Electricians? Weird problem!!!!!

   / Electricians? Weird problem!!!!! #1  

Fuddy1952

Elite Member
Joined
Apr 17, 2018
Messages
4,332
Location
South Central Virginia
Tractor
1973 Economy and 2018 John Deere 3038E
I installed a fan and a light in the horse stable. Fan is 120v, 5.5 amp. Light is 35 watt (300watt equ) LED. To test everything I used a 50 ft 14 gauge extension cord, wires just pushed in socket. Worked fine, and I let fan run an hour or so, even cycled it a few times.
Today I wired in conduit. Square D box, out of 20 amp breaker (of course on black hot) which goes up to a simple ceiling light above tack room, a 60w bulb with socket. Pull string switch. Nothing else on the circuit. Convenient and not far from fan so that's where I picked up power. All wire, panel box to there...that to switches is 12-2.
In double switch box 120v in (12-2), then out with 12-3 up to fan & light. I have all bare grounds tied together, white neutrals together. Before I put switches in, I just touched red going to light to black hot...light works perfectly. Then I tried hot to black fan hot...fan motor hummed & tiny bit smoke came out!!!!!
I checked, blade turns free, I double checked wiring. With Fluke meter 124.5vac no load, same with light on...108.4vac touching fan wire! (I just try it a second). It sparks when I touch it, fan never moves.
If it worked with 14ga extension cord...wouldn't it work with 12 ga?
From upstairs light up to fan is a little less than 50 feet, probably 20 feet there to panel box. The circuit breaker never trips.
Any ideas much appreciated!!!!!
20220413_202403.jpg
 

Attachments

  • 20220413_202403.jpg
    20220413_202403.jpg
    253.5 KB · Views: 121
   / Electricians? Weird problem!!!!! #2  
I'm no electrician, but have wired many lights and plugs. I really don't see anything wrong with your wire diagram.
12/2 wire should make no difference. on what you are running. I doubt that fan and light pull 20 A
Have you checked voltage at the fan hot wire with fan disconnected ?

Perhaps something is shorted in the fan motor
 
Last edited:
   / Electricians? Weird problem!!!!! #3  
This has nothing to do with wire guage or breaker amps,something is crosswired or fan is kaputt. If I was taking bets I'd give odds on sub-panel not properly wired for ground/earth/green. Make sure you follow code for ground and neutral bar separation at sub-panel. It doesn't make a lick of sense but has been proven voltage can go from black to bare then to white unless bars are isolated by removing screw.
 
   / Electricians? Weird problem!!!!! #4  
Use a voltmeter and check your voltage from your black wire to the white wire and from the red wire to the white wire and see if you have 220 volts instead of 110. If you do your fan is toast because you let the smoke out.
 
   / Electricians? Weird problem!!!!!
  • Thread Starter
#5  
Use a voltmeter and check your voltage from your black wire to the white wire and from the red wire to the white wire and see if you have 220 volts instead of 110. If you do your fan is toast because you let the smoke out.
I'll make lots of checks tomorrow. Thanks all!
 
   / Electricians? Weird problem!!!!! #6  
If you are only feeding this with a single breaker, and a single black hot, you can't possibly have 240 v. Is the fan known good, or was it old.

your schematic looks fine.
 
   / Electricians? Weird problem!!!!! #7  
If you applied power and tried to start the fan when it's switch was in Low (or even Med), you probabaly 'locked' the fan motor and it overheated. There is a reason fans always have High as the first setting and have to go through it to start the fan.

Impeadence of the motor coils mean there is voltage drop across it so will read lower voltage with the meter.

Make sure the fan is in High setting and rotate the blades before adding power, if it spins up, the fan is still good and you know your problem. If not, then most likely fan is now blown and you know what not to do.
 
   / Electricians? Weird problem!!!!!
  • Thread Starter
#8  
If you applied power and tried to start the fan when it's switch was in Low (or even Med), you probabaly 'locked' the fan motor and it overheated. There is a reason fans always have High as the first setting and have to go through it to start the fan.

Impeadence of the motor coils mean there is voltage drop across it so will read lower voltage with the meter.

Make sure the fan is in High setting and rotate the blades before adding power, if it spins up, the fan is still good and you know your problem. If not, then most likely fan is now blown and you know what not to do.
Fan doesn't have speed settings, just a GE 120v motor...(I'm guessing 3/4?hp) capacitor start.
 
   / Electricians? Weird problem!!!!! #9  
Fan doesn't have speed settings, just a GE 120v motor...(I'm guessing 3/4?hp) capacitor start.
OK. Was thinking it was more like a ceiling fan.. Have you checked the cap then? Could still start the blades by hand and try to check if motor itself is still good.
 
   / Electricians? Weird problem!!!!! #10  
“If you applied power and tried to start the fan when it's switch was in Low (or even Med), you probabaly 'locked' the fan motor and it overheated. There is a reason fans always have High as the first setting and have to go through it to start the fan.”
I’ve never seen, or heard of a 3 speed fan, that was designed so it would burn up, if started in low or medium speed
 
   / Electricians? Weird problem!!!!! #11  
Op: Can you better explain exactly where you measured 108volts? Looks like you’re dropping 16 volts somewhere, which maybe due to a loose connection. Does the fan have a locked rotor amp rating? Your complete wiring path may be inadequate.
Did you try it back through the cord that it worked with originally?
 
