Running Power to Detached Garage

   / Running Power to Detached Garage
  • Thread Starter
#51  
Distance of current home to future home will be around 75-100 feet. Distance from future home to detached garage will be around 50 feet.
 
   / Running Power to Detached Garage #52  
4/0 alum feeders for 200 amps is fine. 2 inch conduit. Need to run 2 power runs, 1 neutral run and a ground wire. 4 total wires. I use #2 alum for ground.
 
   / Running Power to Detached Garage
  • Thread Starter
#53  
Out here, we use Ufer Grounds to ground the circuit panel. The ground wire gets tied into the rebar cage in the footing before the concrete pour. The copper ground wire then runs into the circuit panel.

Will a 100 sub panel be enough power in the garage for a 2 post car lift plus some LED lighting and 2 garage doors?
 
   / Running Power to Detached Garage #54  
Plenty of power. Those lifts don’t take much power at all
 
   / Running Power to Detached Garage #55  
I've got a 50amp 220v sub panel in my garage.
I run an arc welder, a 2hp swimming pool pump, air compressor, garage door opener, lights... all the modern conveniences. ;)
 
   / Running Power to Detached Garage #57  
That would easily fit in 1-1/4” conduit.
 
   / Running Power to Detached Garage #58  
So, my shed, I ran 50 amp 220 with conduit and aluminum wire (yes, it was rated for the amps/distance). At the sub panel; I had a single 25 amp 220v outlet for my welder; and 2-110v circuits for outlets and led lights. Posts are at 8 ft OC, so I put a duplex receptacle at each post. Lights are 110v duplex outlets on roof rafters; but switched. Outlets are all higher then normally; ment to be 8" above "bar height"; and my work benches/stools are also bar height.

No permits pulled; and it's just a 24x36 shed; but I still did all 12 ga romex inside shed, and 8 ga (If I remember) for the very short, 10 ft run to the welder outlet.

I would make sure to make a least 1 110v outlet at your metal working station; probably a 4x4 box; I have to unplug the drill press or grinder to use a 3rd tool at the metal working station. Wood working station, same; table saw and chop saw; but got to unplug (or use extension cord) to use sander.

I do have the window unit ac on the closest 110v outlet to panel on 1 circuit and the air compressor on the closest outlet on other circuit.

I also ran a 3/4" cold only water service to the inside of the shed with an inside hose bib; makes watering dogs, washing hands; cooling hot metal parts, a breeze.
 
   / Running Power to Detached Garage #59  
I like the SIMpull wire. It is much easier to pull in my opinion.

Good luck!
 

Tractor & Equipment Auctions

2018 HINO 268 24FT NON CDL REEFER BOX TRUCK (A59575)
2018 HINO 268 24FT...
2020 FREIGHTLINER CASCADIA 126 SLEEPER TRUCK (A59575)
2020 FREIGHTLINER...
John Deere 855DXUV Gator (A57148)
John Deere 855DXUV...
2016 KENWORTH T680 TANDEM AXLE DAY CAB (A59575)
2016 KENWORTH T680...
Year: 2019 Make: Nissan Model: NV200 Vehicle Type: Van Mileage: 88,557 Plate: Body Type: 4 Door Van (A55853)
Year: 2019 Make...
2010 Toyota Highlander SUV (A59231)
2010 Toyota...
 
Top