Grounding Rod For Portable Generators Necessary?

   / Grounding Rod For Portable Generators Necessary? #81  
This discussion seems to have slowed down, but I hope someone else can comment on the above quote. I am currently looking into welders for running with a generator. The comment above has me curious about whether inverter welders need grounding rods connected to generators more than non inverter based welders...

It has been a while since I have seen equipment with a parasitic filter which is implemented with a capacitor linking an internal power source with a ground. This type of equipment can cause the chassis to have some voltage, depending on the exact voltage wave of the incoming voltage. The purpose of this type of filter is to filter out any transient spikes from the power source, and it requires the metal chassis (which can be touched by a human) to be attached to a physical ground.

So as long as the generator is well behaved (and I would look for one with a sine wave output or simulated sine wave), it should be fine. If it is one of the cheap ones, which can generate a bunch of noise (voltage spikes) from the dirty brushes, burned commutators, and a malfunctioning governor, it is best to ground it *if* you are plugging in equipment that needs a real ground to keep from possibly shocking you. This equipment could include power tools with a metal case or electronic gear.

A sine wave (like the power company supplies your house) looks like the black line in http://www.marine-deals.co.nz/images/inverter_sinewave.gif
The red square wave exaggerates what a stepped square wave looks like, but shows the difference in the type of what is generated. Better generators either generate a sine wave, or a stepped square wave with lots of steps. Typically, equipment can't tell the difference, but some more sensitive equipment can, and some can even be damaged.

Almost all "standard" generators under 10 kw certainly and quite possibly most under 25 kw are inherently "noisy" in the electrical sense and most of them simply do not have the rotational mass to ensure close frequency control OR close voltage control. On the other hand, generators which contain inverters have crystal-controlled frequency and will indeed hold the frequency within 1/2 Hz. from no load to full load. The voltage regulation is far tighter than "standard" generators at about 1% from no load to full load. In addition, it is the elimination of the transients that are common with non-inverter generators where the name brand inverter generators have the leg up.

Hope that helps.
 
   / Grounding Rod For Portable Generators Necessary? #82  
I hope you take these slight disagreements as constructive and not offensive, as nothing is meant. But there are some thoughts for discussion here.

It has been a while since I have seen equipment with a parasitic filter which is implemented with a capacitor linking an internal power source with a ground. This type of equipment can cause the chassis to have some voltage, depending on the exact voltage wave of the incoming voltage. The purpose of this type of filter is to filter out any transient spikes from the power source, and it requires the metal chassis (which can be touched by a human) to be attached to a physical ground.

Two things to think about here:

1. Assuming you mean "physical ground" to mean ground rods, since power goes back to its source, this doesn't quite make sense... it would just return via the ground wire to the generator head.

2. If this concept were in practice, and if there was enough voltage and current available on the device chassis and thus the ground wire to injure or kill someone, none of these devices would work on GFCIs, since that would be a ground fault! All my computers, power tools, etc. work fine on GFCI receptacles. If it were not enough to trip the GFCI, it would not be enough for a person to be at risk. It would also likely not pass UL standards.

A sine wave (like the power company supplies your house) looks like the black line in http://www.marine-deals.co.nz/images/inverter_sinewave.gif
The red square wave exaggerates what a stepped square wave looks like, but shows the difference in the type of what is generated. Better generators either generate a sine wave, or a stepped square wave with lots of steps. Typically, equipment can't tell the difference, but some more sensitive equipment can, and some can even be damaged.

All mechanical generators produce a regular, true sine wave like the power company supplies and the black line. This is because AC power has a sine wave because that is how power is mechanically produced from an alternator - it's the natural output. Versus an inverter which has to make it using solid state components. The only thing that produces modified/square waves are less expensive inverters. More rotational mass and larger generators mean better response to sudden load increases, however, which will decrease low voltage situations when large loads are suddenly applied. Surge ratings are just as important as running ratings when warranted.

Realize small inverter generators like the Honda EU-series may not have a neutral/ground bond. The Hondas to my knowledge DO have a main GFCI breaker.

