Vapor barrier - house wrap question!

   / Vapor barrier - house wrap question! #1  

inane2

Silver Member
Joined
Feb 26, 2012
Messages
137
Location
Kentucky
Tractor
NH T4.75 Powerstar, Kubota KX161-3 & SVL75-2
Hey guys!

Slowly working on remodeling a 36'x48' shop that was on my property when I moved here. A little about the building up front :

- 5.5" concrete slab
- Trusses on 6' centers
- 2x6 girts (flat) on 30" centers
- White ribbed metal panels on the ceiling, 10' tall
- No soffit on either end on the building, trusses were cut flush with the posts
- Heated by a barrell wood stove

I went back in and replaced metal on two sides of the building due to damage and very badly faded, chalky paint. Once the new metal was up, we went in and toe-nailed in 2x6 bookshelf girts on top of the flat girts (still retaining 30" centers).

I've bought R-19 batts, 15" wide and 6.5" deep, kraft faced. These will fit perfectly between the new girts. Once installed, going to cover the walls with 7/16" OSB. The corner where the barrell stove resides will get white metal instead of OSB.

I went ahead and bought new metal for the roof. It will be spring before it's installed unless we get a nice weekend sometime soon. Before laying the new metal roof down, I'm going to install "Low-E" radiant barrier. 1/4" thick, basically double bubble with aluminum foil on both sides. This will be installed over the purlins, beneath the new metal. Also, there is currently insulation batts between the trusses, on top of the metal ceiling. This stuff is in rough shape, so I'm going to remove it and use blow in insulation.

Two questions:

1. Should I install a plastic vapor barrier over top the batts in the wall before I install the OSB (or metal in the stove corner)? Any recommended thickness?

2. Should I install tyvek or house wrap against the inside of the metal before I install the batts in the wall cavities? Looking back, I had a perfect chance to do this when the metal was off. I've read different opinions on having bare fiberglass against metal panels.

To help you visualize, here is a pic before I installed new metal and bookshelf girts:

picture.php



Thanks guys!!!
 
   / Vapor barrier - house wrap question! #2  
nice shop tyvex . it helps with holding the isolation in place and the heat and plastic inside ya . and for your heat just put a pic of steal tin 1/2 from the wall and strap it 1/2 off the floor the cool air will run behind it and you will never melt the plastic ..it will never get hot behind the steel ..even if it is on the ceiling keep a space between the steel and let the air through it it will make its own draft and keep cool behind it i hope this will help
 
   / Vapor barrier - house wrap question! #3  
On the building/houses they build here they put the OSB/sheathing on the outside of the wall, then the Tyvek - and completely wrap the building/house.
 
   / Vapor barrier - house wrap question! #4  
I like to use 6mil poly for vapor barrier on large walls like this. 4 mil does the job but the 6 mil is easier to stretch tight & staple without tearing holes in it. Don't put a vapor barrier on both sides of the insulation but Tyvek would work, it is a wind barrier but does "breath". The Kraft faced is a vapor barrier it self so if stapled in smooth with no rips, poly is not supposed to be required, but we always used it anyway in the houses we used to build. You could also cut slits in the kraft face to let is breath, install the paper side towards the outer wall against the outer steel then poly on the inside.
 
   / Vapor barrier - house wrap question!
  • Thread Starter
#5  
Thanks for the responses guys.

The 6 mil makes sense on handling it vs the 4 mil. I have quite a bit of 6 left over from another concrete pour. This would be a good place to use it.
 
   / Vapor barrier - house wrap question! #6  
Since you live in Kentucky, your vapor barrier should go on the outside of the insulation, not the inside, since your predominant climate is humid and hot. Now if you live in the mountains and the weather is more mild and you have some cold weather in the winter, might want to put the barrier toward the living space. Kraft facing is considered class II vapor retardant, which is more than the IRC requires or recommends for your area, so you should put that against the exterior wall. If you haven't bought the insulation yet, I'd get it unfaced. The insulation manufacturer's guidance is to avoid any class I retardant (like poly) in warm climates because of condensation complications.
 
   / Vapor barrier - house wrap question!
  • Thread Starter
#7  
Thanks BeezFun. Great info. I live in central KY, gets cold in the winter, but our summers are very hot and very humid.

I did already buy the insulation. It's Owens Corning EcoTouch R-19 kraft faced batts. 15" wide by 6.5" deep. If I skip the poly and housewrap both, do you recommend putting the Kraft facing against the metal and the fiberglass against the OSB?
 
   / Vapor barrier - house wrap question! #8  
Thanks BeezFun. Great info. I live in central KY, gets cold in the winter, but our summers are very hot and very humid.

I did already buy the insulation. It's Owens Corning EcoTouch R-19 kraft faced batts. 15" wide by 6.5" deep. If I skip the poly and housewrap both, do you recommend putting the Kraft facing against the metal and the fiberglass against the OSB?

