the ditch will "bow" far more then you would think - even 2" pipe will "curve" so you do not need to use 90's unless you need to turn in a short distance. When you do need a sharper turn, use a "long sweep" when you can or heat the PVC and bend the sweep yourself.
Also, if you can get it, and you are using PVC, use pipe with bells. It will cut down on the number of couplings you need and you would want to install them in the direction you plan to pull.
exactly, why use soap or talc when you can get something engineered to be friendly to the wire jacket is available and not expensive. In a pinch yes maybe you reach for the dawn dish soap but a quart of Ideal Yellow 77 wire pulling lube is like 6 or 7 bucks. I have never tried threading wire or cable through individual pieces of conduit before gluing them together but I don't think I would even consider it for more than two sections, its just not worth the risk of the glue attacking the cable jacket or wire insulation to me.
I would highly recommend against pulling wire with any kind of winch or motorized device unless it has the proper gauges for determining pull. A commercial wire puller has an amp meter which determines how much pull is being exerted.
If the pull exceeds the wire's strength it will stretch. What occurs is that a 10ga wire might be stretched at some point into a 14ga wire. This is a recipe for future failure.
When I catch a contractor doing this on my projects, I make them megger the line and many times it fails and they end up replacing the wire at their expense.
Think about a bungee and as you pull it it gets smaller in diameter but longer.
How does an amp meter determine that your pulling #10 wire or 500 mcm ??? And another thought,, a megger is only used to check the value of the insulation on the wire not that the copper wire itself is deformed ???