Please show me a quote where I said you should bond neutral to ground at a sub panel. Please.
:confused2: Where do I say you did?
Please show me a quote where I said you should bond neutral to ground at a sub panel. Please.
:confused2: Where do I say you did?
Still several things wrong here.
There is more than one wire being run through a box connector. There is an open knock out on the top of the panel. The box is hanging on one screw. 30 amp is too light for the average welder. Any serious home welder requires a 50 amp plug, cable and breaker. The supply cable to that pony panel is several steps undersized being #12 or #10 by the looks of it. Should be #6 or #4 depending on the wire insulation temperature rating. To your credit it appears that the neutral to ground bond screw has at least been backed out. Cables are supposed to be supported within in 6" of the box instead of hanging free air.
Sorry Bud but your wiring job is sub standard, illegal and dangerous to life, limb and property.
I just re-read it. I think you are mis-understanding the point I made.
And? That is allowable. See: http://www.aimedia.co/media/spec-sheets/NM94.pdf and http://www.aifittings.com/reference/files/pdf/charts/nm-cable-ranges.pdf for a fitting that specifically allows it and the manufacturers list of all the possible wire combinations for their box connectors.Still several things wrong here.
There is more than one wire being run through a box connector.
Agreed.There is an open knock out on the top of the panel.
Are you sure? Looks to me like the 2nd screw is mostly hidden by the 12/2 in the top left and there appears to be a 3rd screw in the bottom right quadrant (below the 30 amp breaker but above and between the supply cable and the 10/3 for the welder).The box is hanging on one screw.
If he has #10 wire (which it appears that he has) and a 30 amp breaker, what is the problem? Yes, it would be undersized for a larger welder, but if he only wants 30 amps out there, that is his business.30 amp is too light for the average welder. Any serious home welder requires a 50 amp plug, cable and breaker. The supply cable to that pony panel is several steps undersized being #12 or #10 by the looks of it. Should be #6 or #4 depending on the wire insulation temperature rating.
Agreed, but that can be fixed with a half dozen staples.Cables are supposed to be supported within in 6" of the box instead of hanging free air.
Its tied at the service and isolated everywhere else so that there's only one return path back to the service. Its the multiple paths that cause people to get electrocuted. They think something is off, and it is not, because the ground is still carrying current.
Amuse me. Here's a test. Give me scenario of a fatal situation caused directly by the sub's N being tied to gnd.
I know It's not code, so you can skip that part.
Still several things wrong here.
There is more than one wire being run through a box connector. There is an open knock out on the top of the panel. The box is hanging on one screw. 30 amp is too light for the average welder. Any serious home welder requires a 50 amp plug, cable and breaker. The supply cable to that pony panel is several steps undersized being #12 or #10 by the looks of it. Should be #6 or #4 depending on the wire insulation temperature rating. To your credit it appears that the neutral to ground bond screw has at least been backed out. Cables are supposed to be supported within in 6" of the box instead of hanging free air.
Sorry Bud but your wiring job is sub standard, illegal and dangerous to life, limb and property.