ChatGPT answer to my 16x30 CMU storage building request.
Awesome—here’s a practical, build-ready concept for a CMU storage building with a monolithic slab and a low-slope (1:12) single-slope roof, plus a detailed materials list. I’m making a few reasonable assumptions to keep this complete and usable; tweak anything you need.
16' × 30' CMU Storage Building — Concept Design
Key assumptions (you can change these)
Footprint: 16' (width, slope direction) × 30' (length).
Two open door openings, each 8'-0" wide × 8'-0" high, centered on the 30' front wall (leave them open; no doors installed).
Low eave height = 10'-0". High eave height = 11'-4" (1:12 rise across 16' width gives 16" rise).
CMU walls: 8" nominal units; fully grouted only where reinforced & at bond beams.
Exposure: standard, non-coastal; generic 115–130 mph wind region (verify locally).
Roof: wood rafters @ 16" o.c., 5/8" sheathing, fully adhered underlayment, mechanically seamed standing-seam metal (suited to 1:12).
This is a prescriptive concept, not a stamped structural design—have a local pro review for your site loads, codes, and inspections.
---
Plan & elevations (described)
Plan (30' side is front): Two 8'×8' openings on the front wall, centered and separated by a ~6' pier. Side and rear walls solid.
Heights: Front (low eave) top of wall ≈ 10'-0". Rear (high eave) ≈ 11'-4". Gable (16' ends) follow the roof slope.
Roof slope: Rises from front to rear at 1" per foot (1:12).
---
Slab & foundation (monolithic)
Slab: 4" concrete slab, 3,000–3,500 psi, fiber or 6×6-W1.4xW1.4 WWF.
Thickened edge (turndown): 12" wide × 16" deep around perimeter (measure from slab top), with (2) #4 continuous bottom bars; corners hooked.
Vapor barrier: 10-mil min poly over compacted base (4" min compacted gravel/stone).
Control joints: ~12' max spacing each way (sawcut 1/4 slab depth within 6–12 hrs).
Anchor/dowels
#5 vertical dowels from thickened edge @ 48" o.c. (embed 24"), lap with vertical wall steel.
5/8" J-bolts @ 48" o.c. in top bond beam (or use CMU strap anchors) to fasten treated wood plate for roof connection.
---
CMU walls
Units: 8" CMU (ASTM C90).
Reinforcement (typical):
Vertical #5 @ 48" o.c., at corners, each side of openings, and at ends of walls; fully grouted at reinforced cells.
Horizontal: Top bond beam course continuous with (2) #5; grout solid.
Additional lintel course over the 8' openings (bond-beam units) with (2) #5 cont.; provide at least 8" bearing each side.
Mortar: Type S. Grout: fine grout where called.
Sill/Top Plates: Pressure-treated 2×8 plate anchored into the top bond beam to receive rafters/hurricane ties.
---
8' × 8' door openings (no doors)
Jambs: Reinforced CMU jambs each side: (2) #5 bars (one in each adjacent cell), grout solid.
Lintels: One course of 8" bond-beam units over each 8' opening with (2) #5 continuous; provide temp shoring until grouted & cured.
Sill: Slab flush; consider a slight recess/steel angle edge if you want impact protection.
---
Roof (single slope, 1:12)
Framing: 2×12 rafters @ 16" o.c., spanning the 16' width from low eave to high eave.
Connections: Simpson (or similar) hurricane ties at each rafter to the PT top plate; plate anchored to CMU bond beam.
Decking: 5/8" plywood (Exposure 1) with H-clips; nail per code.
Underlayment: Full-coverage self-adhered ice & water membrane (low-slope requirement).
Roofing: 24-ga mechanically seamed standing-seam metal panel system approved for 1:12 slope with manufacturer’s clips/trim/closures. Provide eave/drip/sidewall flashings and sealants per manufacturer.
Overhangs (optional): ~12" front & rear with fascia; add blocking at eaves.