Once you add plain inverters to the mix, you run into more interesting issues, such as many cheap inverters producing 120v by having the neutral leg at +/- 60v, and the hot leg at +/- 60v, so the neutral has potential!

EDIT: The EU-series do not appear to have GFCIs.
 
   / Grounding Rod For Portable Generators Necessary? #83  
My Gen-Set is a Generac 17.5 KW. It runs power tools and my 50A input rectifier AC/DC welder just fine w/o a ground rod. I tried the ground rod deal and checked the potential from the N and G conductors and 0 volts, same from the gen frame. When connected to the house circuits it is bonded through N and G cord conductors to the house neutral and grounding systems. I have had no problems running all my electronics including the computers and various solid state appliances and power supplies, probably 50 HRs in the last 2 years. I have not had a GFCI trip on anything for a long time, but I test them once a year along with fire alarms and all that stuff you need to do on a schedule. I will leave all the theory to others and believe in the proof in the pudding I have experienced. Yes, I do know the codes also, both NEC and OSHA; no grounding of portables and only one grounding system for house connections.

Ron
 
   / Grounding Rod For Portable Generators Necessary? #84  
As I said, its main purpose is lightning/static dissipation... check out HiV's post above. If that was true, then why does a 100 amp service have a different size grounding electrode conductor than a 400 amp service?

The NEC requires a maximum resistance to ensure that the ground rod can participate in that fashion effectively, or two rounds must be driven if you cannot test.



The grounding rods serve no purpose there. They will not flow enough current to trip a regular breaker as they have a very high resistance compared to a "good conductor".

Where a metal item becomes insulated, the EGC connected to the metal case should allow the fault current to flow back to the main panel, meter can, or wherever neutral/ground are bonded. When this happens, the short travels over the EGC, the breaker trips and everything is fine. The ground from the ground bar to the ground rod, and ground rod itself, are not used for clearing the fault and unnecessary for that particular purpose. True! ...but, if not for the ground rod how would we get 2-120V phases from a 240V service? Also, when that short occurs and there is no ground rod, only a bonded "EGC" and the "floating" neutral like you talk about, if you are touching the metal, it's hard to say what voltage (and current) you will experience. Actually, if you can limit the coupling capacitance between the source and earth , it may be safe to touch it, as there will be no ground fault current using your body and earth as a path, although I wouldn't recommend it. I believe some European systems are ungrounded. Often in an industrial setting, on an ungrounded (delta) or high resistance grounded system this type of system is purposely installed so that the system can continue to run if 1 phase becomes accidently "grounded".


GFCIs are used to better protect people from wet circumstances or ground faults. Despite the name "ground fault", a GFCI does not use the grounding rods and need not have a grounding wire to function... in fact, they are the accepted way for replacing a 2-wire ungrounded outlet when no ground wire is present and its not feasible to get one there.

*****
 
   / Grounding Rod For Portable Generators Necessary? #85  
If that was true, then why does a 100 amp service have a different size grounding electrode conductor than a 400 amp service?

Dunno, code and science are closely related but different. I'm guessing the assumption is a larger service would service a larger potential area. I'm not an electrician, one could probably explain better the reason for the code. Check Mike Holt's forums.

if not for the ground rod how would we get 2-120V phases from a 240V service?

Single phase 240V in the United States is brought in using two 120V hots (180 degrees apart) and one neutral (0V). The difference between those two hots is 240V RMS. Ground has nothing to do with whether 240v is available unless you're on a VERY archaic single wire service, used only in incredibly rural areas.

Also, when that short occurs and there is no ground rod, only a bonded "EGC" and the "floating" neutral like you talk about, if you are touching the metal, it's hard to say what voltage (and current) you will experience.

Neutral does not float, it's 0v potential. If 120v electrifies something metal, the purpose of the EGC is it completes a circuit to neutral, creating a short. Once you have a short, the breaker servicing that circuit blows.
 
