sailfast
Silver Member
Glad you got it figured out. ..Hey Everybody,
The boiler situation is fixed, and the radiant system is operating just fine. After exhausting everything I learned from the manual, I called the factory (US Boiler Company) in Pennsylvania. I spoke with Ron in the Tech Support Dept and he was terrific, patient, and very knowledgeable.
I really studied the system, boiler, circulating pumps, and all of the plumbing and wiring. The one situation I could not remedy is getting the pumps to run when they are commanded, not when something else initiated it.
I started when there was zero demand for heat and domestic hot water. I ran DHW to initiate a call for that. The boiler and control panel responded by starting the boiler, the boiler pump, the DHW pump, and the System pump. I wanted the DHW pump and boiler pump to run, but not the system pump. I would do this repeatedly, and make changes to the system parameters with the boiler controller. At every evolution, the system pump kept running, which sent hot water through the main loop up to the manifolds. The pumps on the manifolds did not run until thermostats called for heat.
The zone 4 light went on, telling me that DHW was active, and the priority switch was enabled. The boiler control display showed Central Heat was active, and made no mention of DHW. I sat there, keeping logs, checking pumps and temps and could not figure it out. On a subsequent try, I noticed the temps at the manifolds were 120 degrees as I set them. Then the zone 4 light would go out, and the boiler would shut off. Humph. Did it again, and finally realized it was one hour from start to shut down. Did it again to prove it and yes it shut off after one hour. I knew about the one hour priority wait time for Central Heat to wait for DHW. I could not correlate that to my situation though, because I tried every single combination on the boiler controller.
Next morning I called the factory, and Ron found the problem in the first 4 minutes. My plumber used a TACO switching relay 504. It controls the t-stats for central heat, but it would not work for the DHW, despite the priority switch on zone 4, where the DHW was connected. Ron told me to remove the DHW t-stat from the TACO switching relay, and connect it to the boiler terminal strip on the boiler. Same with the pump for DHW.
I did that, and it works fine now. Not only that, but the pump settings in the boiler software now actually work on the choices I was selecting this whole ordeal. Priority for DHW is chosen by the boiler software, not a switch on the switching relay. The boiler factory wiring is really mostly done for the installer, if the installer knows how to read a diagram.
I set DHW to 170, and central heat to 140, with the mixing valves at 120. In weather similar to this, the boiler would run 7 to 11 hours after the sun went down. Last night it ran one hour about 4am today. It will get cold later this week so we'll know how it performs.
I know, this is long, too windy. Thanks to all of you who responded and supported my cause. I do appreciate it.
Now how much time did you waste and energy did you waste? Penny wise and pound foolish.
If you had a trained professional instead of a plumber install it would have been right to start with....
AND if you had called a trained professional to begin with to fix the problem you would have saved yourself a huge amount of time and money.
So, how much did this really save you?