LOOONNNGGG Underground Cable Run

   / LOOONNNGGG Underground Cable Run #51  
I noticed where someone earlier recommended you to use sch 80 90's on the ends of your long pulls and I am not saying that that is a bad idea but if you don't bevel the inside lip of the pipe you are going to have a heckuva ridge inside the pipe that can do some serious damage to the conductor, at least on one end anyway as you will be going against the coupling on one end or the other. A large beveled mill bastard file will do wonders to the inside lip of the pipe.:thumbsup:
 
   / LOOONNNGGG Underground Cable Run #52  
Best method of install a pull line is blowing it thru with sponge or industrial vac sucking it. Most of the time it is poly and looks like binding twine. Previous poster showed a bucket of it.The second line looks like ski rope for water skiing, and best is poly, but we have used nylon..We have never pushed a line while installing and glueing.

I have pushed a fish tape and used a "mouse" to pull fish line. Skip the feeding the line as you lay the pipe and just pull it with a large shopvac, or a leaf blower that does suction. If you use the poly pullstring as suggested, it will take about 15 minutes to pull the whole run. WELL worth it IMO.

Aaron Z
 
   / LOOONNNGGG Underground Cable Run #53  
Wow, I just enjoy reading this thread and all the knowledge shared. I have a similar project (not as long of a run) and will definitely consult what I've learned here!
 
   / LOOONNNGGG Underground Cable Run #54  
Whoops! Some other issues and comments I neglected to address in my last reply:

Conduit length and orientation:
To be clear, my conduit sticks will be oriented male end to female bell end, in the direction of the cable pull (from power pole to my transformer pad), to prevent extra friction at join points when running line and pulling cable.

Checked with my electrical supplier: I will take advantage of using 20' sticks of the 3" Sch40 PVC elec conduit that PowerCo spec'd, in order to reduce the number of cemented joints. I will be happy to prime and glue to get a good seal. This is not a job I want to do twice because I was compelled to save.. what? 10 seconds on a joint on an epic underground run...

Where did the 240V drop over 1500' run concerns come from?

I might have used a poor choice of words or misused terminology (thought I wrote 'primary feed' from nearest pole) in my original post. Apologies if I used improper language. Somehow a few concerned folks seemed to get the impression that I planned to take a 240V feed from the nearest pole's transformer, run it 1500 feet underground, and through some miracle of physics end up with a 600A primary service feed at my end, apparently with negligible voltage drop. I'm not exactly sure how we got from wondering about the best way to feed pull line through a long conduit run, (one rope? multiple sections?) to Ohm's law and figuring voltage drop on 240 volts over 1500 feet. I apologize for the confusion I somehow created.

The nearest utility pole supplies power to my neighbor's 1BR cabin which is 1/4 mile from the state road. PowerCo poles supply high voltage overhead then a line drops to a pad mount transformer on the ground. Transformer feeds the cabin with 200A / 240V primary service. Boy, if I can just figure out how I to pull a 240V secondary feed off that transformer, run it 1500 ft underground in plastic pipe, and end up with a 600A / 240V service at the other end, I'll forget the tree farm, invest in a trencher and all the conduit I can afford, and start my own power company. :laughing:

Kidding aside, the plan is for PowerCo to drop high voltage from the pole to the buried pipe (leaving neighbor's transformer alone) and run high volts underground to a pad mount transformer 1500 ft up the hill, leaving ample juice for the transformer to supply 600A / 240V to my non-residential service entrance and distribution point. That's what the PowerCo engineer and I have agreed upon.

So, what's your plan for the pull line now?
The engineer who will be on site to surpervise the PowerCo installation said 1/4" polyvinyl rope would be fine. They use it to pull their own line for the actual cable pulling task. Said a continuous length wasn't required for that as long as I could tie a clean splice knot that wouldn't unravel when pulling their line. That makes things easier--I am an old rock climber who hasn't forgotten ropecraft.

