Mechanical is the biggest issue inspected by Jacob Justice. I liked that name.
These were his last reasons to fail on 9-8-2022
1. Bath exhaust terminations must terminate outside per plans
2. Will require rfi for intake air duct for office areas, not per plans
3. Unit heaters will need to be installed per installation instructions, see figure 8.1 for
condensate line installation
4. Will need letter for condensate line system for proper sizing and manufacturer
recommendation on how much unit heaters can be tied together
5. Properly terminate condensate lines from unit heaters, see exterior termination
locations
6. Per unit heater installation instructions figure 13.1 adapter box with combustion
air intake pipe attached, box not adequate size for model 310
7. Will require letter from manufacturer for height of unit heater
8. Will need letter for exhaust fans, have been modified and requesting more
information on model of exhaust fans (14)that have been installed
A week before that he reported
1. Max height of tstats 48"
2. Rfi for bath exhaust fans terminating inside of building
3. Rfi for condensate line for unit heaters and provide specs on condensate pump
4. Provide manufacturer instructions for unit heaters to verify installation
5. Rfi for fresh air duct install, different from plans
They were approved to start 4 heating units for temporary heat on 12-22-22
On Gas inspections by the same inspector. on 9-8-22
1. Install Ballard at gas meter location
A week before
1. Properly label gas line throughout
2. Provide Ballard to protect gas line at meter location and interior side where it exits
wall
On the building itself by Damon White on 9-08-22
1. Will need structural engineer evaluation for added weight and added exhaust fans installed
a week before
. Need adequate egress lighting
2. Need to exit lighting
3. Do not have proper turning radius in all restrooms with hot water heater installed
Those are the Failed items that have not been corrected.
Finals have been received for Plumbing on 8/30/22 and Electrical on 4/6/23.