I'd study this page. I would have said use housewrap, but since your siding is on it's hard to do that now. Steel siding really likes to condense moisture, so it's not ideal to have insulation right against it, but you can minimize that problem by making a really good air barrier out of the OSB. I'd caulk the OSB joints and foam any larger openings along floor or top sill, that will make the OSB your air barrier. Since you plan to heat the structure in winter, and I assume will not air condition it in summer, I think I'd put the kraft facing against the living space, especially since you have cold winters. You'll never have any hot exterior summer air hitting a cold living space, so there shouldn't be any condensation in the summer.

If there's any chance you could exchange that fiberglass for foam board insulation, I'd do that. Moisture is not a problem with the foam board and it also stops air migration if it's installed well. It's much more forgiving when you use it with steel.
 
   / Vapor barrier - house wrap question! #9  
I always thought house wrap let inside moisture out but didn't let outside moisture in. The outside sheathing is metal and theoretically impervious. If you put tyvek or some such up against it won't that tend to concentrate moisture inside the sheet metal? Usually outside walls are T-111 or siding or clapboards or brick or some other semi-permeable material.
 
   / Vapor barrier - house wrap question! #10  
I always thought house wrap let inside moisture out but didn't let outside moisture in. The outside sheathing is metal and theoretically impervious. If you put tyvek or some such up against it won't that tend to concentrate moisture inside the sheet metal? Usually outside walls are T-111 or siding or clapboards or brick or some other semi-permeable material.

100% agree.
 
   / Vapor barrier - house wrap question! #11  
Howdy,

Everyone here is thinking this is a framed house structure. It's not. It's a post and beam building. House wrap should not be used.. The only items which should even be considered would be true foam board, or plastic or foil covered foam board. You do not want to have open fiberglass insulation next to the metal panels. The interior of the building can have its own atmosphere. You can even have a rain forest inside on those hot humid days. Buildings like this will always have some draft.
 
   / Vapor barrier - house wrap question! #12  
I would do 1/2" celotex or similar board between the girts, then the R19 batts paper facing in, then cover that with the poly - a dual barrier so to speak.

The concern I would have is the batt insulation slumpinig in the 30" space - the 1/2" board would keep the insulation away from the siding and provide a air passage, then the R19 would be tighter along with the plastic in the space between the girts would be a very good insulation R value and reasonably tight.

The other alternative is to return the FBG insulation and do 2-3" spray insulation directly on the metal - this would be the best solution overall and eliminate the condensation aspects.

Carl
 
   / Vapor barrier - house wrap question! #13  
I always thought house wrap let inside moisture out but didn't let outside moisture in. The outside sheathing is metal and theoretically impervious. If you put tyvek or some such up against it won't that tend to concentrate moisture inside the sheet metal? Usually outside walls are T-111 or siding or clapboards or brick or some other semi-permeable material.

You're correct, but moisture and water vapor are two different things. Housewrap prevents the passage of water as in rain, but allows the passage of water vapor, as in humidity. Poly prevents both, kraft facing prevents vapor but not water, some paints prevent both, some paints prevent neither, interior plywood is poor at stopping vapor but exterior plywood is pretty good because of different adhesive. Designing this properly isn't easy, the manufacturers give really good guidance but very few people seem to look at it.
 
   / Vapor barrier - house wrap question! #14  
Howdy,

Everyone here is thinking this is a framed house structure. It's not. It's a post and beam building. House wrap should not be used.. The only items which should even be considered would be true foam board, or plastic or foil covered foam board. You do not want to have open fiberglass insulation next to the metal panels. The interior of the building can have its own atmosphere. You can even have a rain forest inside on those hot humid days. Buildings like this will always have some draft.

Post and beam buildings are used for everything from medical clinics to retail stores and offices. You happen to be familiar with them as barns, and barns are drafty, but they can be made as airtight as any other structure if that's a requirement. This fellow is trying to build something that isn't drafty and can be heated. I agree with you that I would not put fiberglass next to metal panels, but he has purchased the material and needs to find a solution that optimizes what he has. After thinking about this, I think I'd staple felt paper into each cavity against the metal. It passes water vapor easily, stops condensation on the metal from reaching fiberglass, it's cheap, and provides some thermal break between the metal surface and air in the wall cavity.
 
   / Vapor barrier - house wrap question! #15  
I would do 1/2" celotex or similar board between the girts, then the R19 batts paper facing in, then cover that with the poly - a dual barrier so to speak.
Carl

This is the worst possible combination of solutions. The foil on Celotex and the poly are both class I vapor barriers. So you've created a cavity in which moisture condensation in the fiberglass would never be able to evaporate in either direction. Here's a good article on vapor barriers. I think the pendulum swung too far trying to create air tight walls, that resulted in mold and moisture damage. Now things are swinging back to a middle ground that recognizes the importance of allowing a wall to dry out once it gets wet, because they all get wet at some point.
 
   / Vapor barrier - house wrap question!
  • Thread Starter
#16  
Here is some photos (from my phone) of the inside walls with the bookshelf girts and new metal up :

picture.php


And the corner with the wood stove :

picture.php


The posts are 5x5 and are on 12' centers. There is a short scab section of post on 6' centers between the actual posts. This puts the trusses 6' OC. There was a single 2x10 header. After toenailing in a 2x6 on the top 2x6 girt, we ripped a 2x10 down and placed it below the header. This formed a box (opens into the attic cavity). We already put in a single 15" wide batt in this area before we nailed the ripped 2x10 in place.

