Pulling Wire through conduit- tips ?

/ Pulling Wire through conduit- tips ? #21  
This post started a while back but I wanted my 2 cents worth in there.

like others said, it is easier to pull the length of wire through a stationary conduit than to try and pull one little bit of conduit all way down and risk getting glue all over the wires when assembling the conduit. wires actually pull pretty easy if done right. especially the thhn/thwn/USE types of wires. mtw is harder and is not really meant for service anyway. "U.S.E." (underground service entrance) can be direct burial wire & type THHW/THHN are meant for in conduit for this type of application the THHW/THHN have an outside jacket of slippery material (Teflon/Nylon like coating) which helps it pull much easier. the type U.S.E. also has the coating but a little thicker jacket meant for direct burying.

Pulling lube ONLY in any type of conduit, ya lots of stuff can be used but type #77 or T & B also has some which is only slightly more cost than dish soap and is 100% non-effecting the wire jacket.


it is best to assemble the conduit into the flat bottom trench count up the # of sticks you have and add a few feet, remember they are 10' lengths, if ya cut one in half count it as a hole length. a few extra feet of wire is cheap compared to pulling the short length out and replacing it. not to mention you can take it to the scrap yard and get back some $ for the copper scrap.

ONLY use straight runs and sweeps at ends coming in and out, if you have to have bends in there some place be sure to take a running count of the total # of degrees of bends, never have more than 360 degrees of bends in any single run a pull box is required at or before 360 degrees of turns. there are also max distances of run prior to needing a pull box. I like to ave more boxes just in case, but at least every hundred feet unless you are making one single run from building to building or to a pole. then you can stretch that distance out but beware local codes & elec companies may want pull boxes more or less at shorter distances. make sure to check this out prior to buying anything.!

Shop vac and or compressed air with kite string and a plastic bag/mouse works well for getting string started through the conduit then pull in a rope and use the rope to pull in the wires. keep a few extra feet on each end which can be cut off easily adding it back is a lot harder ;) having the conduit stationary in the ground makes pulling a LOT easier than attempting to pull wires into it then bury it as the conduit will move about a lot... something that makes it darn near impossible to do a long run with and assembling it in the trench can get a lot of dirt into conduit and glue onto wires ... adding an extra 3 wire set of 12 gauge for lights on/off is also a great idea!

my 2 cents worth,

markM

mark M

have fun
 
/ Pulling Wire through conduit- tips ? #22  
I did a 650' pull with 3-#4's and 1-#6 wire a couple of years ago and got lots of good tips here. One piece of advice that stuck - do NOT use liquid soap for the pull; only use wire lube. Something about the soap possibly doing damage to the wire over the years. I buried the conduit first, but what Eddie said makes sense for 125 ft.
 
/ Pulling Wire through conduit- tips ? #23  
hi,
Im trying to replace some wires for my A/C. The wires run under my slab to the circuit breaker box about 40 feet. I disconnected everything so all I have left is the wires and I cant get them to budge. There is one pull box but it is right under the circuit breaker box. Does anyone have any ideas on how to replace these wires. I wanted to just attach a new set of wires to the old ones and pull them through. I have to replace the wires becuase water got into the pipe and ruined the wires. What are the tricks of the trade?
Thanks
 
/ Pulling Wire through conduit- tips ? #24  
when I pull wire usually 4/0 phases 2/0 nuetral I always put a ladder above the pipe I'm pulling from and hang a pulley,dolly, wheel or whatever you may call it and put rope thru dolly and pulldown. Sometimes making a loop in rope (twisst it a couple of times and hold knot with hand) and stand on loop, comes thru nice without braking your back or cutting rope on side of pipe, as long AS PULLEY IS RIGHT ABOVE PIPE.
 
/ Pulling Wire through conduit- tips ? #25  
EddieWalker said:
You're only going 125 feet. Is the pipe already in the ground and buried?

If it was me, I'd unroll the wire along the trench, then slide the pipe over it and glue together. It's simple to slide the pipe over the wire and with only 13 pieces to deal with, it will take you less than an hour.

Don't make it complicated when you can do it easy.

Good luck,
Eddie

I agree.
 
/ Pulling Wire through conduit- tips ? #26  
I worked at a cable shop where we built large and small cables. From 2' long to 300' long. Wires that were 1/4" thick up to about 1.5". We had a machine that blew compressed air through the correct size nozzle. Inside of that nozzle was what we called the "mouse" it was a steel slug with a winch cable attached to it. We would shoot the compressed air down the tube that dragged the winch cable behind it. Before we shot the mouse we put talcum powder in the tube to reduce friction. Once the mouse reached the end of the tube we connected our cable to it. Then winched the cable back down thru the tube. It worked slick. So what my point is if you want either blow a string down with compressed air or try to suck it down with the vacuum. Use talcum for reducing friction. I don't believe you would need to use a winch to pull the cable thru. That might break the pipe if you weren't careful.
Jim
 
/ Pulling Wire through conduit- tips ? #27  
125ft?
For the cost of the rope that you're pulling through it , just by a Greenlee 250' fish tape. You can easily push the tape through the conduit, as long as you have the couplings snug, then just loop the wire to the end of the fish tape, wrap it with electrical tape, put a little yellow 77 on, and pull...
 
