CobyRupert
Super Member
1.The conductor is larger because the wire is sized according to the size of the service. If a fault would occur, the conductor needs to be sized for the maximum fault current. Yes the code says to size the grounding electrode conductor (to the ground rod) based on the size of the service (conductors). My question is: why? Fault current doesn't flow through the ground rod on it's way back to the neutral of the transformer, unless you are relying on the earth as a ground path, instead of your (green) equipment grounding conductor (EGC) Normally all fault current should travel back to the transformer neutral on the EGC, not through the earth, ground rod or the grounding electrode conductor attached to it .
2. The code never says not to trust the earth as a ground path conductor. NEC 250.4:"The earth shall not be considered as an effective fault-current path" "
If you drive a ground rod, you should always check that it has a reference to ground. Ou also need a second ground, ie.. Cold water pipe.
3. The fault current needs to go back to the grounded conductor. Remember it's a system. The grounded conductor is the return path for current. -To the neutral of the source (transformer or genny) The grounding electrode is strictly for fault current. It's a safety wire.
The only thing I can conclude is you have to vary the grounding electrode conductor size to the ground rod in case the earth does become the path back to the transformer's neutral, despite NEC 250.4 saying not to consider it an effective path it.