Pole Barn Insulation and finishing questions.

   / Pole Barn Insulation and finishing questions. #1  

lowerthanu

New member
Joined
Jun 2, 2007
Messages
9
Hey guys,

I have been a member here for years and always just have read other posts, but now have a question I need your advise on. I just bought a new house that has an existing 30x60x9 Cleary pole building on the property. It is only a few years old and in great shape. I am working on finishing it to make it my shop. Right now it is a bare building with a dirt floor. Next week I have concrete going in with full insulation under it and tubing for in floor heat. My question is regarding insulation. I have been reading up on it for several weeks on various forums and have come to the conclusion that everyone has a different opinion on how to do it.

I live in Minnesota where it gets hot in the summer and below zero in the winter. The building will be heated 24/7 via in floor heat in the winter and it will have air conditioning that will be used periodically in the summer. From what I understand spray foam insulation is the best way to go. I got a quote on it for $8500 for 2.5" in the walls and 3" sprayed on the underside of the ceiling. This is more than I am willing to spend so looking at the alternatives. Here is my game plan.

Frame out between the posts to run R19 5.5 thick" faced (so I can staple into place verticallly) bat insulation in the walls with a vapor barrier towards in inside of the building and sheeted with steel. The inner wall framing will give approximatly 1.5" of clearance between the exterior steel and the insulation. A few questions regarding this. I have heard some people talk about putting tyvak house wrap stapled on the girts and poles to block condensation from coming in contact with the insulation but allowing the interior of the walls to breath. Any thoughts on this?
Also some people have talked about putting 1.5" pink foam between the girts covering the exterior steel? Is this necessary or a worthwile idea?

For the ceiling I intend to put a vapor barrier up, then steel and have blown in insulation done on top. This seems like the best way to go, but my question is on venting. The building has no soffits on any side as there is no overhang. The roof has 2 8.5' long ridge vents on it. The gable wall runs up inside the trim so there is some air movement but no vents. My question is will this be enough venting or do I need to add a gable vent on each side, or is there something else I should do?

Thanks in advance and sorry for the lengthy post.
 
   / Pole Barn Insulation and finishing questions. #2  
I don't know your post spacing but I have two bulidings where 6" thick rolls of fiberglass 7 1/2 feet wide were used. Takes a couple guys to handle to put up. Sure beats studding or patching in 24" wide rolls.

Around here you can also get loose fiberglass blown on the walls that has glue added and it stays in place, then you cover it how you want.
 
   / Pole Barn Insulation and finishing questions. #3  
You're in a climate where condensation can be a problem, particularly if you're going to air condition. You need to make sure that air infiltration is stopped from moving into the insulation cavity. If they had put up tyvek or tar paper when they did your siding that would be a good barrier. But if it's just bare metal you will be getting a lot of air migrating through. That's one advantage of foam, it creates an air barrier. You could use foam board and foam it along the edges. Downside is foam board is really expensive. You're on the right track with the ceiling putting up a continuous vapor barrier to stop air from moving into the attic.

I'd put up a solar powered fan on the roof and a few vents on the gable end. They make fans really compact now, the panel is built right on top of the fan shroud. You can also put a few vents on the roof down low since you don't have soffit vents, but in your climate you'll have to protect them or the snow and ice will damage them. You can put an icebreaker above them to make sure they survive. The more ventilation up there the better.
 
   / Pole Barn Insulation and finishing questions. #4  
I have had many pole barns, insulated myself ( I'm Cheap) I got the silver backed 4x8x 1.5" sheets foam board, cut them to fit between the 2x4 slats to make everything flush, then put an additional layer of 1.5" top to bottom between the 6x6 posts, 3" total insulation then put up 1/2" osb board and screwed through everything into the original 2x4 cross slats. Ceiling I put furring strips 16" on center and did same with 4x8 sheets. I've done this in 3 different pole barn shops, 40x80x14'H , 30 x 50 x 14'H , and a garage 24x30x12'H , North east PA ( pocono's) can get very cold in the winter and my propane hanging furnace does a nice job keeping it warm. Summer as you can get hot, in the morning the inside willbe nice and cool and hold the coolness untill you open the doors. I did the whole 30x50 start to finish myself for under $3500. Iwould recomend going with the 1.5" to make the slats flush and second layer 2" , the 1/2 osb will add an "R" factor so total you'll have 4" insulation, no problem even where u are at.
 