   / Electricians? Weird problem!!!!! #12  
fan motor hummed & tiny bit smoke came out!!!!!

They only put so much smoke in those things. I think it requires ALL the smoke to function properly. But anything can be a smoke machine if it is operated poorly enough :).

I didn't see anything wrong with your diagram either. I would still check hot to neutral just to be sure you don't have some wires touching that shouldn't be. It is really tight in those quad/duplex boxes for all the wire you have to cram in there.
 
   / Electricians? Weird problem!!!!! #13  
I agree with the above poster who said to find out where / why you measured 108V.
Also check connections are good.

Did you measure the 108V when fan was humming and stalled (in a locked rotor condition)? Basically, the large locked rotor current would cause a voltage drop in the wiring from the panel so that the 120V (124.5V) is dropped to 108V. (Knowing circuit length and wire gauge, one could calculate how much current it takes to drop 16 volts (or whatever it is) in a #12 AWG wire).
I’m surprised the breaker doesn’t trip. Maybe it would eventually. It’s probably a race between the breaker and the motor making smoke because it’s wires can’t handle large locked rotor currents for very long before burning up.
Motor starting capacitor may be toast.

For giggles let’s say circuit’s length from panel is 100’, so 200’ total travel in hot and neutral conductors. Say #12 gauge wire has resistance of 1.93 ohms/1000’. So 200’ of wire would be .386 ohms. 16 volts drop through .386 ohms only happens when 41 amps is “humming” through the fan.
As a rule of thumb, the “locked rotor” (aka “stalled”) current of a motor is about 6 times its normal current. So 41 amps is in the ballpark.
If you look at the trip times (curves)of a 20amp circuit breaker experiencing 41 amps, I bet your breaker would of tripped right on schedule, probably around 10 seconds.
If you had wires crossed and a dead short, breaker would of tripped in about .01 seconds.
 
Last edited:
   / Electricians? Weird problem!!!!! #14  
When I wired my barn I had something similar happen. Turned out that when I pushed the wires back into the box, the sharp end of the bare ground wire cut thru the insulation of the white neutral wire and put voltage on the ground wire. And this was on a different circuit from the main breaker panel. You may want to pull all the wire connections out of the box and recheck to see if it all operates properly and put things back in one at a time.

I agree, your wiring schematic should not be a problem and should work correctly.
 
   / Electricians? Weird problem!!!!! #15  
I’ve never seen, or heard of a 3 speed fan, that was designed so it would burn up, if started in low or medium speed
Exactly. Ceiling fans have a chain to pull to switch the speed, but are turned off and on with a switch. They can be left in low/med speed and turned on/off with the switch with no problem.
 
   / Electricians? Weird problem!!!!! #16  
Could be a floating ground or neutral too. But fan smoke is long gone, sometimes ok, but not often.
Cross wired, or wires touching also could be the issue.
 
   / Electricians? Weird problem!!!!!
  • Thread Starter
#17  
Here's what I did this morning as I explained it to the contractor friend who was helping me:
"The motor is bad.
I tried down below connecting motor to extension cord...hummed & didn't turn. So I went up on scaffolding connecting motor wires right to cord like we had before & same thing.
An electrician wrote me and said little puff of smoke meant start winding burned up. One he had he got lucky & it opened winding where he could resolder it. Most motors you can't get to it.
Now if I plug it into a ground fault breaker circuit it trips instantly. Plugging into another outlet breaker doesn't trip but you can tell it's drawing lots of current.
It (motor hot & neutral) measures 4.6 ohms.
I took front off panel box and everything is wired ok...it's just too weird.
My plug in tester says it's OK. I measure zero ohms ground to neutral. 123.6 vac black to ground or white neutral.
Electrician said motor had "the smoke of death"!
I'll have to get another fan, electrician said rewinding is more expensive, probably motor is too.
I do have a very large squirrel cage fan, about same cfm I'm thinking, but outlet is rectangle I'm guessing 30"X 18". Heavy...probably weighs 50-60#. That one is belt drive motor to squirrel fan blades."
 
   / Electricians? Weird problem!!!!!
  • Thread Starter
#18  
Oh...I forgot to thank everyone for replies.
Thank you!
 
   / Electricians? Weird problem!!!!! #19  
I’ve never seen, or heard of a 3 speed fan, that was designed so it would burn up, if started in low or medium speed

Never said it was designed to, but 'could' and 'might'.
 
   / Electricians? Weird problem!!!!! #20  
Just out of curiosity where you say you picked up power at a simple single light fixture, are you sure that the black wire is the hot wire? Many people will use the white wire on a single run from the switch to the light fixture as their hot wire, and very few mark it with a ring of black tape. Only way to be sure is check white to bare ground to be sure, inside wiring is one of those things that sometimes will still work even when someone has wired it up wrong.
 

Tractor & Equipment Auctions

2025 MACK GRANITE GR64F DUMP TRUCK (A59823)
2025 MACK GRANITE...
iDrive TDS-2010H ProJack M2 Electric Trailer Dolly (A55851)
iDrive TDS-2010H...
2017 Toyota Tundra SR5 Ext. Cab Pickup Truck (A59230)
2017 Toyota Tundra...
1998 INTERNATIONAL 9400 (A58214)
1998 INTERNATIONAL...
Redirective Crash Cushion Guardrail (A59230)
Redirective Crash...
Bell 1600 Gallon Nurse Trailer (A56438)
Bell 1600 Gallon...
 
Top