/ Pulling Wire through conduit- tips ? #28  
SPIKER said:
This post started a while back but I wanted my 2 cents worth in there.

like others said, it is easier to pull the length of wire through a stationary conduit than to try and pull one little bit of conduit all way down and risk getting glue all over the wires when assembling the conduit. wires actually pull pretty easy if done right. especially the thhn/thwn/USE types of wires. mtw is harder and is not really meant for service anyway. "U.S.E." (underground service entrance) can be direct burial wire & type THHW/THHN are meant for in conduit for this type of application the THHW/THHN have an outside jacket of slippery material (Teflon/Nylon like coating) which helps it pull much easier. the type U.S.E. also has the coating but a little thicker jacket meant for direct burying.

Pulling lube ONLY in any type of conduit, ya lots of stuff can be used but type #77 or T & B also has some which is only slightly more cost than dish soap and is 100% non-effecting the wire jacket.


it is best to assemble the conduit into the flat bottom trench count up the # of sticks you have and add a few feet, remember they are 10' lengths, if ya cut one in half count it as a hole length. a few extra feet of wire is cheap compared to pulling the short length out and replacing it. not to mention you can take it to the scrap yard and get back some $ for the copper scrap.

ONLY use straight runs and sweeps at ends coming in and out, if you have to have bends in there some place be sure to take a running count of the total # of degrees of bends, never have more than 360 degrees of bends in any single run a pull box is required at or before 360 degrees of turns. there are also max distances of run prior to needing a pull box. I like to ave more boxes just in case, but at least every hundred feet unless you are making one single run from building to building or to a pole. then you can stretch that distance out but beware local codes & elec companies may want pull boxes more or less at shorter distances. make sure to check this out prior to buying anything.!

Shop vac and or compressed air with kite string and a plastic bag/mouse works well for getting string started through the conduit then pull in a rope and use the rope to pull in the wires. keep a few extra feet on each end which can be cut off easily adding it back is a lot harder ;) having the conduit stationary in the ground makes pulling a LOT easier than attempting to pull wires into it then bury it as the conduit will move about a lot... something that makes it darn near impossible to do a long run with and assembling it in the trench can get a lot of dirt into conduit and glue onto wires ... adding an extra 3 wire set of 12 gauge for lights on/off is also a great idea!

my 2 cents worth,

markM

mark M

have fun

I think this guy has pulled some wire.

Back in the day, I use to pull 500 MCM all the time. We used lots of lube, pulleys, aircraft cable, and a forktruck, piece of cake.
 
/ Pulling Wire through conduit- tips ? #29  
I think by code, you are required to assemble the conduit and then pull the wire. Part of the idea of the limited length, limited number of corners, and frequent pull boxes is so that the wire can be replaced or upgraded someday if necessary without digging everything up.

If you assemble the conduit around the wire, you may find that you can never pull the wire back out for replacement due to too many turns, too much wire packed in that you would never be able to pull out through the whole length, kinks and tangles, or the glue sticking to the wire or something.

As the old saying goes - most mechanical problems are easily solved by applying a little more force or a little more lubrication.

In this case, go with the lubrication. It makes a world of difference. Also, make sure the wire is layed out kink-free and tangle-free and not dragging too much dirt into the conduit with it.

If working alone, squirt a bunch of lube into the in-going side of the conduit so the wire gets pulled through a healthy blob of the stuff. Then run to the other end, pull a few dozen feet, run back and add some more lube, repeat.

Always use the purpose-formulated stuff like the Ideal #77. Using anything else could weaken the wire jacketing or the conduit, or cause corrosion in a metal conduit. Even baby powder has some solvent and perfume in it that can degrade some plastics over time.

- Rick
 
/ Pulling Wire through conduit- tips ? #30  
(1) Fish tape is easier than using rope.
(2) DO NOT use grease.
(3) DO lubricate the cables; having helper to assist feeding and lubricating [with approved cable/conduit lubricant ONLY] will make job easier.
(4) 2" conduit is plenty big. Up to 14 #4 cables may be used although in practice, that is almost impossible to pull that many.
(5) #6 ground should be all you will need.
(6) MAX 360 degree combined bends. More will require pull bodies or junction boxes.
(7) Pull bodies and box access covers MUST BE accessible.
(8) Stranded cables will be MUCH easier to pull than solid cables.
 
/ Pulling Wire through conduit- tips ? #31  
Came across this thread as I am preparing to build a home and need to get power back to my site which is about 800' back. The power company said I am responsible for the trench and conduit (4" Sched 40 with a 36" radius to 90 degree at each end) and they will pull the wire.

I have not yet asked them this question, but when I assemble the conduit, I assume I have to feed some type of rope or something in it so that they can pull, but what can I use that would stand up to an 800' pull of 200amp service wire?
Should I bury the conduit in spots so that is does not move while they are pulling?
Any advice would be appreciated.
 
