Generator question (household wiring to be more accurate)

   / Generator question (household wiring to be more accurate) #91  
Leedscase,
Thanks for the reply. 702 is the correct section for this discussion. User permitted to manually transfer load. Nothing prohibiting generator connection to subpanel, as long as you have manually tranferred from utility.
So both the OPs and Aarons cases meet code if they follow the correct procedures. Aarons case with the kirk keys makes it fool proof, does the same function as the sliding lock.

As i said before, i don't do this, but don't believe it is against code, if your AHJ agrees. I use extension cords from generator to the load.
 
   / Generator question (household wiring to be more accurate) #94  
Usually generator threads degrade into a pi$$ing contest over back feeding. Glad to see this one was different.
 
   / Generator question (household wiring to be more accurate) #95  
Usually generator threads degrade into a pi$$ing contest over back feeding. Glad to see this one was different.

Agreed.. and on that note I think I'll install a kirk key on my dryer plug and main breaker.... Should be ok right ???
 
   / Generator question (household wiring to be more accurate) #97  
Agreed.. and on that note I think I'll install a kirk key on my dryer plug and main breaker.... Should be ok right ???
Save your self some money and just pull the meter!

SR
 

Tractor & Equipment Auctions

2023 54' Hooklift Dumpster 15 Cubic Yard (A53422)
2023 54' Hooklift...
(APPROX 18) 2" X 6" X 68" TUBING (A54756)
(APPROX 18) 2" X...
Peterbilt (A51692)
Peterbilt (A51692)
2016 Ford F-550 Palfinger PSC3216 4,000LB 2 Ton Crane Service Truck (A54814)
2016 Ford F-550...
2005 NEW HOLLAND DC95WT CRAWLER DOZER (A51406)
2005 NEW HOLLAND...
2019 Caterpillar DP35N 7,000lb Diesel Forklift (A55851)
2019 Caterpillar...
 
Top