MikeD74T said:In my case the hot water made it 70' to the basement thru insulated pipe & was still hot enough to lift the relief. I can't imagine that anyone is going solar with uninsulated pipes!!! Fortunately my relief is piped to a 5 gallon jug so I didn't loose any antifreeze but lost system pressure & had to pump it all back in after the collectors cooled down. Don't know if it would affect PEX but it should be considered. MikeD74T
The question I have is did the heat open the relief valve, or did the pressure open it? Hot water expands quite a bit as it heats up, and if it starts boiling the pressure goes up very quickly. Depending on your antifreeze concentration, it would need to get to about 250-260 degrees to boil, but i suppose it could happen on a roof on a hot day.
If your system has an expansion tank that should have taken care of any ordinary expansion as the water heated up, but if it got hot enough to boil the water an expansion tank would definitely not have been enough to prevent the relief valve from opening. When water turns to steam it expands app 1,680 times, so it takes up a LOT more room than before.