Which rating are you talking about?

- The Nominal Discharge Current (In) – the peak value of current, through the surge protective device (SPD) remains functional after 15 surges.

- The Short Circuit Current Rating - the amount of “available” current that the SPD can be subjected to and safely disconnect from the power source under short circuit conditions.

- something else?

The Generac SPD my standby generator installer installed as a NDC rating of 20kA and a SCCR rating of 200kA.
 
   / Surge Protection Install Ques #22  
Mine is just down stream of the main service entrance breaker, And I believe it is only good for one lightning strike. We had a big strike, and all the circuits were protected, but the surge protector sacrificed itself I think. Had to get a new one.

Meanwhile, the neighbors had damage to their standby generators and their electronic equipment. I guess they didn’t have surge protectors! I suppose I you spellI guess they didn’t have surge protectors! I suppose I should ask them one day.
 
   / Surge Protection Install Ques
  • Thread Starter
#23  
I’m going to go w the F140 and install on the inside of main 200amp panel. Thank you very much for all the suggestions.
 
   / Surge Protection Install Ques #24  
I put my arrestor at the main breaker on the pole
where the power lines are just have the 200 amp
breaker and the arrestor.

willy
 

Tractor & Equipment Auctions

2000 MACK CH DAYCAB (A58214)
2000 MACK CH...
2003 Big Tex 10PI 16ft. T/A Pipe Top Utility Trailer (A55973)
2003 Big Tex 10PI...
2021 Polaris Ranger Electric Utility Bed UTV (A56859)
2021 Polaris...
2018 Doosan C185 Trailer Mounted Air Compressor, Model 484289UBACG07, S/N C185WD20T4F, Deutz Diesel (A59076)
2018 Doosan C185...
Bucket (A55973)
Bucket (A55973)
New/Unused CFG Industrial MX12RX Mini Excavator (A57453)
New/Unused CFG...
 
Top