Super Star Member
Joshua, it doesn't matter what you are powering, it only matters that it is plugged into a receptacle mounted on the portable generator, and that the grounding terminal of the receptacle and the metal parts of the generator are bonded to the generator frame. Dave, a GFCI works by comparing the current in the hot and neutral wires. They must add up to zero. Say you only turn on your water heater. You would have about 20 amps going out one hot wire and the same 20 coming back on the other hot wire, with nothing on the neutral, so the sum is zero. If you only turn on a 120 volt light you may have 1 amp going out on a hot and 1 amp coming back on the neutral, with nothing on the other hot. The sum is still zero. Turn them both on: 21 out on one hot, 20 back in on the other hot, 1 back in on the neutral... you get the idea. If more than a few thousandths of an amp is unaccounted for in the three wires, something is wrong... current is going somewhere it shouldn't. When you connect your backfeed breaker to your 4-wire generator receptacle, you create a parallel circuit because the neutral and green wires are connected at both ends. Current divides in parallel circuits, so with the green connected, the currents in the neutral and 2 hot wires no longer add up to zero because of the current in the parallel green / white circuit you created. Current in the green wire is unaccounted for and interpreted as a ground fault.
Clear as mud?
The creation of the parallel circuit does make sense, thanks! All things being equal, half of the current in the neutral would be "missing" as seen by the GFCI.