Generator question (household wiring to be more accurate)

   / Generator question (household wiring to be more accurate) #91  
Leedscase,
Thanks for the reply. 702 is the correct section for this discussion. User permitted to manually transfer load. Nothing prohibiting generator connection to subpanel, as long as you have manually tranferred from utility.
So both the OPs and Aarons cases meet code if they follow the correct procedures. Aarons case with the kirk keys makes it fool proof, does the same function as the sliding lock.

As i said before, i don't do this, but don't believe it is against code, if your AHJ agrees. I use extension cords from generator to the load.
 
   / Generator question (household wiring to be more accurate) #94  
Usually generator threads degrade into a pi$$ing contest over back feeding. Glad to see this one was different.
 
   / Generator question (household wiring to be more accurate) #95  
Usually generator threads degrade into a pi$$ing contest over back feeding. Glad to see this one was different.

Agreed.. and on that note I think I'll install a kirk key on my dryer plug and main breaker.... Should be ok right ???
 
   / Generator question (household wiring to be more accurate) #97  
Agreed.. and on that note I think I'll install a kirk key on my dryer plug and main breaker.... Should be ok right ???
Save your self some money and just pull the meter!

SR
 

Tractor & Equipment Auctions

2014 Ford F-550 Ext. Cab 4x4 Auto Crane 6406H 6,400 LB Crane Service Truck (A55788)
2014 Ford F-550...
2015 Hyundai Veloster Hatchback (A55758)
2015 Hyundai...
2011 Mack GU713 Granite Cooper TM-1882 18 Ton Crane Truck (A55788)
2011 Mack GU713...
UNUSED WOLVERINE ADB-13-1218R HYD AUGER (A54757)
UNUSED WOLVERINE...
2019 Bobcat 3400 4x4 Utility Cart (A55851)
2019 Bobcat 3400...
2021 FORD F-150XL CREW CAB TRUCK (A51406)
2021 FORD F-150XL...
 
Top