---
Estimated quantities (materials list)
Concrete & base
4" slab (16'×30'): ~6.0 yd³
Thickened edge (12" wide × +12" thick extra, around 92' perimeter): ~3.4 yd³
Order total concrete: ~10.0 yd³
4" compacted base (gravel/stone): ~6.0–7.0 tons (≈ 6–7 yd³)
Vapor barrier: 10-mil poly, 1 roll (400–1000 sq ft)
Reinforcing steel
Slab edge: (2) #4 cont. around 92' → ~200 lf (#4 comes in 20' sticks → 10 pcs)
Dowels from footing into wall: #5 @ 48" o.c. around 92' → ~23 pcs @ 24"
Vertical wall bars: #5 @ 48" o.c. around 92' + corners/jambs → ~31 pcs @ 12' (cut/field lap as needed)
Top bond beam: (2) #5 cont. around 92' → ~200 lf (≈ 10 sticks)
Lintel over two 8' openings: (2) #5 cont. each opening (~10' incl. bearing) → ~40 lf (≈ 2 sticks)
Tie wire, chairs, etc.
CMU & masonry supplies
Wall area estimate (accounts for slope and subtracts two 8'×8' openings):
Gross wall area ≈ 982 sq ft, minus 128 sq ft openings → ≈ 854 sq ft of wall
Standard 8×8×16 CMU: ≈ 960 units (0.889 sq ft face each), add 5% waste → ≈ 1,010 units
8" bond-beam CMU (top course around ≈92'): ~69 units, add 5% → ~73 units
Additional bond-beam CMU for two lintels (one course spanning each opening incl. bearing): ~18 units total
Half blocks/corners: ~50 half units, corner bond-beams ~8
Mortar Type S (pre-blended): ~26–30 bags (rule of thumb ~1 bag/35–40 blocks; add a couple for lintels/jambs)
Grout (fine): ~1.5–2.0 yd³ (lintels, bond beam, reinforced cells at verts/jambs)
Cleanout ports as needed, rebar spacers, cell plugs
Anchors & connectors
5/8" J-bolts for top plate @ 48" o.c. (stagger near corners/openings): ~28 pcs with washers/nuts
Simpson hurricane ties (one per rafter): ~23 pcs
Straps/anchors for jamb steel as required
PT sill/top plates: PT 2×8 around 92' → ~12 pcs (8'–10' lengths; adjust to available lengths)
Roof framing & sheathing
2×12 rafters @ 16" o.c. along 30' length → 23 rafters at ~18' cut length (includes ~12" eave overhangs). Order 23 pcs 2×12×20' (trim to fit).
5/8" plywood roof sheathing: Area ≈ 480 sq ft → 15 sheets, add waste → 17 sheets
H-clips and 8d nails per code
Roofing (low-slope metal)
Self-adhered underlayment: ~5 squares (500 sq ft) total coverage
Standing-seam metal panels (mechanically seamed, 16" o.c. typical):
Panel count along 30' = ~23 panels
Panel length ≈ eave-to-eave (allow for overhangs/hem) ~18' each
Clip/fastener kit, eave/drip/sidewall trims, end-closures, sealant, touch-up paint
Fascia/soffit (if overhangs enclosed)
Miscellaneous
Control-joint filler/caulk for slab sawcuts
Expansion joint material at slab-to-CMU (if desired at interior face)
Flashing at openings (optional) and jamb corner guards (optional if equipment use)
---
Build notes & sequencing (high level)
1. Excavate, place and compact base; set forms for monolithic pour with edge thickening; place vapor barrier and reinforcement; pour and finish slab; early-saw control joints.
2. Lay CMU to 8' opening height; install jamb steel; set lintel (bond-beam units), shore and grout; continue to top; place top bond beam with (2) #5 and anchor bolts.
3. Install PT top plate; set rafters @ 16" o.c. with hurricane ties.
4. Install sheathing, underlayment (full coverage), then standing-seam metal with all trims/closures.
5. Optional: seal CMU exterior, add gutters at low eave, add bollards near openings.
---
If you want, I can turn this into a printable one-page plan set (plan + elevations + details) and a CSV shopping list. Tell me any changes (number/location of openings, desired eave heights, interior finishes, gutters, etc.), and I’ll bake them in.