   / Grounding Rod For Portable Generators Necessary? #86  
Dunno, code and science are closely related but different. I'm guessing the assumption is a larger service would service a larger potential area. I'm not an electrician, one could probably explain better the reason for the code. Check Mike Holt's forums.



Single phase 240V in the United States is brought in using two 120V hots (180 degrees apart) and one neutral (0V). The difference between those two hots is 240V RMS. Ground has nothing to do with whether 240v is available unless you're on a VERY archaic single wire service, used only in incredibly rural areas.
That's true but backwards (IMO). A single phase 240V is the output of one (1) utility transformer's secondary coil. The 2 legs of 120V are obtained by grounding (pegging to 0 Volts) the center (tap) of the transformer coil. Perhaps we are talking about the same thing, tomato/tomata, but the difference is the 120V is derived by splitting the 240V output of the transformer, rather than constructing 240V from (2) 120V sources like you state. Again, this may be tomato-tomata


Neutral does not float, it's 0v potential. If 120v electrifies something metal, the purpose of the EGC is it completes a circuit to neutral, creating a short. Once you have a short, the breaker servicing that circuit blows.
Unless there is a ground rod bonded to the neutral, the neutral will float and is NOT 0 volts with respect to a person (on the ground) touching it. If neutrals are not grounded (pegged to 0 volts) as you originally spoke about, now your (2) "120V" legs may be not be split 120V/120V , but the voltage split (totaling 240V) will be a function of the load (resistance) in each leg (e.g. L1=160V/L2=80V, etc..)
 
   / Grounding Rod For Portable Generators Necessary? #87  
Neutral does not float, it's 0v potential. If 120v electrifies something metal, the purpose of the EGC is it completes a circuit to neutral, creating a short. Once you have a short, the breaker servicing that circuit blows.

Not true. V = IR. The current in the neutral wire (I) is greater than zero, and the resistance of the neutral wire (R) is greater than zero, therefore voltage (V) must be greater than zero.

In addition, neutral is the middle of what could be an unbalanced load, so it can contain some voltage potential due to the unbalanced load. Since it is the return leg of 120 volt loads, and if many of those loads are on one of the 120v leg and not the other, it can have additional voltage.
 
   / Grounding Rod For Portable Generators Necessary? #88  
Not true. V = IR. The current in the neutral wire (I) is greater than zero, and the resistance of the neutral wire (R) is greater than zero, therefore voltage (V) must be greater than zero.

In addition, neutral is the middle of what could be an unbalanced load, so it can contain some voltage potential due to the unbalanced load. Since it is the return leg of 120 volt loads, and if many of those loads are on one of the 120v leg and not the other, it can have additional voltage.

Huh? It wouldn't be 120v if the neutral was not 0v. Voltage is the potential difference between two points. 120v - 0v = 120v. (And, irrelevant but, the resistance of the neutral wire is nearly 0, or it would be a poor conductor and a better space heater :))

EGC and neutral are directly connected and you usually use the EGC to measure the voltage on the neutral, so of course the potential between the two (being connected) is 0v.

Say you have 120v, and the neutral is at 20v as you propose. The voltage you would measure would then be 100v. This comes in handy when you have multiple voltages and need something "in the middle" - for example, a computer fan. Connect one half of the fan to +12v and the black negative wire to +5v, and the fan sees +7v and operates happily.

("Neutral does not float" as I put it is in the discussion of a discrete system/circuit)
 
   / Grounding Rod For Portable Generators Necessary? #89  
It's amazing how a resurrected thread can take on a new life. All this theory stuff gives me a headache like it did when I first was exposed to it. The majority of our readers could care less as long as they do get a tingle when they touch metal. I at least can measure it with my volt meter.

Ron
 
   / Grounding Rod For Portable Generators Necessary? #90  
Dunno, code and science are closely related but different. I'm guessing the assumption is a larger service would service a larger potential area. I'm not an electrician, one could probably explain better the reason for the code. Check Mike Holt's forums.



