Sizing branch-circuit conductors. Branch-circuit conductors that serve a single motor must have an ampacity of not less than 125% of the motor's FLC as listed in Tables 430.147 through 430.150 [430.6(A)]. You must select the conductor size from Table 310.16 according to the terminal temperature rating (60ーC or 75ーC) of the equipment [110.14(C)].
Not sure what your getting at, you might have a smart (adjustable) breaker, or engineered overloads or some kind of electronic circuit protection... If your everyday motor is FLA rated at 40 amps, and you run it on 12awg, and put a 60 amp breaker on it... you MIGHT have a problem.... I was only illustrating that a motor might only run at 8A, but is a dynamic load. No load amps, Full load amps, locked rotor amps, inrush current.... Single phasing not withstanding.
Your wire should never be the weak link.