This is why I really love this site-more collective knowledge that you can shake a stick at! :thumbsup:
My setup is a little bit different because I use n transfer switch external to the breaker panel, but the general implementation approach is the same as you are considering. My inlet receptacle is located in a detached workshop, and outside on the apron there I can run either a small Honda E2000i inverter-generator (120Vac only @ 2KW, but it sips gasoline) or a larger tractor PTO-powered generator head (120Vac/240Vac split-phase @ 10KW).:thumbsup:
Getting back to the OP's original question: You could "wire" your system for 50A., but currently use a 30A. breaker in the panel, with your current gen set. Then, if you get a larger gen set, you could replace the 30A breaker in the panel with a 50A.
With the future in mind, you might as well use 6awg wire and 50amp breakers.
Does anyone know whether I should be using solid or stranded wire or if it makes a difference in terms of code?
both rated the same, but more than likely youll only find stranded #6 wires. Solid #6 are quite unyielding to work with.
type THHN/THWN wire, which is stranded.Does anyone know whether I should be using solid or stranded wire or if it makes a difference in terms of code?
THHN/THWN are essentially insulation ratings. They do not specify solid or stranded. The "W" means wet as in it is suitable for installations where it may get wet, for example. You can find both types in solid or stranded, which mostly depends on size. Anything larger than 10 ga tends to be stranded. You can find smaller wires stranded as needed, but most house wiring is done with 14/12/10 ga solid wire.type THHN/THWN wire, which is stranded.
Home Depot or Lowes, in the electrical aisle.
Wrooster
Ok, heres the poop, at least for the Siemens brand interlock sets sold by my wholesale house.
NONE of their generator interlocks are UL approved. None.
Manual Transfer Interlock Kits
These interlock kits are used to interlock two main breakers in a load center or meter combination together so that both cannot be "ON" at the same time. This is required to prevent dangerous feedback between the two power systems. These kits work on most Siemens load centers and meter combinations.
Standard features
* UL listed for use in most Siemens load centers and meter combinations
* Suitable for use with optional standby systems in accordance with article 702 of the National Electric Code
* Corrosion resistant finish
* Easy assembly requiring no modifications to the load center or meter combination
* Remains attached to the main breakers when load center cover is removed