</font><font color="blue" class="small">( @Rambler:
If I have two 50A double pole breakers tied in parallel, that makes 100A. (Only if there were in series would I have a limit of 50 A). Therefore, I at least have 100A service for my main panel. Any draw over that and my main will trip. If the same is being used for the barn out of the main panel, I could in theory use the full 100 A in my barn. This would create a condition where my well pump, furnace or other household things would cause the main to trip.
In actuality, I should probably limit my use to the barn to something like 60 A. There is very little chance of needing more and that would ensure that the necessary household items wouldn't blow the main.
However, and this is the main point, this is all reliant on the fact that the wiring in the conduit is able to carry 60 A.
@Everyone:
Thanks so much for the help so far. I promise that I won't do anything stupid! /forums/images/graemlins/tongue.gif
Edit: Also, I should mention that the distance from the house to the barn is around 250 ft. )</font>
Ok. I missed the part where you have a 100 amp main disconnect. Current code, as of August, requires a main breaker, not disconnect, to start with, so I was taking the 50 amp breaker as your first disconnect. I might be using the wrong terms here, but I was looking at it differently, your way makes sense now.
Then you likely can pull 60-80 amps at the barn. I have a 200 amp service now, with 100 amps in the house, & 8 buildings each with a 60 amp (possible - most are still with the 20 amp box) serice. I have 3 wire runs going to the various buildings, 2 braches are over 300 feet, the branch tot he house is 75 feet. Takes some _serious_ size wire for long runs. I'm thinking your current wire will be limiting for the distance you have....... Most of my wire is not measured in 'gauge' any more, bigger than that......
So, we need to figure out those wires. Only limiting factor.
As others suggest, with safety in mind, open up the barn box, and see what you can see for the wires. They better be huge, you should be able to make out some writing on the lengths in behind the screw-in cover. Also, is it copper or aluminumn, makes a big difference.
If this is an older shed, it could be rewired, as my buildings are now. I have 220v, 60 amp service wires into each building. However, a couple of old 120v, 20 amp fuse boxes are still being used. Until I make more $$$$ and can do fruther upgrades. /forums/images/graemlins/smile.gif
A pic or a description of what the box is located in your shed will help to figure out what you have there, if you will be needing a whole new box, or upgrade the breakers, or....
--->Paul