dcarman
Bronze Member
When it is empty the startup current draw is low enough to get through your little cord. When the pressure is higher at restart the current draw is a lot more causing your issue. Not only are you using to light a cord, it is way to long for this application. The solution is more power at the compressor - in other words a shorter and/or heavier cord.I picked up a couple of compressors, one is electric the other gas. The electric starts up fine from my temporary power source a hundred feet away with a 100 ft 15 amp extension cord but as soon as it needs to automatically re start itself cause the air pressure drops it will not start, it just sits there making an unhappy noise until it blows a fuse or damages the outlet it’s plugged into.
What might be the problem?
It operates fine when plugged directly into the same outlet.