Since I won't have to work with a big 1000' spool of line, I'm inclined to do this one-time job using 100' or 150' lengths of the 1/4" poly the PowerCo engineer spec'd, stringing a few 20' sticks at a time on grade using the "monkey-wrench weight" method suggested here to thread each stick in order, and then carefully glue each threaded section on (being sure not to slop adhesive past the bell where it could foul the line) and splice knotting the ropes as required. It sounds less elegant and less efficient than pulling a mouse through with twine line and a shop-vac, but I the brute-force simplicity appeals to me for this one-off job. I can be careful with the glue, and if a little primer gets on the rope, it won't hurt. If I grow weary of repetitively pulling 100' lengths of rope through 2 or 3 sticks at a time, I can try the suction / mouse method on the 1000' length that follows the spec'd junction box at the 500' mark. I've got a 3500W generator that fits nicely in the loader bucket of my DK40SE and I bet the shopvac will fit as well. Then I'd use the threaded twine to pull the 1/4" poly rope PowerCo requested.

I've got one more walkthrough with the installation engineer before I order the conduit and schedule the trench work. I'll get the final details I'll need to submit for my county permit (and plan for trench inspections before backfillng, if required in my county). Thanks for all the great suggestions to consider, gotchas to watch out for, and I'll be sure to verify that my trench man's equipment can meet the depth *and* width specs that PowerCo requires.

Thanks for the generous feedback so far, and don't hesitate to point out any logic flaws, bad assumptions, continuity gaps in procedure, or just stuff that I've said that doesn't make sense. I'm very grateful for those willing to offer help and tactical advice. I appreciate every bit of time you folks have donated to try and help me do this right so I don't have to do it twice.

-Chip
Robiefield Mountain Farms



















-A couple of things come to mind here
working with your conduit.


First build a simple light weight work table that you can
slide along the trench with the tractor on skids with
using 2 by 6's and using a plywood top.


The table can be three feet wide and foor feet high, I am getting there!!

Now purchase 4 Ridgid or Reed pipe vises with the open sides to create conduit clamps to mount on the table.

one pipe clamp will free both hands and allow proper cleaning and glueing of the joints.

The second pipe clamp will hold either the male or bell end securely while spinning the free piece of conduit to set the glue.

The third pipe vice will help center the third piece and allow you to clean and glue the other end which is locked in the vice.

Making a narrow table you can pull with the tractor to connect 2 or three joints together at one time will save you work and allow you to put conduit under the table top to use as you move along.

The area under the table top can store the supplies and couplers if you need to cut a bell end and replace it with coupler splice.

You can simply lower the pipeline on the ground as you connect it and then use the shop vac and a hand full of shopping bags ties together and suck them through from one end to the other BEFORE you lower the pipe in the trench.

Its easy to make a pipe roller to lower the conduit in the ground as it lies along the trench using a few small pneumatic tires making up a sling roller to lower the conduit in place with low stress on the conduit (its the same way pipeline is laid in a lot of places.


So in doing it this way you have the work right in front of you and you can control the pipe while spinning it to set the glue and simply lie it on the ground for the running of the twine and suck the grocery bag wad through after you check for leaks at the joints by listening for an air leak squeal by capping the far end temporarily.


We used a pair of pipe vices on a small table to splice 4160 with 3 conductors, 2 grounds, and a continuity line and heavy 480 trailng cable and it was a godsend.


I would build 2 16-foot tables and bolt them together end to end, add the lower shelf to store pipe joints, glue and cleaner and it keeps the pipe clean too.

Using 4 pipe vises would gove you even better control with the conduit if you used both 10 and 20 foot pieces or simply make it 40 feet long to work with 4 10- foot pieces or 2 20-foot pieces at one time and simply splice and move along after you are sure the glue has set.

If you pre-glued two or 4 joints together and slid them under the table top the gluing job will go even faster for you and lowering the conduit in the trench can be done with the tractor supporting the pipe sling as it advances along the conduit with no issues of stressing the conduit as it is all one piece now.

So in this way you can glue 48 pipe sets together using the pipe vices on the bench to get ready and have 40 foot joints under the work table ready to glue together using the 4 pipe vices on the tabletop along the trench.