Single phase 240V in the United States is brought in using two 120V hots (180 degrees apart) and one neutral (0V). The difference between those two hots is 240V RMS. Ground has nothing to do with whether 240v is available unless you're on a VERY archaic single wire service, used only in incredibly rural areas.



Neutral does not float, it's 0v potential. If 120v electrifies something metal, the purpose of the EGC is it completes a circuit to neutral, creating a short. Once you have a short, the breaker servicing that circuit blows.

You're right, and your wrong. A house is fed 240 volts single phase, center tapped. No need to confuse yourself, or others here with the notion of "2 120 volt feeds 180 degrees apart". "
Neutral is derived from ground which comes from the center tap of the pole transformer. It's potential is midway between the 240V legs.
 
   / Grounding Rod For Portable Generators Necessary? #91  
Theoretically, if there was no resistance in the wire and all connections were perfect, neutral would be at zero across it's entire length from the pole to the end of all branch circuits. But it's not. There is resistance in wires that can be hundreds of feet long, and there are connections that aren't perfect. So voltage measured at different points in a neutral circuit will be different. Do you understand that?

How neutrals can have voltage, as opposed to being at the same electrical potential as the earth, is that there are various 120 volt loads on each portion of the 240 volt center tapped supply. So if one is highly loaded, and the other lightly loaded, there will be some voltage measurable on the neutral. It's basic ohms law.

And derived neutrals can certainly float, it depends on how they are derived. It was commonly done by putting two electrolytic capacitors across the 120v to the chassis in earlier transistor amplifier design, and commonly done with vacuum tube amps.

I'm done, this is not the discussion that the poster asked for.
 
   / Grounding Rod For Portable Generators Necessary? #92  
you know, im an electrician and even im sick of this thread
 
   / Grounding Rod For Portable Generators Necessary? #93  
you know, im an electrician and even im sick of this thread

Ok. I agree. But the original question was " do I need a ground rod?". The answer is no. You don't need a ground rod. NFPA 70 article 250.34


A generator is a "separately derived system". BUT - 250.20 (D) FPN says - an alternate ac power source such as an on site generator is NOT a separately derived system if the neutral is solidly interconnected to a service supplied system neutral.

Do we drive a ground rod if we install a generator outside? **** yes. A 400 kw generator in a steel soundproof enclosure has a good chance of getting hit by lightning. We BOND the rod to the metal frame of the genset. 99% of the time that's what the engineer wants.

Here are a few definitions for reference..
Ground- 1. the earth.
2. A conducting connection, whether intentional or accidental, between an electrical circuit or equipment and the earth or to some conducting body that serves in place of the earth.

Grounded conductor - a system or circuit conductor that is intentionally grounded. ( typically called the neutral).

Grounding conductor- a conductor used to connect equipment or the grounded circuit of a wiring system to a grounding electrode or electrodes.

Grounding electrode conductor - the conductor used to connect the grounding electrode(s) to the equipment grounding conductor, to the grounded conductor, or to both, at the service, or at the source of a separately derived system.

A ground rod, ground ring, 2' square plate, metal underground water pipe, is a grounding electrode. Typically you need 2 grounding electrodes at a service ie: ground rod and cold water pipe, 2 ground rods 6' apart.
Resistance of a ground should be 25 ohms or less.

The grounded conductor and grounding electrode are bonded Together at the service.

The bonding of the two makes a system.
The grounding electrode system does 2 things,
1. Provides a path for lightning discharge ( not that it won't destroy stuff in its path)
2. Provides a reference to ground for the service in a fault situation.
scenario1. John lives on a block with 10 other houses. John lives closest to the transformer. The scrapper that roams johns street decides he wants the ground wire that runs from the transformer to the ground rod at the bottom of the pole. The grid ground isn't such a great connection, so John's transformer outside his front window is not happy. The transformer now finds the next path to ground, which is johns service. It sees johns ground rod and cold water pipe ground and is happy. If not for johns grounding electrode system, the transformer would have looked for the next available ground. Maybe ms. Jones house down the street. If it didn't have a ground to love, the scenario of a "floating neutral can happen".

