Cat driver, did you suck a bag through or just tied a bag tie to the string?
My question is, I've got the choice where the transformer will be, just a minimum of 15' and maximum of 200' from the structures. Where should I put it? Should I stick it between the house and barn to minimize the secondary run or put it 100' or so away from everything?
Even thou they eliminated pcb oil along time ago, they still have over 50 gallons of oil. The primary gushing sometimes expand and blow out so keep it away from your well.
The transformers used around here to step down underground primary voltage aren't big enough to hold 50 gallons of oil even if the housings were filled with nothing else. That said, I'd be looking for 50'-75' of separation from the transformer to any structure.
All new construction for primary distribution and transmission is aluminum or acsr which is aluminum with a steel strand, that's underground and overhead, all residential secondary services that are installed by power company's are gonna be aluminum, if it's a copper service it's probably commercial that has been paid for by the customer. Aluminum services are not as good as copper but if installed in conduit most have a life expectancy of over 30 years.Since Rick-B is semi/anonymous too. Transformers come in many types and sizes..not all are underground....I would just allow a good distance, from structures and wells.. Wire is not cheap, but please don't use Aluminum type. Many will try to save on the initial cost, it just is not worth the risk...And Yeah , a lot of the primarys are aluminum. So there is 2 more cents.
My question is, I've got the choice where the transformer will be, just a minimum of 15' and maximum of 200' from the structures. Where should I put it? Should I stick it between the house and barn to minimize the secondary run or put it 100' or so away from everything?
I'll be doing this same project in a few weeks, going 2000' from the road to a pad mount transformer for a new house and barn. I dig the 48" deep trench and the rural electric company takes care of everything else (conduit, junctions boxes, etc.). Luckily, I'll mostly be going through top soil (northeast OK).
It'll run from the pole at the county road, along the north side of the driveway easement, but then what? I'll also be running water along the same length, with 1' horizontal and vertical separation requirements. I'll put the electric trench closest to the driveway and the water line trench just north of that.
My question is, I've got the choice where the transformer will be, just a minimum of 15' and maximum of 200' from the structures. Where should I put it? Should I stick it between the house and barn to minimize the secondary run or put it 100' or so away from everything?