Jerry,
Thanks so much for the reply. I should have been a bit more clear. This wiring is in a barn. There's no water meter and no plumbing of any kind. Believe it or not, when this was served from the now-gone house the ground rod from the panel in the barn was INSIDE!
If I understand you correctly, I'm going to be driving an eight foot long rod into the ground. Is that right? If my locality wants it in the breaker panel can I just come out of the panel with the bare wire and go through the siding to the outside? It's a pole building with metal siding.