No inspections here other than when I had them pull the meter so I could add a service disconnect switch. That was $75 and took about two hours, most of which was waiting for the inspector to arrive. I only did that so I could turn power off and on as needed while doing other things so I wouldn't have to have them pull the meter more than once.
 
   / Generator Selection?
  • Thread Starter
#392  
Local dealer now says if they get to a self-install and find something that isn't right, they won't start it.

What kinds of things would make a dealer refuse to start one? I'd like some ideas of what they look at so I can be prepared.
 
   / Generator Selection? #393  
It has to be installed per code. Such as distances from gas source, window openings, etc. control wires all have to be correct. I have come upon jobs with burnt controllers...brand new units, where all black wires were run to controls. They crossed connected controls and burnt controller. I will not fix this under warranty. GENERAC should not have to cover costs because some idiot can’t be bothered to purchase colored wires.

incorrect gas piping sizes are another thing I see. People running 70 feet of 3/4” pipe to the natural gas meter and thinking the old 250cfm meter will supply the existing house and a nearly 400,000 btu generator. All these things will not let a generator perform correctly.
 
   / Generator Selection?
  • Thread Starter
#394  
There are no codes here. Gas supplier has seen the install and made no objections. I had specifically asked them about distance to the second stage regulator and they said they have no issue. They also said no problems at the tank end from the first stage regulator to the 3/4" underground. I got about 11.5 WC on the low pressure side of the regulator about 5' from the unit.

It's setting about 30" from the wall, maybe more. There are windows, but they should be at or beyond the 5' distance mentioned in the install manual. One issue might be the vents in the concrete block foundation, but I plan to cover those when it's running.

Cable is the special 10 conductor in the pictures above.
 
   / Generator Selection? #395  
Inspectors allow (at least here) you to seal a crawl space vent with a Permanent sheetmetal plate and silicon to prevent exhaust entering crawlspace. They do NOT allow someone to place a seal on an opening when unit is running. Again, this is an auto start unit. What happens when no one is around.
as long as the windows are 5 feet away, sounds good.
 
   / Generator Selection?
  • Thread Starter
#396  
I covered the vents with tin this morning.

This dealer isn't giving me a real warm fuzzy though. The guy I've been talking to hasn't been real good at returning emails and phone calls. He keeps telling me they don't stock any parts, yet they're the warranty service point for all of the retail sellers here including the big box stores. That just seems a bit off to me.

Now, he says he can't answer my last question until the service tech gets in later today.

I may scrap them altogether and start it myself if I don't start getting some better information.

I'm personally not at all concerned with clearances. I'm the only one ever here and I'll take whatever precautions are necessary when the time comes if it needs to run for any period of time. I've even planned on having a fan in the area to blow air away from the house any time it's running.

But I can't pay for a service call and have them refuse on a technicality.
 
   / Generator Selection? #397  
Warranty on air cooled does not require a service dealer startup. But if something fails on unit , free warranty may not be accepted if the failure was caused by improper installation.
 
   / Generator Selection?
  • Thread Starter
#398  
Rapidly losing faith in this dealer.

One guy quotes me a price on a battery (written , in email), but doesn't know what brand. I finally get the install tech (yes, only one apparently) on the phone and ask him about it. His price is double what the sales guy quoted, and he still can't quote a specific brand..

Tech asks for pictures, so I send him a few. Today, he says something about only seeing one cable and asks why I ran the control cables in the same tube. I tell him it's factory made that way for this application, all in one, rated for exposed runs. He claims he's never heard of that. 'We'll have to look that up and see the ratings.'

Some of the questions he asks make it seem like he's trying to apply commercial/manufacturing plant/heavy industrial criteria.


I'm not concerned with the electrical connections. I know all of that works. I've tested the transfer switch functions manually with a portable generator hooked into the E1/E2 lugs. What I don't know is if the SACM works and will engage the transfer when called for.

All I'm concerned with is that the engine starts and runs the first time. Things can fail out of box through no fault of the customer.

There are several points in the startup procedures that mention doing gas pressure tests at different times. I bought a manometer, but I'm not proficient with it.

It seems like a fairly simple procedure, but with many steps. I'd just rather have somebody do it that's done it before instead of my 'first time'. But I'm about tired of begging these guys and am wondering what will happen a year or two from now when something acts up.
 
   / Generator Selection? #399  
very odd. even if it wasnt an all in one cable, as long as control wires are rated at 600 volts they can run in same conduit as power legs. i cant believe they have not heard of 10 10 conductor cables. they have been out for many years.

is there any other companies near you to check with? Napa sells a group 26 battery. i stock Exide units myself.
 
   / Generator Selection?
  • Thread Starter
#400  
One other about 50 miles away, but they gave me some trouble too. Refused to even quote prices. Then they want a $125 travel charge regardless of anything else.

Supposed to be a third one according to the dealer locator, but they seem to be an HVAC outfit selling generators on the side. Not sure they even have service.


RK has a 26R battery for $52 but I don't know who makes theirs.
 
Last edited:

Tractor & Equipment Auctions

2015 HINO 195 16FT REEFER BOX TRUCK (A50505)
2015 HINO 195 16FT...
1500 Gallon Water / Chemical Tank (A50860)
1500 Gallon Water...
2018 Chevrolet Tahoe SUV (A50324)
2018 Chevrolet...
2025 K2010 UNUSED Chicken Coop (A50860)
2025 K2010 UNUSED...
2007 MAGNUM GENERATOR TRAILER (A50854)
2007 MAGNUM...
2017 Kia Soul Hatchback (A48082)
2017 Kia Soul...
 
Top