Last edited:
   / Pole Barn Insulation and finishing questions.
  • Thread Starter
#5  
Thanks for the reply's. Anyone else have input?
 
   / Pole Barn Insulation and finishing questions. #6  
Thanks for the reply's. Anyone else have input?

I have a Morton building and suggest you go to their website to view how they insulate their building. I had them build my building but insulated myself. Here is the insulation that I bought from them. I installed it myself and it fits perfectly between the posts. A couple other pictures (not very good ones) showing the insulation installed. Hope this helps! It certainly makes a difference with the cold. When I get the funds I will have blown in insulation done in the ceiling. Questions feel free to ask. Stanley
 

Attachments

  • SCAN0002.jpg
    SCAN0002.jpg
    908.8 KB · Views: 3,748
  • SCAN0001.jpg
    SCAN0001.jpg
    445.9 KB · Views: 4,970
  • 100_2280.jpg
    100_2280.jpg
    75.5 KB · Views: 3,619
   / Pole Barn Insulation and finishing questions. #7  
NOTE: The blue styrofoam board was used for another project. I just had it leaning against the rolled insulation.
 
   / Pole Barn Insulation and finishing questions. #8  
I've just finished insulating the walls of a pole barn that's about 30 years old. I was able to find some used polyiso roofing insulation sheets. I layered it into the walls, sprayed some "Great Stuff" into any cracks, then covered it with 4 mil plastic as a vapor barrier and finished with OSB and paneling. I was going to use metal liner panels, but I went with OSB to save money and make it easier to mount things on the walls. I think the walls are about R-30 now at a reasonable cost.

The used polyiso is available from roofing companies around here periodically. 4x8 sheets, 1.5 or 2 inches thick, usually go for about $5 each.

I put horizontal nailers between the poles on the inside at about 4 foot spacing. I ran wiring in the walls before I insulated, but if I had to do it again, I would run the wiring in conduit on the surface. I spent way to much time fitting around wiring and boxes.
 
   / Pole Barn Insulation and finishing questions. #9  
I am just now finishing a 30x60 pole barn with 14' ceiling.

In preparation for insulation I wrapped the buiding with tyvek prior to putting up the metal. Wind infiltration and also water leaks should be kept at the metal and not enter into the insulation within the wall this way. You can install tyvek after the fact by wrapping it around the inside of the posts and stapling it to the wall girts.

I plan to frame between the posts and install regular batt FG insulation, cover with plastic and then fire code sheetrock. This is the cheapest way to do it and the framing will give you lots of oopportunity to mount electrical devices, cabinets, shelves, workbenches, etc. and make the wall stronger. The framing is a good thing.

The attic will be done as you describe, add 24" OC ceiling joists between the trusses and attach something to that. Blown in FG or cell above.

Spray foam has some benefits but they do not justify the cost if you have other choices. Sometimes spray foam is the only choice.

Oh and I did the radiant tubes as well, 1800 LF on top of 2" EPS 25 psi foam. Don't let anybody tell you that you must use XPS foam, contact the manufacturer for the facts.
 

