There are many ways that work. You must have a check valve between the pump and the pressure tank. Most pumps have one built in. You can share a pressure tank between two location, but the far location will have all its demand satisfied by the tank when the pump is not running so bigger pipe will improve performance. With pressure tank at both locations, local tank satisfies local short term demand and flow from other tank will balance both to same pressure. 20 minute shower will cause one or two pressure tanks to empty and performace will depend on pipe diameter. If you run pressure tank on at 40 and off at 60 psi, and you want minimum of 25 psi at shower head, decide shower head size .. flow rate....only one at a time ?.... and see pressure drop for various pipe diameters. Water softeners are pressure robbers. Also dual location pressure tanks absorb water hammer. 100 feet of water flowing and the washer or dishwasher solinoid valve closes, you can get pipe rattle or worse as the water stop suddenly.
I have 1" poly pipe and 60 feet between location with pressure tanks at both locations. I recommend sizing pipe for full pump output at either location and no more than 5 psi drop at max flow. My $.02
Just ran example at calc web site. 10 gal per minute is 3+ psi drop for 100 feet of plastic pipe. 1.25" is 1psi drop.
Pressure Drop: Calculation of pressure drops in pipes
I have 1" poly pipe and 60 feet between location with pressure tanks at both locations. I recommend sizing pipe for full pump output at either location and no more than 5 psi drop at max flow. My $.02
Just ran example at calc web site. 10 gal per minute is 3+ psi drop for 100 feet of plastic pipe. 1.25" is 1psi drop.
Pressure Drop: Calculation of pressure drops in pipes