I'll babble here for a few minutes. I had an electrician friend who did a lot of farm work at one time. He had a farmer call him and tell him that his cows would not go near the barn. He took the neutral off the panel and measured between the incoming neutral and the panel grounding rod and measured over 900 volts. He called the power company and they actually found the broken ground at the base of the pole the transformer was on. Come to find out the ground was a plate poured into the concrete pad in the barn thus the transformer on the pole was getting it's ground through the farmer's panel ground and over that distance (something over a thousand feet, the resistance of the wire is high enough to allow a voltage drop) is not a good enough ground for the transformer. The cows obviously knew there was a problem as they are very sensitive to electricity. If the same scenario is happening at your place, I would definitely have the power company investigate as this is a serious shock hazard, not only to you but also to anyone who comes in contact with the grounding of anything in your house, especially if you are standing in the basement in a damp area or outside standing on the ground and touching some object that is grounded to your panel. It may be that your ground rod or plate (as someone mentioned above is not sufficient) is not getting a really good bonding to dissipate the potential on the ground line. I hope this may help, at least let us know if the problem is resolved.