Surge Protection Install Ques

   / Surge Protection Install Ques #21  
Which rating are you talking about?

- The Nominal Discharge Current (In) – the peak value of current, through the surge protective device (SPD) remains functional after 15 surges.

- The Short Circuit Current Rating - the amount of “available” current that the SPD can be subjected to and safely disconnect from the power source under short circuit conditions.

- something else?

The Generac SPD my standby generator installer installed as a NDC rating of 20kA and a SCCR rating of 200kA.
 
   / Surge Protection Install Ques #22  
Mine is just down stream of the main service entrance breaker, And I believe it is only good for one lightning strike. We had a big strike, and all the circuits were protected, but the surge protector sacrificed itself I think. Had to get a new one.

Meanwhile, the neighbors had damage to their standby generators and their electronic equipment. I guess they didn’t have surge protectors! I suppose I you spellI guess they didn’t have surge protectors! I suppose I should ask them one day.
 
   / Surge Protection Install Ques
  • Thread Starter
#23  
I’m going to go w the F140 and install on the inside of main 200amp panel. Thank you very much for all the suggestions.
 
   / Surge Protection Install Ques #24  
I put my arrestor at the main breaker on the pole
where the power lines are just have the 200 amp
breaker and the arrestor.

willy
 

Tractor & Equipment Auctions

2018 Cadillac Armbruster 70IN Limo - 43,279 Miles, Professional Coachwork, Clean Executive Vehicle (A56435)
2018 Cadillac...
2007 Sterling L9500 National Crane 1800 40 Ton Tri Axle Telescopic Boom Crane Truck (A55973)
2007 Sterling...
6' LANDSCAPE RAKE, 3PT (A52708)
6' LANDSCAPE RAKE...
VINTAGE EVINRUDE OUTBOARD MOTOR (A58374)
VINTAGE EVINRUDE...
NEW Fork Extensions (A59000)
NEW Fork...
30in Forks and Frame Mini Skid Steer Attachment (A56857)
30in Forks and...
 
Top