Grounding Rod For Portable Generators Necessary?

   / Grounding Rod For Portable Generators Necessary? #111  
Exactly right!
...so why does the grounding electrode conductor connecting the neutral to the grounding electrode system of a 400 amp service have to be a different size than a 100 amp service? (i.e. is there any logical reason?)

Ground faults can occur anywhere in the system, so the grounding electrode conductor has to be sized to carry the fault current back to the main bonding jumper wherever the fault occurs so the overcurrent device will trip.
You will find that the code does not require a grounding electrode conductor larger than 6AWG to ever be connected to a ground rod, regardless of the size of service. This is because it is understood that the #6 wire will be able to carry all the current that a ground rod is capable of disapating. This only applies to driven electrodes, not the Ufer ground, or the water main, etc.
The SOARS book on grounding is considered the authority on grounding.
 
   / Grounding Rod For Portable Generators Necessary? #112  
Ground faults can occur anywhere in the system, so the grounding electrode conductor has to be sized to carry the fault current back to the main bonding jumper wherever the fault occurs so the overcurrent device will trip. You mean the equipment grounding conductor (EGC) (i.e. the green wire) you run with the circuit has to be sized to carry the fault current back to the main bonding jumper (usually at the service panel)
You will find that the code does not require a grounding electrode conductor (GEC) larger than 6AWG to ever be connected to a ground rod, regardless of the size of service. Maybe not to a single round rod, but from the bonded neutral/ground bus to the ground electrode system it's sized based on NEC table 250.66 This is because it is understood that the #6 wire will be able to carry all the current that a ground rod is capable of disapating. This only applies to driven electrodes, not the Ufer ground, or the water main, etc.
The SOARS book on grounding is considered the authority on grounding.
06cfitgerald_tb1_894040155.jpg

IMO, this is no logical reason, or I haven't figured it out anyways. Other than if you have a fault, AND your EGC (green wire) is compromised, so you are now relying on earth (or perhaps a better electrode system (e.g. building steel, ground ring, etc..)) as your fault path. It's a bit counter-intuitive, but the fault current would be flowing from the "ground" to the panel (panel's neutral). Whereas I think most people envision current flowing to ground.
 
Last edited:
   / Grounding Rod For Portable Generators Necessary? #113  
View attachment 364774

IMO, this is no logical reason, or I haven't figured it out anyways. Other than if you have a fault, AND your EGC (green wire) is compromised, so you are now relying on earth (or perhaps a better electrode system (e.g. building steel, ground ring, etc..)) as your fault path. It's a bit counter-intuitive, but the fault current would be flowing from the "ground" to the panel (panel's neutral). Whereas I think most people envision current flowing to ground.

All the building steel, piping systems, and other grounding systems are bonded together to the grounding electrode conductor. The grounding electrode conductor sees fault current all of the time. Imagine a conductor faulting to an interior water pipe...the fault current would travel back to the main bonding jumper, then to the neutral via the grounding electrode conductor.
If YOU were to write the code, how would you size the grounding elctrode conductor?
 
   / Grounding Rod For Portable Generators Necessary? #115  
You answered your own question. If you lose the neutral, 1. Your electrical system becomes a series circuit. 2. The grounding electrode system picks up where your neutral failed and clears the fault current.

That's not right, at all.
A grounding electrode does not specifically "clear fault current" during a failed neutral conductor failure.
That's not the purpose, or the reality, of a ground electrode.

If your saying I'm wrong, then post the right answer

I don't like typing a lot, The way you worded your impression of a ground system makes it hard for me to correct what you wrote without a lot of typing. I'll try to use examples to make it easier for both of us.

Ground circuits don't "clears the fault current". Thats kind of circular logic. If there's current on a ground wire, then you are having a fault.
Ground wires don't "picks up" where a neutral failed. That would require a parallel circuit and would result in current on the ground circuit all the time= wrong.
Example: Go disconnect the white wire from a house circuit ( failed neutral )- anywhere in the house, even the pole feed. Does the ground keep the current flowing?
Example: with neutral wire cut doesn't the device stop operating? What current would you be "clearing"?
 
