Electrical advice needed
   / Electrical advice needed #51
Based on the information I have supplied, can you recommend a wire size and amperage for the breaker? That's all I am asking.
A planer does not start under load, so locked rotor current of ~ 100A on a 30A motor would be extremely brief. A 30A double pole breaker may sustain that brief starting surge. ... AWG 10 copper will sustain your FLA running current fine, and if a short length run thats what Id use IF a 30A breaker is determined not to give nuisance trips on startup. Going to 40A and 8Ga would give plenty of wiggle room.
You need 3 wires -- 2 hots and Ground. A 4th wire will be needed only if your planer needs a neutral to run an auxiliary 120V circuit.
   / Electrical advice needed #52
I am not versed in electrical code, and cannot cite anything....but protecting a 8ga circuit with a 60a breaker for an electric motor dont sound right?
The breaker is to protect the cable and router from over current due to a short circuit . The thermal overloads in the motor starter protect the cable and router motor from over heating to to overloading . Over loading is a state where line current is approx 115-300% of the motor nameplate amps.
   / Electrical advice needed #53
Finding this whole conversation somewhat amusing...regardless of the site/board, when it comes to electricity the board "lights up". OP apparently has the manual for his tool. I would do what they say. I'm sure the manufacturer has "done the math" because of legal/warranty concerns. Can't hurt to oversize the circuit but why? Cost goes up as the size goes up.
   / Electrical advice needed #54
Under sized cable causes VD and can become too warm.
Undersized breaker will trip during starting inrush.
Undersized breaker will fail earlier than the proper sized breaker.
It's amazing how persons with no formal electrical training in theory or practical. The jackleg electricians will argue all day that they know more than the electrical engineers who wrote the National Electrical Code Book.
Electricity is a "Mystical Black Art" best left to the professionals. Remember what happened to Mickey Mouse with a little knowledge.
   / Electrical advice needed #55
The breaker or fuses at the panel provide Short Circuit protection which motor thermal overloads can not provide.
Motor Thermal Overloads in the motor starter provide protection to the supply cable, connections, starter and motor from thermal damage due to overloading.
Both systems are required to provide electrical protection.
   / Electrical advice needed #56
If the manual says 6-30R, that's what I would install, with 10awg and 30A breaker. 8awg is ok too.
   / Electrical advice needed #57
Well...if you have a well known manufacturer and they lay out the requirements (surely passed by their engineers and legal departments), why argue with them? As for the National Electric Code, it is becoming a joke in too many ways...the basic principles have not changed since before Edison. I find the biggest objectors to "DIY" electrical are those that object to people figuring out that most things don't require a professional. I hired one on this house and spent a lot of time fixing his screw-ups (some that will never get fixed without tearing out drywall and doing it right). Guessing you are in that camp.
That makes too much sense for some on here. Not enough technical jargon and useless gobbledygook.
   / Electrical advice needed #59
Why not start out with " do you still beat your wife ? "
   / Electrical advice needed #60
Look at the wiring diagram and tell me where the motor overload is. The thing that labeled reset? Is the 30amp circuit breaker the overload protection? I haven't seen anything that tells me this manufacturer and its instructions have a clue on the wiring requirements. Clue #1: it's a motor >1 hp.
2014 JLG G12-55A 12,000lbs 4x4 Rough Terrain Telehandler (A53421)
2014 JLG G12-55A...
2009 MACK GRANITE (A52472)
2009 MACK GRANITE...
FORD 555B BACKHOE (A51246)
FORD 555B BACKHOE...
Adams 6 Ton Hydraulic Lime Spreader (A53473)
Adams 6 Ton...
NEW 2024 LOAD TRAIL 83IN X 14FT Tandem Axle Dump Low-pro Trailer (A53473)
NEW 2024 LOAD...
2011 DODGE CARAVAN (INOPERABLE) (A53843)
2011 DODGE CARAVAN...