May be. But if I put a 20 amp load on a 15 amp breaker for any longer than a minute, that sucker had better trip, or it's getting canned pronto.
- Jay
Looking at the "AMPS - TIME graphic" posted above for a 15 amp Square D QO breaker, a 15 amp load should trip the breaker in just under 0.4 seconds and a 20 amp load should trip it in under 0.02 seconds.A 15 amp breaker will carry 15 amps 24 hours a day 365 days a year and not disconnect. It will carry 20 amps a long time, before tripping, depending on heat dispensation of the breaker. If you throw out a 15 amp breaker if it doesn't trip within a minute loaded with 20 amps, you will throw out every breaker you buy.
It is all in the "AMPS - TIME graphic". You need to understand the graphic to understand the breaker!
:thumbsup:It is all in the "AMPS - TIME graphic". You need to understand the graphic to understand the breaker!
NEVER test a breaker " short cutting" the breaker. The breaker is designed to disconnect in case of a short (and prevent fire), but can only do so a few times.
Testing a breaker can not be done at home, since you have to test Amps in relation to time over the whole band.
Bert, retired Electrical Contractor.
- Bert is correct, a 15 amp breaker will carry 15 amps all day. The numbers on the bottom of the "amps- time graph (a.k.a. time-current curve) represent the multiple of the breaker's rated current. Thus 15 amps is represented by the number "1". The above graph has the top of the curve cut off at a little over 10 seconds, but we can see that the curve needs a lot more time to even approach "1".Looking at the "AMPS - TIME graphic" posted above for a 15 amp Square D QO breaker, a 15 amp load should trip the breaker in just under 0.4 seconds and a 20 amp load should trip it in under 0.02 seconds.