/ Pulling Wire through conduit- tips ? #32  
Came across this thread as I am preparing to build a home and need to get power back to my site which is about 800' back. The power company said I am responsible for the trench and conduit (4" Sched 40 with a 36" radius to 90 degree at each end) and they will pull the wire.

I have not yet asked them this question, but when I assemble the conduit, I assume I have to feed some type of rope or something in it so that they can pull, but what can I use that would stand up to an 800' pull of 200amp service wire?
Should I bury the conduit in spots so that is does not move while they are pulling?
Any advice would be appreciated.

My electric company had me put a twine string in the conduit and when they came to put their wire in they used that to pull their rope thru to attach to the wire. Mine was only 100+ feet though, the rest was left open trench and they pulled the wire thru 4" plastic drainage tile before putting it in the trench.

I would ask them what they want, maybe they will blow there own string in.
 
/ Pulling Wire through conduit- tips ? #33  
I have not yet asked them this question, but when I assemble the conduit, I assume I have to feed some type of rope or something in it so that they can pull, but what can I use that would stand up to an 800' pull of 200amp service wire?
The electric company will tell you if they need anything left in the conduit to pull with, so i would ask them first.
If you want to put a string in, get a container of pullstring from Lowes and tie it to a 3' piece of re-rod. That will let you throw it through each piece as you go.
If you want to wait till later, put a shop vac on the end of the conduit and tie a bag to the end of the string so that the shop vac will pull on it and stuff it into the far end of the conduit.

Aaron Z
 
/ Pulling Wire through conduit- tips ? #34  
Forget all that weights and pushing a string, put your pipe together and take a shop vac and tie your string around a sandwich bag and blow it through. You will be amazed at how fast it goes through. Don't worry about how you will know when it's through, it will stop moving once the sandwich bag is out the other end. Make sure the string roll is unobstructed and there is no water in the pipe.
 
/ Pulling Wire through conduit- tips ? #35  
How far apart does the power company want pull boxes ?
I did 900 ft. A few years ago with pull boxes at 300 ft and 600 ft. Once the conduit is in you need to make a mouse and get a box of twine.
The mouse is a produce bag that has insulation in it. Just enough insulation to make it fit the id of the pipe.
Duct tape a shop vac to the other end and drop the mouse in. It will get there fast.
Do this to the entire run and turn it over to the power company. They will use your twine to pull in there rope and then the wire.
 
/ Pulling Wire through conduit- tips ? #37  
They will use a winch to pull the wire so you usually just need to provide some pull string to help get the process started. The baggy on twine with a shop vac works great. Just need some type of adapter between the nozzle and pipe so it can only suck through the pipe... duct tape can work in pinch :D When that twine starts flying in there don't touch it... rope burns for sure!
 
/ Pulling Wire through conduit- tips ? #38  
We just pulled 600' of wire through 4" conduit here about three months ago. We dug the trench, laid pipe, and filled it back in except for the last 15' or so on each end. When the power company cam out, they had a fiberglass "rod" on a reel that they pushed in. When that 200' ran out, they screwed on another 200' reel, and pushed on. When the third reel poked out the end, they tied their rope to it, and pulled it back with rope in tow. Three guys pulling and one guy squirting soap, they pulled the wires through by hand. When all was said and done, they left me the 600' of the rope they used, great stuff BTW.
 
/ Pulling Wire through conduit- tips ? #39  
Hmmmm - most people who have pulled through conduit seem to use a liquid lube. I've always used talc - "Johnson's Baby Powder" to be precise. Clean and doesn't risk messing with the insulation. And cheap!

My $0.02.

+1
In all my years working as an Electrician that's what I used. Clean and effective. And if you run into problems and have to pull the cable back you won't have cable on the ground collecting all the crud on the floor.
 
/ Pulling Wire through conduit- tips ? #40  
I pulled 4-0 service through 60' of 2" PVC with a 90*sweep on each end last summer. I was afraid it was going to be ****! It was not! Pulling took 5 minutes!!!
I blew a 1/4" rope through with a paper towel tied to the end with shop vac, then pulled a 5/8" rope back through. Taped/wired the rope to the 4-0 and fed while friend pulled. One hand full of lub and it slide right through. I pulled from inside the home to the pole which kept the wire clean.
One of the easiest things I have ever done! All that sweating before hand for nothing.
 

Marketplace Items

2025 Wacker Neuson EZ50 Zero Tail Excavator Extremely Low Hours (A63118)
2025 Wacker Neuson...
(APPROX. 100) UNUSED SDLANCH 6' CORRUGATED STEEL (A62131)
(APPROX. 100)...
UNUSED WOLVERINE GB-11-72W 72" HYD GRAPPLE BUCKET (A62131)
UNUSED WOLVERINE...
2013 BMW 528I Sedan (A61569)
2013 BMW 528I...
UNUSED RAYTREE RMBD72 - 72" DRUM MULCHER (A62131)
UNUSED RAYTREE...
2024 COLEMAN MINI BIKE (A58375)
2024 COLEMAN MINI...
 
Top