   / Grounding Rod For Portable Generators Necessary? #116  
Ground circuits don't "clears the fault current".

Kinda.

Ground rods do not, where this discussion began.

"Ground circuits" is not really a standardized term, but the EGC (bottom/green/ground wire on a 3-wire outlet) IS for clearing fault current. If an internal short should energize a metal appliance case, power tool case that's steel (no longer in use really), etc... the ground wire (EGC) provides a path back to the point where the ground and neutral busses are bonded. This creates a short and should cause the breaker to blow.

Despite being connected, current does not flow through the ground rod of course, but gets back to the neutral as fast as it can - via the neutral/ground bonding between the two bus strips or wherever it is connected. (Sometimes it's in the meter can)
 
   / Grounding Rod For Portable Generators Necessary? #117  
Kinda.

Ground rods do not, where this discussion began.

"Ground circuits" is not really a standardized term, but the EGC (bottom/green/ground wire on a 3-wire outlet) IS for clearing fault current. If an internal short should energize a metal appliance case, power tool case that's steel (no longer in use really), etc... the ground wire (EGC) provides a path back to the point where the ground and neutral busses are bonded. This creates a short and should cause the breaker to blow.

Despite being connected, current does not flow through the ground rod of course, but gets back to the neutral as fast as it can - via the neutral/ground bonding between the two bus strips or wherever it is connected. (Sometimes it's in the meter can)

Give me a break. If your gonna try to get some satisfaction trying to debate 1 tiny fact out of my entire post, at least have the facts to back it up. Using an example "no longer in use" is a piss poor example.
 
   / Grounding Rod For Portable Generators Necessary? #118  
Give me a break. If your gonna try to get some satisfaction trying to debate 1 tiny fact out of my entire post, at least have the facts to back it up. Using an example "no longer in use" is a piss poor example.

Wow, relax. I was clarifying for people who didn't know the difference. I actually thought you did when I wrote that, I guess not. :) No satisfaction whatsoever and it wasn't my intention to debate, simply clarify the difference between the ground rods (which do not clear faults) and EGCs (grounds) (which do, and is their "primary" purposes)

I'm not sure what you mean "no longer in use", my other examples like metal appliance cases/frames clearly are. It's just not frequent you see a metal-cased drill or hand tool anymore. Stoves, dish washers, refrigerators, etc. all still do, metal surface-mount EMT receptacles, etc

The EGCs DO clear shorts/faults. The ground rods DO NOT. They are both connected together, as is the neutral.
 
   / Grounding Rod For Portable Generators Necessary? #119  
It's amazing how much of a passion people at TBN have for grounding... wow! :)
 
   / Grounding Rod For Portable Generators Necessary? #120  
Give me a break. If your gonna try to get some satisfaction trying to debate 1 tiny fact out of my entire post, at least have the facts to back it up. Using an example "no longer in use" is a piss poor example.

Dark, please read all the posts from beginning to end to understand the whole conversation. Your not an electrician, there's more theory than you understand. I believe soares grounding reference (the grounding bible) is a good reference to use regarding this matter. This comments I made were regarding a single phase 240v service.
 

Tractor & Equipment Auctions

2018 CATERPILLAR D6T LGP CRAWLER DOZER (A51242)
2018 CATERPILLAR...
2019 CATERPILLAR D5K2 LGP CRAWLER DOZER (A51242)
2019 CATERPILLAR...
2014 International DuraStar 4300 Terex BT3063 30,000LB Crane Truck (A48081)
2014 International...
John Deere 700 Hydraulic Hay Rake - Durable Side Delivery Rake for Efficient Windrowing (A52128)
John Deere 700...
2018 GENIE GTH-5519 TELESCOPIC FORKLIFT (A51242)
2018 GENIE...
King Kutter 6' 3 pt Mower (A50515)
King Kutter 6' 3...
 
Top