Boy, that’s a hard one to answer. Ive seen some that were installed as well as a professional, and others that were....” what were they thinking”. I saw one air cooled unit installed in a garage with a vent cut into the wall. Death trap.What do you find to be the most over looked or unplanned items/expense/work that the DYI guys run into? Instead of having you do the install?
Mostly I see units installed too close to an opening of a house. Ive see a few installed with shed covers that were so low I couldn’t open the top of the generator. I went to one a few weeks ago that had a cover and sealed front to keep snow off of unit. I could not even get to the front opening to change the oil.
Electrically I see a lot with too small of wires run from generator to transfer switch. I had to replace a control panel on a brand new unit because homeowner ran all 6 control wires using red #12 THHN wires.... and got a few crossed. Shorted control panel... a nearly $500 mistake.
I replaced a starter on a new unit because homeowner kept trying to start unit over and over..... didn’t turn on the gas.
I always pour a concrete pad for my installs. I see lots of units sitting on gravel. These tend to sink here in Pacific Northwest. Unlevel units have issues with oil flow.not to mention it sucks to drain oil when motor is lower than drain pan.