Attachments

  • shop12-1-11.jpg
    shop12-1-11.jpg
    244 KB · Views: 8,920
  • IMAG0285.jpg
    IMAG0285.jpg
    446 KB · Views: 5,805
  • shoptube.jpg
    shoptube.jpg
    202.5 KB · Views: 6,320
   / Pole Barn Insulation and finishing questions. #10  
Hey guys,

I have been a member here for years and always just have read other posts, but now have a question I need your advise on. I just bought a new house that has an existing 30x60x9 Cleary pole building on the property. It is only a few years old and in great shape. I am working on finishing it to make it my shop. Right now it is a bare building with a dirt floor. Next week I have concrete going in with full insulation under it and tubing for in floor heat. My question is regarding insulation. I have been reading up on it for several weeks on various forums and have come to the conclusion that everyone has a different opinion on how to do it.

I live in Minnesota where it gets hot in the summer and below zero in the winter. The building will be heated 24/7 via in floor heat in the winter and it will have air conditioning that will be used periodically in the summer. From what I understand spray foam insulation is the best way to go. I got a quote on it for $8500 for 2.5" in the walls and 3" sprayed on the underside of the ceiling. This is more than I am willing to spend so looking at the alternatives. Here is my game plan.

Frame out between the posts to run R19 5.5 thick" faced (so I can staple into place verticallly) bat insulation in the walls with a vapor barrier towards in inside of the building and sheeted with steel. The inner wall framing will give approximatly 1.5" of clearance between the exterior steel and the insulation. A few questions regarding this. I have heard some people talk about putting tyvak house wrap stapled on the girts and poles to block condensation from coming in contact with the insulation but allowing the interior of the walls to breath. Any thoughts on this?
Also some people have talked about putting 1.5" pink foam between the girts covering the exterior steel? Is this necessary or a worthwile idea?

For the ceiling I intend to put a vapor barrier up, then steel and have blown in insulation done on top. This seems like the best way to go, but my question is on venting. The building has no soffits on any side as there is no overhang. The roof has 2 8.5' long ridge vents on it. The gable wall runs up inside the trim so there is some air movement but no vents. My question is will this be enough venting or do I need to add a gable vent on each side, or is there something else I should do?

Thanks in advance and sorry for the lengthy post.

You do need a vapor barrier between the metal wall and the insulation. You should also seal the bottom of the metal and the concrete contact. Too keep critters out. I would add a power vent that comes on at a set temperature.

I finished my pole barn with R-19 insulation the Vapor barrier and the power vent and never had a problem. We built living quarters in the barn while the house was being built. We had a second floor bedroom that got a little warm in the summer. The Vent took care of that. The interior is finished with plywood and is now my shop.
 
   / Pole Barn Insulation and finishing questions. #11  
I have a 40x81 Cleary building. I am sure your posts are 9 feet on center. I did not insulate the ceiling at construction. I should have. It "rained" from condensation off the ceiling on certain days.
I was fortunate to find 3500 sq feet of 4x8 sheets of 3 inch thick foam for $300. I cut them to size and placed them between the nailers of the ceiling. Alot of work but little expense. Not sure how well it will work but that is what I did. If it does not I am not out much.
 
   / Pole Barn Insulation and finishing questions. #12  
I was fortunate to find 3500 sq feet of 4x8 sheets of 3 inch thick foam for $300.

Are you sure you weren't wearing a mask and carrying a gun? I recall last time I bought a 4x8 sheet of 3" pink foam it was about $30, which means the new cost of your purchase was about $3000.
 
