I need help understanding AC electricity and generators (1/3 phase)

   / I need help understanding AC electricity and generators (1/3 phase) #21  
The best way I can think of to explain this is that power distributed throughout the country is 3 phase. To deliver the power to a house one of these phases is tapped to run a line to the house (hence the term single phase). The transformer the house is connected to puts out 240v. However, it is a center tapped transformer, so between the center tap and either end is 120v. You have both ends and the center tap (plus ground) being run to your main breaker panel. Generators will have to emulate this.

Grounding electrical systems is a whole course by itself.

That's about the clearest, easiest to understand explanation I've heard in a long time. :thumbsup:
 
   / I need help understanding AC electricity and generators (1/3 phase) #22  
I guess that I have been spoiled, I have never had anything that wouldn't run on my generators.
I have had engine driven as well as pto powered.
They all worked for everything I have run.
I will note that they have all been 4 pole generators so 1800 rpm for the generator head.
As far as not being within spec for frequency that is a drive rpm function,
and the voltage regulator should be adjusted as needed.
 
   / I need help understanding AC electricity and generators (1/3 phase) #23  
Description needs to add the 120 volt segments are 180 degrees out of phase to each other resulting in the 240 volts between the two.
 
   / I need help understanding AC electricity and generators (1/3 phase) #24  
Something you should do is look at all of your 240V appliances and read the plates on them. You might be surprised that many/most/if not all will say they can run on 208/240. If they all say that, then you could run a 3 phase generator, take one leg for 120v, and combine 2 legs for 208 and be just fine. The generator will only be running at 2/3 rating (2 of the 3 legs), so it won't be that efficient, but it will work with no problems.

Take a look. See what you find on your appliances. Look at your servers, too. Many have switches for 120v/240v. See if they're rated for 208.

Just remember that if you want 15kw total out of a 3 phase generator that's only using 2 legs to get your 208, you'd need something at least 22.5kw due to the 2/3 usage. Make sense?
 
   / I need help understanding AC electricity and generators (1/3 phase) #26  
Just remember 3 phase generators are rated by adding up each phase. Use only 1 phase and 1/3 the rating. Also best to try and load balance the 3 phases if possible.
 
   / I need help understanding AC electricity and generators (1/3 phase) #27  
I have googled and googled over the years and have come to a limited understanding on how things work. I will go down the list of my current assumptions, if I'm wrong please correct me.

I currently have a generator that is 10kw 110/220v. In 220v mode i have a ground, neutral, and 2x 110v's 180 degree's out of phase. These 2x 110v's go to the 2 busses in my breaker box by way of a 50a 2 pole breaker. When the power goes out, I switch off my main, switch on my generator, and I can use electricity, both 110v and 220v devices.

There's many generators on craiglist that are 3 phase. From my understanding, it's 3x 110v's 120 degree's out of phase. Being that my breaker box is only 2 phase(i know hte terminology is wrong, but i don't know the right way to say it), I would only be able to utilize 2 of the 3 phases available from the generator. So 15kw becomes 10kw. However does putting those 2 phases together create a usable 220v? I'm guessing no. Which means I wouldn't be able to utilize any 220v appliances in my home.

Why is a 110v/220v generator called single phasea nd not 2 phase? It provides 2 phases of electricity capable of generating 220v? They're definitely distinct from generators that only provide single phase 110v.

I realize that some of this I am not even asking the right questions, so please be patient.

What kind of 10kw generator do you have?

Your typical 10kw gas unit is rated at 10kw peak and some won't run at that for any length of time without faltering. Most of those will run at 8kw tops.

I have one of the MEP803A military surplus diesel generators. It was designed to run 10kw continuous. I can load it to 13.5kw and it will not falter. It has switches to run at 3 phase or single. My house is all electric with a 3.5 ton AC and a 1.5 HP well so it will NOT run everything at once. My rule of thumb is to leave all the 120 V breakers on and any two of my 240 breakers. Basically if I turn off my AC I can run my water heater or stove as needed. I might could get away with leaving the whole house on but why take a chance. In the off chance my water heater was on and my AC and well tried to start at the same time it would probably cook something I didn't want to replace. I can run the water heater for an hour and have enough hot water for 3 showers. There have been times during a long outage we turn on the oven and bake cookies to put more load on the unit so it doesn't get wet stacked.

At the prices the military surplus units are fetching these days I would just take out a loan and buy a brand new single phase generator that would run my whole house.

One thing about running diesel is the need to run it at or near full load periodically to prevent wet stacking. Everything has a trade off. I built myself a 13.5kw resistive load bank to run my set on monthly. I run it at 40 amps for at least an hour every month.
 
   / I need help understanding AC electricity and generators (1/3 phase) #28  
Just remember 3 phase generators are rated by adding up each phase. Use only 1 phase and 1/3 the rating. Also best to try and load balance the 3 phases if possible.

Which is kinda hard to do if you're only using 1 phase for 120v or 2 phases for 208 in a residential panel. You can't use the 3rd phase anywhere, so the genny is gonna run inefficiently. But it's an emergency, so we don't care right now. Gotta have that air conditioning and ice for the drinks. :laughing:
 
   / I need help understanding AC electricity and generators (1/3 phase) #29  
Just remember 3 phase generators are rated by adding up each phase. Use only 1 phase and 1/3 the rating.

This is incorrect. When you connect a single phase load to two leads of a 3 phase generator, you're utilizing 2 phases (to obtain single phase) -confusing, but that's how it is. You use 2/3 of the generator rating.

Also best to try and load balance the 3 phases if possible.
Agreed, but kinda hard to do when you're only using 1 phase. Hence the derating.
 
   / I need help understanding AC electricity and generators (1/3 phase) #30  
I beg to differ on the 120/240 being out of phase. AGAIN, someone confuses the issue. If they were 180 degrees out of phase, they would cancel each other out. They are simply different taps, or windings, on a single phase.

Or am I totally misinformed? I'm not an electrical engineer and this stuff, the math, has never been my strong point.

Single phase IS single phase. Not suddently two phases! Not on a generator and not in your house panel.
 

Tractor & Equipment Auctions

1990 Ford F800 7 Yd. S/A Dump Truck (A48081)
1990 Ford F800 7...
71067 (A49346)
71067 (A49346)
2016 New Holland Boomer 47 4WD Front Loader Utility Tractor with Bush Hog BH16-2 (A50322)
2016 New Holland...
2020 PETERBILT 337 BOX TRUCK (A51222)
2020 PETERBILT 337...
2021 FORD F-150XL CREW CAB TRUCK (A51406)
2021 FORD F-150XL...
2022 Case IH Steiger 470HD AFS Connect RowTrac 4WD Tractor (A50657)
2022 Case IH...
 
Top