Scenario 2. Johns house loses his grounded conductor. His house is ok hopefully because his grounding electrode system is keeping a floating neutral in check.

In electronics static discharge and isolated grounds come into play, but that's a whole different thread. Lol

My god I had to whip out the code book for this. It was a good brush up.
 
   / Grounding Rod For Portable Generators Necessary? #94  
Ok. I agree. But the original question was " do I need a ground rod?". The answer is no. You don't need a ground rod. NFPA 70 article 250.34


A generator is a "separately derived system". BUT - 250.20 (D) FPN says - an alternate ac power source such as an on site generator is NOT a separately derived system if the neutral is solidly interconnected to a service supplied system neutral.

Do we drive a ground rod if we install a generator outside? **** yes. A 400 kw generator in a steel soundproof enclosure has a good chance of getting hit by lightning. We BOND the rod to the metal frame of the genset. 99% of the time that's what the engineer wants.

Here are a few definitions for reference..
Ground- 1. the earth.
2. A conducting connection, whether intentional or accidental, between an electrical circuit or equipment and the earth or to some conducting body that serves in place of the earth.

Grounded conductor - a system or circuit conductor that is intentionally grounded. ( typically called the neutral).

Grounding conductor- a conductor used to connect equipment or the grounded circuit of a wiring system to a grounding electrode or electrodes.

Grounding electrode conductor - the conductor used to connect the grounding electrode(s) to the equipment grounding conductor, to the grounded conductor, or to both, at the service, or at the source of a separately derived system.

A ground rod, ground ring, 2' square plate, metal underground water pipe, is a grounding electrode. Typically you need 2 grounding electrodes at a service ie: ground rod and cold water pipe, 2 ground rods 6' apart.
Resistance of a ground should be 25 ohms or less.

The grounded conductor and grounding electrode are bonded Together at the service.

The bonding of the two makes a system.
The grounding electrode system does 2 things,
1. Provides a path for lightning discharge ( not that it won't destroy stuff in its path)
2. Provides a reference to ground for the service in a fault situation.
scenario1. John lives on a block with 10 other houses. John lives closest to the transformer. The scrapper that roams johns street decides he wants the ground wire that runs from the transformer to the ground rod at the bottom of the pole. The grid ground isn't such a great connection, so John's transformer outside his front window is not happy. The transformer now finds the next path to ground, which is johns service. It sees johns ground rod and cold water pipe ground and is happy. If not for johns grounding electrode system, the transformer would have looked for the next available ground. Maybe ms. Jones house down the street. If it didn't have a ground to love, the scenario of a "floating neutral can happen".

Scenario 2. Johns house loses his grounded conductor. His house is ok hopefully because his grounding electrode system is keeping a floating neutral in check.

In electronics static discharge and isolated grounds come into play, but that's a whole different thread. Lol

My god I had to whip out the code book for this. It was a good brush up.

i told him no 8 pages ago with the code requirements.
 
   / Grounding Rod For Portable Generators Necessary? #95  
Ok. I agree. But the original question was " do I need a ground rod?". The answer is no. You don't need a ground rod. NFPA 70 article 250.34


A generator is a "separately derived system". BUT - 250.20 (D) FPN says - an alternate ac power source such as an on site generator is NOT a separately derived system if the neutral is solidly interconnected to a service supplied system neutral.

Do we drive a ground rod if we install a generator outside? **** yes. A 400 kw generator in a steel soundproof enclosure has a good chance of getting hit by lightning. We BOND the rod to the metal frame of the genset. 99% of the time that's what the engineer wants.

Here are a few definitions for reference..
Ground- 1. the earth.
2. A conducting connection, whether intentional or accidental, between an electrical circuit or equipment and the earth or to some conducting body that serves in place of the earth.

Grounded conductor - a system or circuit conductor that is intentionally grounded. ( typically called the neutral).

Grounding conductor- a conductor used to connect equipment or the grounded circuit of a wiring system to a grounding electrode or electrodes.