   / Pole Barn Insulation and finishing questions. #13  
I spent 24 years in the home and farm construction business. Here's what I did on my own. I'm in northern Iowa. I made a 30x40x14 heated shop on one end of a 40x75x14 Astro building as follows.
Poured a 5" floor with 8" deep "rodent trench" at the perimiter. Installed 2 drains in the floor by digging a hole 4' deep and setting 18" concrete tiles on end and sloping the concrete to these. They drain all water when washing vehicles. Made steel lids for them.
Installed an insulated 9x7 door on the exterior wall for small vehicle use. Nice thing is my good pickup (4wd) sits inside a nice heated shop all winter, only taken out during snow storms when the old pickup (2wd) can't get through the snow.
I built a 2x6 studded wall on the open end, unsulated and covered both sides with steel.
The posts are 7.5 ft on center, so I laid 2x4's on edge between them 2' on center, secured to posts with joist hangers. Installed R19 kraft faced insulation between 2x4's. Covered with steel. Contrary to belief, you don't need or want a vapor barrier on the outside of the insulation- this will trap any moisture in the wall (not good). The moisture will be on the heated inside of the building, wanting to migrate out to the cold dry air in winter, thus the vapor barrier needs to be on the heated side of the wall, just like a house is built. Tyvek is not a vapor barrier- it's a wind barrier, but is similar to GoreTex that will let moisture through from one side. If you do a good job of insulation installation, you don't need a wind barrier, but to each his own. It (Tyvek)won't hurt anything, if installed the right way (label OUT).
I ran my electrical in the walls before I insulated, and mounted the boxes on the face of the walls. If I had to do it again, I'd put the wiring in conduit on the face of the walls.
For the ceiling, I put 2x4's between the bottom chord of the trusses, 4' on center, secured with joist hangers. I always told my customers use caution doing this, as the truss should be made for a ceiling load, but this building was built 25 years ago, and it's the only one I have with a 14' ceiling. Need that for combine clearance. I installed a 4 mil poly vapor barrier to the ceiling before putting steel on the ceiling.
I then blew 18" of cellulose insulation on top of that, and covered the truss with plywood to seal it up from birds, etc.
I then built a 20x14 sliding door for the end, high density foam insulation, outside covered with steel. This door opens into the unheated portion of the building, so it gets no wind at it unless the big sliding door on the unheated end of the building is open to the outside.
I've had this for 11 years now, and spend most of my time out there. Built most of my gadgets out there during winter- snow pusher for loader tractor, pallet fork for loader tractor, hydraulic tree puller, towed yard and garden cart, and about a thousand other small things, as well as work on farm equipment.
Hope this helps, and sorry about the long post.
I use forced air as a heat source- a used furnace out of a house.

Edit: Forgot to mention, the poly in the ceiling is necessary with cellulose. It keeps the cellulose off the steel. Cellulose contains a salt/sodium that will rust steel if moisture migrates or condenses between the steel and insulation.
 
Last edited:
   / Pole Barn Insulation and finishing questions. #14  
how did you do it so cheap where did you get your metal? if you can let me know so i can get some im building a 40x40x14 and dont have much money to play with so im looking for the best way to build i already have the post and the 2x4 around it i still need trusses and the metal thanks for your help john.bolesjr @ yahoo . com
 
   / Pole Barn Insulation and finishing questions. #15  
IMHO, spray foam is the only way to go in a pole building if you can afford it. Being that pole building steel has ribs, there are tons of places for air and critters to infiltrate. Spray foam seals everything up, adds rigidity and sound proofing. Don't bother putting any foam on the underside of the ceiling unless you don't have a vapor barrier. If you don't have a vapor barrier on the ceiling then foam is pretty much a must. If you have a vapor barrier, then its way cheaper to have cellulose blown in on the ceiling. I'm in Minnesota and with no heat my building is about 20 degrees warmer than the outside temperature. Its super easy to heat and keeps cool in the summer. I love the foam.
 

Marketplace Items

2020 MACK PINNACLE (A58214)
2020 MACK PINNACLE...
2008 DOOSAN G25 GENERATOR (A55745)
2008 DOOSAN G25...
Crown RM6025-45 4,500 LB Stand-On Electric Forklift (A59228)
Crown RM6025-45...
2003 International 7400 T/A Heil 12 CuYd Dump Truck (A55853)
2003 International...
Unused 2025 CFG Industrial H15R Mini Excavator (A59228)
Unused 2025 CFG...
UNUSED FUTURE FT-72-72" HYD MULCHER (A60432)
UNUSED FUTURE...
 
Top