Are you sure that applies? I looked at that section last night and as I understand it, that section only applies to things like emergency lighting that are considered critical to life and health. This genset would be classed as an optional backup genset (702.9) rather than an emergency system.700.19 Multiwire Branch Circuits Prohibited
A new 700.19 has been added addressing multiwire branch circuits used in emergency systems. This new provision prohibits multiwire branch circuits protected by common trip circuit breakers to serve emergency lighting and power circuits. Emergency lighting and power could be unavailable during ordinary line to ground faults and other problems where common trip circuit breakers or handle ties are employed. Continued reliability of emergency circuits requires this change. [ROP 13-118]
Aaron Z