Grounding electrode conductor - the conductor used to connect the grounding electrode(s) to the equipment grounding conductor, to the grounded conductor, or to both, at the service, or at the source of a separately derived system.

A ground rod, ground ring, 2' square plate, metal underground water pipe, is a grounding electrode. Typically you need 2 grounding electrodes at a service ie: ground rod and cold water pipe, 2 ground rods 6' apart.
Resistance of a ground should be 25 ohms or less.

The grounded conductor and grounding electrode are bonded Together at the service.

The bonding of the two makes a system.
The grounding electrode system does 2 things,
1. Provides a path for lightning discharge ( not that it won't destroy stuff in its path)
2. Provides a reference to ground for the service in a fault situation.
scenario1. John lives on a block with 10 other houses. John lives closest to the transformer. The scrapper that roams johns street decides he wants the ground wire that runs from the transformer to the ground rod at the bottom of the pole. The grid ground isn't such a great connection, so John's transformer outside his front window is not happy. The transformer now finds the next path to ground, which is johns service. It sees johns ground rod and cold water pipe ground and is happy. If not for johns grounding electrode system, the transformer would have looked for the next available ground. Maybe ms. Jones house down the street. If it didn't have a ground to love, the scenario of a "floating neutral can happen".

Scenario 2. Johns house loses his grounded conductor. His house is ok hopefully because his grounding electrode system is keeping a floating neutral in check.

In electronics static discharge and isolated grounds come into play, but that's a whole different thread. Lol

My god I had to whip out the code book for this. It was a good brush up.

i told him no 8 pages ago (post 27) back in 2011 i believe. code hasnt changed.
 
   / Grounding Rod For Portable Generators Necessary? #96  
I'm done, this is not the discussion that the poster asked for.

Regarding carrying on a conversation about something related after the poster has been given an answer, repeat after me: "It's Ok. It's Ok. It's Ok".

Hivoltage98: Any idea why a 400 amp service requires a bigger grounding electrode conductor to the ground rod then say a 100amp service, when as per code, you shouldn't rely on the earth as a ground path conductor? (And the purpose of the EGC (equipment ground conductor) that you run with circuits is to get fault current back to it's source (transformer or gen) so the breaker will trip, not to get fault current into the ground.)
 
   / Grounding Rod For Portable Generators Necessary? #97  
ok..im gone from this post...later all
 
   / Grounding Rod For Portable Generators Necessary? #98  
Regarding carrying on a conversation about something related after the poster has been given an answer, repeat after me: "It's Ok. It's Ok. It's Ok".

Hivoltage98: Any idea why a 400 amp service requires a bigger grounding electrode conductor to the ground rod then say a 100amp service, when as per code, you shouldn't rely on the earth as a ground path conductor? (And the purpose of the EGC (equipment ground conductor) that you run with circuits is to get fault current back to it's source (transformer or gen) so the breaker will trip, not to get fault current into the ground.)

1.The conductor is larger because the wire is sized according to the size of the service. If a fault would occur, the conductor needs to be sized for the maximum fault current.
2. The code never says not to trust the earth as a ground path conductor. If you drive a ground rod, you should always check that it has a reference to ground. Ou also need a second ground, ie.. Cold water pipe.
3. The fault current needs to go back to the grounded conductor. Remember it's a system. The grounded conductor is the return path for current. The grounding electrode is strictly for fault current. It's a safety wire.
 
   / Grounding Rod For Portable Generators Necessary? #100  

Tractor & Equipment Auctions

CASE 610 Sprayer System 2000 Gallons (A61307)
CASE 610 Sprayer...
2016 John Deere 35G Mini Excavator (A55973)
2016 John Deere...
Ratchet Straps (A59230)
Ratchet Straps...
2017 Autocar Xpeditor T/A Heil V-161 Front Loader Garbage Truck (A59230)
2017 Autocar...
2439 (A60432)
2439 (A60432)
20FT X 30FT STEEL CARPORT (A58214)
20FT X 30FT STEEL...
 
Top