Electrical question

   / Electrical question #11  
Just got me to thinking. You can draw 15 amp off each side of a split receptacle fed with 14/3, like plugging in a kettle and a toaster oven, for a total of 30 amps (well, in a way) but couldn't draw 30 amps between the two legs as you would exceed the capacity of the 14 AWG. That, can become confusing.

Also (sometimes) confusing: If each side of the split receptacle is drawing 15 amps, (for a total of 30 amps passing through the breaker and receptacle), the return current in the neutral is (15 amps + 15 amps =) 0 amps. :eek:

(Some may insist it's really 15 + (-15)=0)
 
   / Electrical question #12  
I wish for starters that there was some universal description of the two (110V) transformer windings. I call them legs, but that not a good description. Hence all the improper talk about "phases". Curious, that there isn't a better description.

It's hard to explain to a DIYer if they don't know how a transformer works.

I always wondered if in Europe they use the same system, which would mean almost 500 volts entering the home.
 
   / Electrical question #13  
IMHO:
I think "legs" are a good description for the conductors or bus. When talking about "the system", I usually just say "120/240V single phase" and anybody who has understand the conversation up to that point knows what you're talking about. And if they don't, then maybe they shouldn't be playing with electricity and we shouldn't be having the conversation.:rolleyes:

Plus, "single phase 120/240" seems more descriptive and easier to say than a "120/240V split phase" system" or a "single phase, 3 wire system', or a "center tapped, single phase, 3 wire system" . Also "leg" is a more universal, familiar term, as it often used with 3 phase systems.
 
   / Electrical question #14  
Stupid question, but where does 208 and 347 (in Canada) come from? We have 600 3 phase.
 
   / Electrical question #15  
Also (sometimes) confusing: If each side of the split receptacle is drawing 15 amps, (for a total of 30 amps passing through the breaker and receptacle), the return current in the neutral is (15 amps + 15 amps =) 0 amps. :eek:

(Some may insist it's really 15 + (-15)=0)

There ain’t no 30 amps anywhere . It is two circuits of 15 amp that are 180 degrees out of phase . Neutral would flow zero current .
 
   / Electrical question #16  
Stupid question, but where does 208 and 347 (in Canada) come from? We have 600 3 phase.


From a wye configured transformer secondary . Three set of windings that are physically and mechanically 120 degrees apart. Divide 600 by the square root of 3 and that makes 347V to neutral.
 
   / Electrical question #17  
I wish for starters that there was some universal description of the two (110V) transformer windings. I call them legs, but that not a good description. Hence all the improper talk about "phases". Curious, that there isn't a better description.

It's hard to explain to a DIYer if they don't know how a transformer works.

I always wondered if in Europe they use the same system, which would mean almost 500 volts entering the home.

Europe sends one live line of a three phase service and the common neutral into homes and businesses with a single phase service . 240V to neutral. A three phase service would still be 240 from any line to neutral. 416V from any line to any other line .
 
   / Electrical question #18  
Sizing branch-circuit conductors. Branch-circuit conductors that serve a single motor must have an ampacity of not less than 125% of the motor's FLC as listed in Tables 430.147 through 430.150 [430.6(A)]. You must select the conductor size from Table 310.16 according to the terminal temperature rating (60ーC or 75ーC) of the equipment [110.14(C)].
Not sure what your getting at, you might have a smart (adjustable) breaker, or engineered overloads or some kind of electronic circuit protection... If your everyday motor is FLA rated at 40 amps, and you run it on 12awg, and put a 60 amp breaker on it... you MIGHT have a problem.... I was only illustrating that a motor might only run at 8A, but is a dynamic load. No load amps, Full load amps, locked rotor amps, inrush current.... Single phasing not withstanding.

Your wire should never be the weak link.


50amp wire will never melt or fail. It is thermally protected .
 
   / Electrical question #19  
Stupid question, but where does 208 and 347 (in Canada) come from? We have 600 3 phase.

208v in the USA is low-voltage 3-phase.

It is used for 120v stuff like office lighting in a factor. And in many cases alot of appliances or motors that are designed for 240v single phase, will also operate on 208v.

So 208 3-phase is a wye configuration that has a center neutral.

Any one of the phases to neutral is 120v. (single pole breaker in that panel) So thats all the lighting.
A double pole breaker can be installed and have 208v between two of the phases. (this can sometimes be used on 240v appliances)
A 3-phase breaker can be installed and power 3-phase motors if the motors can be wired to that voltage (low voltage)
 
   / Electrical question
  • Thread Starter
#20  
I've got lots of training in navy 3 phase ungrounded and industrial 3 phase, but have forgotten most of it. But I'm fairly certain 240v is x2 120v phases that are 180 degrees off.

20171120_102141.jpg
 

Tractor & Equipment Auctions

Show Livestock Tie Up Rack (A50515)
Show Livestock Tie...
Quick Attach Pallet Forks (A47384)
Quick Attach...
1996 Chevy 2500 - Cheyenne Edition (A50515)
1996 Chevy 2500 -...
2021 FORD F-150 XL EXT CAB TRUCK (A51406)
2021 FORD F-150 XL...
UNUSED JCT QUICK ATTACH 84" ROCK GRAPPLE BUCKET (A51244)
UNUSED JCT QUICK...
EZGO (A50324)
EZGO (A50324)
 
Top