PTO Generator inadequate for larger HP motors?

   / PTO Generator inadequate for larger HP motors? #101  
Correct, a 2HP or larger motor with a PTO gen.
Depends on the size of the generator. I have 16 kW generator I used on my farm, it will start and then run three 3 hp motors and three 1 hp motors.
 
   / PTO Generator inadequate for larger HP motors? #102  
I got a lesson last week. Our volunteer fire chief has had a long range goal: In his life he wants the fire house, shared by two very small towns to be an emergency shelter for all of the townspeople. His vision included a giant generator big enough that everybody in town could bring any load they could imagine. After 20 years of him asking me to calculate a generator installation of 50, 100, 85, 200 killowatts, he found a donor willing to pay for the full price of a realistic generator. We chose a 14 KW generator. Biggest load we calculated was a 5000 Watt air compressor. My air compressor starts fine on my 10 KW generator, so I expected no problem with a 14 KW machine.

We found the run capacitor bad. Replaced the run capacitor, it started fine with the generator, as long as not much other load.

My seemingly identical compressor at home was bought used, it originally came from a local industrial supply. The one at the fire house came from Tractor Supply. Mine is code G, starting current is 5-6 times full load current. The one at the fire house is code L, 9-10 times full load to start it.
 
 

Tractor & Equipment Auctions

2013 Mack GU713 T/A VacCon Combination Sewer Jetter Vacuum Truck (A50323)
2013 Mack GU713...
2008 FORD F-450 (A50854)
2008 FORD F-450...
Toyota 6FGU25 Forklift  5,000 lb Capacity (A51039)
Toyota 6FGU25...
2025 Swict 84in Bucket Skid Steer Attachment (A50322)
2025 Swict 84in...
2018 INTERNATIONAL LT625 TANDEM AXLE DAY CAB (A51219)
2018 INTERNATIONAL...
2021 Kubota SVL97-2HFC Compact Track Loader (A50657)
2021 Kubota...
 
Top