Electrical Panel Mounting - Polebarn
/ Electrical Panel Mounting - Polebarn #1
bigballer
Platinum Member
PNW - North Central bWashington - The Evergreen St
2006 Kubota L3400
Wanted for get some ideas on mounting a panel in my pole barn. There are not standard 2x4 wall just post frames with horizontal purlins ad sheet metal. Was thinking about just using a large section of 3/4" plywood And attach it to the purlins. Also, can a I just run romex from the branch ckts breaker to the outlets/switches or does it need to be in conduit?
/ Electrical Panel Mounting - Polebarn #2
Yes, or you could pair up (side to side) a couple of 2X10's vertically between two wall girts (purlins) at "code" level. I'd locate it to one side or the other of a post so that the wiring heading out to your circuits could be fastened to it. I can't answer your romex/conduit question, it may be a code issue for either rodent concerns or open-exposed wiring. If you are going to insulate it, you can place some vertical 2X4,6 ? vertically, then create a solid surface. Similar to how they provided support for windows or doors, this will provide a space for insulation behind the panel and "flush out" to the interior surface for interior finishing.
/ Electrical Panel Mounting - Polebarn #3
My service panel is mounted on 3/4" OSB mounted to the window framing. I added a vertical "stud" to support the center of the OSB.
If I didn't have the window framing to work with, I would just run 2X4's between the posts (narrow side out like a stud) and then use a couple more 2X's for the vertical framing.
My OSB is 5" off the wall tin.
This is a 400A service, with a 200A panel. I used 12ga AC wire. Looking to avoid any possible issues down the road.
My electrician installed the 200A Panel and 200A cutoff. It is inspected by the county. I ran the circuits after. Inspection not required.
/ Electrical Panel Mounting - Polebarn #4
My panel is mounted on a sheer of 3/4" OSB, similar to ace10's.
Will
Thanks for the replies. I like the 2x10 idea too. My electrician will be replacing my main panel at the house so I want to get the barn prepped for the sub panel. Will be nice to scrap the extension cord currently feeding the pole barn. I'll see what he says about code on the branch feeds.
Furthering work on this project, my main panel was replaced and now am ready to dig a trench to extend the wiring to the barn. The run is about 80' and I want a 50amp main in the barn for some lights and a couple outlets. Is #4 wire sufficient for this? I would run 2 hots and a neutral. At the barn, I believe the neutral and ground bars need to be separated with dedicated ground rods coming off the barn panel. Is this correct?
/ Electrical Panel Mounting - Polebarn #7
Three insulated wires and a bare or green insulated ground.
Correct at the panels remote from the first ground to neutral bond near the utility transformer. The neutral bar must float free from the ground system . Or the ground system will be energized with neutral current and have voltage potential above true earth potential. Ground rods at every panel and the entire grounding system tied together is vital.
/ Electrical Panel Mounting - Polebarn #8
Correct, neutral and ground kept separate at barn. But you do need to run a ground wire from your home main panel in addition to the two hots and neutral. And you need an additional ground rod (or rods) at the barn.
#4 Aluminum would be fine, or #6 copper.
/ Electrical Panel Mounting - Polebarn #10
I just had my barn wired and the electricians said the code changed a few years ago, they are no longer allowed to put separate ground rods at each location. The ground wire has to be run uninterrupted back to the ground at the main service panel, and only the main service panel can be connected to a ground rod. I called the county to confirm that, they said the same thing. Not sure if this is something local around here, or part of the NEC.
/ Electrical Panel Mounting - Polebarn #11
Not sure about that -- I checked the most recent code when wiring my pier in 2013, and the rules were no ground rod required if a branch circuit, but ground rod required if a feeder circuit. That hasn't changed from what I know.
/ Electrical Panel Mounting - Polebarn #12
My friend that is an electrician told me the same thing. You need to run four conductors from the house to the barn per code. They changed the code because the ground rod in each locations could be at different potential. Having just one earth ground at the house eliminates the possibility of a difference in potential.
/ Electrical Panel Mounting - Polebarn #13
Wow that is a strange one if it's a service wired with two insulated lines, an insulated neutral and a dedicated ground.
Buuuuuuuuuuttttttttttttttttt..............if it one of those nasty overhead triplex service supplies which the utilities used back when nobody knew any better. And are still Grandfathered to this day. Then yes some utilities made sure the ground system doesn't run neutral current. The triplex neutral will only have one connection to ground at or near the meter base. All breaker/fuse panels will however have a pair of ground rods connected to the ground bar and a floating neutral bar.
Iranch High-End Tricycle (A64119)
Iranch High-End...
3 Point Hay Forks (A62613)
3 Point Hay Forks...
Skid Steer 3 Point Plate (A65640)
Skid Steer 3 Point...
New/Unused ATS T460 Mini Skidsteer (A65583)
New/Unused ATS...
2022 BOBCAT T76 SKID STEER (A65053)
2022 BOBCAT T76...
2018 CATERPILLAR CS44B SMOOTH DRUM ROLLER (A65053)
2018 CATERPILLAR...