Once you have the pipe vices on the table top the gluing will go quickly for you and then you can lower the conduit in the trench later after you suck the bag wad through with the twine then your pull rope later with a little cable lube.

You can glue 10 foot conduit joints quickly the same way and it will not be tedious as you wil have the pipe vices to hold it fast while spinning on the new piece.


As far as the twine zip line goes you can simply use an electric drill and coffee can to wind the twine through and then the pull rope, no point in making it harder to do with a cable spool at both ends winding it up by hand.
 
   / LOOONNNGGG Underground Cable Run #55  
-A couple of things come to mind here
working with your conduit.


First build a simple light weight work table that you can
slide along the trench with the tractor on skids with
using 2 by 6's and using a plywood top.


The table can be three feet wide and foor feet high, I am getting there!!

Now purchase 4 Ridgid or Reed pipe vises with the open sides to create conduit clamps to mount on the table.

one pipe clamp will free both hands and allow proper cleaning and glueing of the joints.

The second pipe clamp will hold either the male or bell end securely while spinning the free piece of conduit to set the glue.

The third pipe vice will help center the third piece and allow you to clean and glue the other end which is locked in the vice.

Making a narrow table you can pull with the tractor to connect 2 or three joints together at one time will save you work and allow you to put conduit under the table top to use as you move along.

The area under the table top can store the supplies and couplers if you need to cut a bell end and replace it with coupler splice.

You can simply lower the pipeline on the ground as you connect it and then use the shop vac and a hand full of shopping bags ties together and suck them through from one end to the other BEFORE you lower the pipe in the trench.

Its easy to make a pipe roller to lower the conduit in the ground as it lies along the trench using a few small pneumatic tires making up a sling roller to lower the conduit in place with low stress on the conduit (its the same way pipeline is laid in a lot of places.


So in doing it this way you have the work right in front of you and you can control the pipe while spinning it to set the glue and simply lie it on the ground for the running of the twine and suck the grocery bag wad through after you check for leaks at the joints by listening for an air leak squeal by capping the far end temporarily.


We used a pair of pipe vices on a small table to splice 4160 with 3 conductors, 2 grounds, and a continuity line and heavy 480 trailng cable and it was a godsend.


I would build 2 16-foot tables and bolt them together end to end, add the lower shelf to store pipe joints, glue and cleaner and it keeps the pipe clean too.

Using 4 pipe vises would gove you even better control with the conduit if you used both 10 and 20 foot pieces or simply make it 40 feet long to work with 4 10- foot pieces or 2 20-foot pieces at one time and simply splice and move along after you are sure the glue has set.

If you pre-glued two or 4 joints together and slid them under the table top the gluing job will go even faster for you and lowering the conduit in the trench can be done with the tractor supporting the pipe sling as it advances along the conduit with no issues of stressing the conduit as it is all one piece now.

So in this way you can glue 48 pipe sets together using the pipe vices on the bench to get ready and have 40 foot joints under the work table ready to glue together using the 4 pipe vices on the tabletop along the trench.


Once you have the pipe vices on the table top the gluing will go quickly for you and then you can lower the conduit in the trench later after you suck the bag wad through with the twine then your pull rope later with a little cable lube.

You can glue 10 foot conduit joints quickly the same way and it will not be tedious as you wil have the pipe vices to hold it fast while spinning on the new piece.


As far as the twine zip line goes you can simply use an electric drill and coffee can to wind the twine through and then the pull rope, no point in making it harder to do with a cable spool at both ends winding it up by hand.

I usually glue it together along side the trench and roll it in on sections and prop it up on a 4x4 across the trench to keep the end up at a working level.

tom
 
   / LOOONNNGGG Underground Cable Run #56  
Hello Tommu56,

I hoped I did not complicate the issue; I was not sure how he was set up with any help and how much dirt he had to deal with as far as useable work area and that is why I suggested the table with the joint carrying shelf under it and the pipe vices:thumbsup:


_________________________________________________________________
Once you go flail you never go back:thumbsup::licking::drool:
 
   / LOOONNNGGG Underground Cable Run #57  
I must admit, I've done quite a bit of this stuff before and I'm still getting new ideas from this forum. I especially like the table with vices idea! It's not worth it for small jobs, but when you're doing more than a quarter mile and a hundred lengths of pipe, building a movable jig becomes worth the investment and makes the job faster and easier. Great suggestions, especially if you've got to do this alone.
 
