Had to jump in on this, One thing not mentioned is rodents, with the wire direct buried the gophers think its some juicy root and gnaw on it and cause it to leak to ground, or just plain blow up wire and themself. I have had this happen 3 times on an 1100' run to my well, very tough to trace out. I wish I had put it in conduit now, but at the time I thought it was ok 2' deep. Also what is important in sizeing the wire is the voltage drop, it should be 3% or the wire will overheat, for long runs the resistance of the wire must be taken into account. to get 20amps at the end of 200' run without overheating wire you would need to use #6 thhn, for 50amps #2 both copper. also running romex in conduit is a no no because of the overheating. Motors can run on a higher voltage drop because of there intermitent use,3% voltage drop is for general purpose,lighting loads. A 50amp sub is the way to go most of the time,compressors,welders,saws,etc. Also very cheap ($15 home depot) considering time and effort