The 5x5 posts worked out great as this allowed my to take the bookshelf girt and sit it back some on the existing girt and toenail into that as well. Toenailing here and at the post ends really stiffened the board up as I was concerned with the 12' span.

There is 8' between the bottom of the ripped 2x10 down to the bottom of the top (non-treated) 2x4 nailed onto the achored treated 2x4. I plan on closing this in with vertical sheets of 7/16" OSB.

Again, the stove will have white metal in the corner. Behind the stove will be 6 feet of metal. The other wall that isn't visible in the stove will have all 12' in metal. This is the front wall and goes to an overhead door.
 
   / Vapor barrier - house wrap question! #17  
Looks very nice. I thought about this and think I'd staple felt paper in the cavities to cover the metal. That will prevent condensation or rain from getting to the insulation, but will pass water vapor so the wall can dry out. It's also cheap and easy to put up. Don't seal the bottom edge of the corrugated metal, the corrugations are the only way water has to drain down behind the wall. If the top edge is open as well that will give you pretty good circulation in the wall cavity to keep things dry.

How do you plan to support the bats of insulation? They are running horizontally and there is nothing to staple the top edge of the bottom roll to in each girt cavity.
 
   / Vapor barrier - house wrap question!
  • Thread Starter
#18  
Thanks BeezFun. Thanks for sharing those interesting links as well.

As you mentioned, the installation of the top row of batts will be fine. I can staple the top edge to the top girt. I can staple the bottom edge of the bottom row but that won't cut it I'm sure. I really don't want to rely on friction and end up with sagging insulation.

I looked at lowes and the longest wire support hangers they had were 24". Do you think using two of those diagonally in both lower corners would suffice? Man, I wish they has used full posts 6' OC!

Also, I've been looking at tar paper. It's cheap, around $15 per roll and it is 36 inches wide which would more than cover each cavity and give me some leftover to staple on top and bottom.

I already have new metal for the roof. What's your take on installing low-e radiant barrier over the purlins when I'm up there replacing the metal? It may be this weekend or next spring before I get to that project.

http://www.low-e.com/products/products_view.php?Product=Low-E

It looks like nice stuff to work with. 1/4" thick, no mess or itch. I will have a 14" ridge cap and will blow insulation into the attic on top of the metal ceiling.

Thank you!
 
   / Vapor barrier - house wrap question! #19  
I looked at lowes and the longest wire support hangers they had were 24". Do you think using two of those diagonally in both lower corners would suffice?
Not really, I think you'd be better off running a horizontal 1x or 2x through the middle of each cavity and staple the bottom roll to that. You can keep it from sagging by nailing through the OSB to catch it. You'll need to use a nail gun or screws to catch it. Not a great solution, but best I can think of. Your other option is to run the insulation vertically and staple the top edge of the facing to the horizontal element you have. Snug the insulation pieces up against each other.

Also, I've been looking at tar paper. It's cheap, around $15 per roll and it is 36 inches wide which would more than cover each cavity and give me some leftover to staple on top and bottom.
Yes, I think that will help improve your situation for not much money.

I already have new metal for the roof. What's your take on installing low-e radiant barrier over the purlins when I'm up there replacing the metal? It may be this weekend or next spring before I get to that project.
It's a good product but since you are installing an insulated ceiling, I think adding the barrier is probably not enough of a benefit to justify the cost and labor of installation. It might reduce the temp of your attic space marginally, but your insulation addresses that more directly. I think better value for that money is to install something like a solar powered roof or gable fan, and make sure you have enough ventilation space either along the soffits or on the gable ends. Or I'd add more insulation to the ceiling.

It looks like nice stuff to work with. 1/4" thick, no mess or itch. I will have a 14" ridge cap and will blow insulation into the attic on top of the metal ceiling.
Make sure you put up something before the metal ceiling to reduce air flow into the insulation, and avoid direct contact with metal. That would be a good application for plastic sheeting to act as a vapor barrier too. When you put it up caulk the seams and staple right through the caulking to make a nice airtight joint. Run it down the walls a few inches before you put up your OSB. Caulk and staple it along that new top plate you've created.
 

Tractor & Equipment Auctions

2024 CATERPILLAR 305 CR EXCAVATOR (A60429)
2024 CATERPILLAR...
2018 FREIGHTLINER CASCADIA TANDEM AXLE SLEEPER (A59905)
2018 FREIGHTLINER...
2014 F-150 STX (A56438)
2014 F-150 STX...
2006 Keystone Laredo 29RL 31ft. T/A 5th Wheel Travel Trailer (A55853)
2006 Keystone...
2014 FREIGHTLINER 108SD CONCRETE MIXER TRUCK (A59823)
2014 FREIGHTLINER...
(1) 36"X8' ADS DRAIN PIPE (A60432)
(1) 36"X8' ADS...
 
Top