   / LOOONNNGGG Underground Cable Run #58  
Hello Tommu56,

I hoped I did not complicate the issue; I was not sure how he was set up with any help and how much dirt he had to deal with as far as useable work area and that is why I suggested the table with the joint carrying shelf under it and the pipe vices:thumbsup:


_________________________________________________________________
Once you go flail you never go back:thumbsup::licking::drool:

I should have elaborated better I stay in one place as much as possible
glue it on the side of the trench and slide pipe away from work area continuing until I cant push the pipe any more.

We have used a farm wagon just like you are saying with all the supplies on it and keep moving along working on the wagon a real back saver!

tom
 
   / LOOONNNGGG Underground Cable Run
  • Thread Starter
#59  
I can't express my gratitude enough for the invaluable sharing of experience and advice on this matter. I'm also glad I'm not the only one getting use out of the experience of others.

I said I'd provide updates on the progress and share the good, the bad, and the ugly.

Well, I'm saving all this information in a very safe place. 'Cause the wheels came off. In a big way. And it's my fault.

I went to great pains to be sure I met every requirement of PowerCo, and it's quite a maze, but I did it. Triple checked.

I also thought I had all the county rules, permits, and inspections in hand. I really did. You know where this is going, don't you...

The project is off. Probably be a bit until I try again. Now, there was no requirement for one of the PowerCo engineers to go have a chat with the county inspector about structures on my land that were totally outside of the scope of the electrical service work and contract... but it happened. And rules are rules.

I won't go into much detail. You can figure out enough anyway. County won't look at the elec service drop permit for my well until I get... a couple of other permits. My boondock RV needs anchor straps and a temporary residence permit. The outhouse needs a health permit. Stuff like that. Gee, that PowerCo guy was a real sweetheart for doing that, wasn't he? But... rules are rules. And I'm 100% accountable for everything, so it's my fault. Gotcha. Time to man up.

None of the advice will be wasted. I'll still be doing the same run. I've just decided to wait until I've started the house and office construction so I qualify for residential power, which will actually save me a little over $10k due to the differences in PowerCo customer class fee structures.

I gotta pick my battles. Wrong time for this one. Come back to it in a coupla years. Reworking the project plan. It won't be the last time I have to do that either, I bet. All part of the process.

Thanks for all the help. I think I'll be building those tables for the job, too. I like that idea a lot. This thing is doable, but it really needs planning and preparation to be exactly right. Close won't be good enough. Ouch, OK, get over it, learn from it, get your head right, son, and move on.

Plenty to do. Work never ends on the farm.

-Chip
 
   / LOOONNNGGG Underground Cable Run #60  
I've pulled 1,500 ft. 3 wire and I hooked one end up to a tractor and started driving. I had a guy at the other end with cable lube. I had three turns and never had a problem.

When I drove as far as I could I backed up and reconnected and drove again. Did that till I saw wire.

To get the rope to me I put a shop vac on one end and a plastic bag ties with a string on the other. She sucked the bah through the pipe in no tome. Then I pulled a bigger rope through and was good to go pulling the wires.

Sometime we over think things. It really was as simple as that.
 

Tractor & Equipment Auctions

2012 CHEVROLET SILVERADO SINGLE CAB TRUCK (A51406)
2012 CHEVROLET...
6 Yard Commercial Dumpster (A51691)
6 Yard Commercial...
(1) 12ft Tarter Gate (A51573)
(1) 12ft Tarter...
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
2007 Ford E-450 Super Duty 16ft Portable Office Truck (A51692)
2007 Ford E-450...
JOHN DEERE XUV590M (A53084)
JOHN DEERE XUV590M...
 
Top