You're looking at the whole problem in the opposite way I am and am making some assumptions that have not been shown with a schematic.
As I understand it, HillStreet said the delivery temp was controlled by the tempering valves at 110 degrees. That means they are mixing return water from the floor loops with hot boiler water to deliver a temp lower than the boiler setpoint. And it means the mixing valves do have an affect. We just haven't seen how they are actually piped in.
Arguing that the return temp determines condensation misses the point. If the boiler is cycling, and we know it is, and if it's set at a higher temp, which we know it is, then the inlet and outlet are close to the same unless there is a severely incorrect flow rate. So close that the boiler has to cycle. They can easily both be above the condensing point or both below it. If the outlet is below it we know the inlet temp is to, but not the other way around. This is especially true with the underfloor delivery system as compared to an in-slab system. With in-floor systems the boiler can be overloaded for some time and have a large differential. Since this is a condensing boiler, we want it to condense as much as possible. But we still don't know how the DHW system is tied in, so we can't necessarily just turn it down. If we can adjust the CH different than the DHW we can turn it down. Just too many unknowns here to make a lot of assumptions.
He has already said that the house heats with 110 degree water, so that is close to the minimum it should run at. 130 or 140 would be a more practical temp, possibly, but apparently the mixing valves are only allowing 110. Since we don't know exactly how his delivery is arranged, or his lifestyle, we can't say that slow even heat is the best either. Often, it's not.
If you have a slow even heating system, one that circulates constantly, or almost constantly, then the outdoor reset begins to make more sense. But if you have a tempering valve controlled delivery, the outdoor reset is somewhat defeated. When heating rooms that are not constantly used, such as spare bedrooms, or even the master bedroom in most cases, slow even heating is a disadvantage. It's better suited to living rooms where retired folks might spend the majority of their time and want a constant temp all the time. Faster recovery works better where you want to sleep in a cool room but get up to a warm floor. That's where the setback thermostat gives better control than delivery temp.
Too bad we can't see a schematic or know more about what is actually going on.
As I understand it, HillStreet said the delivery temp was controlled by the tempering valves at 110 degrees. That means they are mixing return water from the floor loops with hot boiler water to deliver a temp lower than the boiler setpoint. And it means the mixing valves do have an affect. We just haven't seen how they are actually piped in.
Arguing that the return temp determines condensation misses the point. If the boiler is cycling, and we know it is, and if it's set at a higher temp, which we know it is, then the inlet and outlet are close to the same unless there is a severely incorrect flow rate. So close that the boiler has to cycle. They can easily both be above the condensing point or both below it. If the outlet is below it we know the inlet temp is to, but not the other way around. This is especially true with the underfloor delivery system as compared to an in-slab system. With in-floor systems the boiler can be overloaded for some time and have a large differential. Since this is a condensing boiler, we want it to condense as much as possible. But we still don't know how the DHW system is tied in, so we can't necessarily just turn it down. If we can adjust the CH different than the DHW we can turn it down. Just too many unknowns here to make a lot of assumptions.
He has already said that the house heats with 110 degree water, so that is close to the minimum it should run at. 130 or 140 would be a more practical temp, possibly, but apparently the mixing valves are only allowing 110. Since we don't know exactly how his delivery is arranged, or his lifestyle, we can't say that slow even heat is the best either. Often, it's not.
If you have a slow even heating system, one that circulates constantly, or almost constantly, then the outdoor reset begins to make more sense. But if you have a tempering valve controlled delivery, the outdoor reset is somewhat defeated. When heating rooms that are not constantly used, such as spare bedrooms, or even the master bedroom in most cases, slow even heating is a disadvantage. It's better suited to living rooms where retired folks might spend the majority of their time and want a constant temp all the time. Faster recovery works better where you want to sleep in a cool room but get up to a warm floor. That's where the setback thermostat gives better control than delivery temp.
Too bad we can't see a schematic or know more about what is actually going on.