At a certain point you are just wasting money going to big. I'd go at least 1 size bigger than your maximum load.Well, should I go with more than 15K? There is a 20K or 25K that looks good. I probably only need 10K to 12K.
Really, you need to determine what your maximum load is, otherwise you are just shooting in the dark. You have 2 easyish options:
Turn every thing on & decipher how fast your meter is spinning.
Read manuals and/or power supplies for the maximum wattage of all the stuff that is likely to possibly be on at the same time (likely to be a fair bit high as those are maximum ratings & most devices generally pull 40-80% of their max rating).
Personally I didn't take this advice & just used some dead reckoning to do a ballpark guess that what I was looking at on Craigslist would fit. I've got some decent guesses as to my max load though & am fine risking popping a breaker if I'm wrong.
25kw / 240v = 100ish amps. My breaker pannel is rated to 250 amps. So I can run a little under half what my breaker panel could supply.
I've never come close to tripping my breaker panel while the wife was cooking & doing laundry (add in hot water heater & well pump to washer/drier) while the furnace was running. I was up in the shop running an air compressor, welding & stuff. I figure that's a worst case scenario & we won't be doing all of that at once so should be fine. Worst case scenario I manually flip a few breakers to keep the wife from doing laundry or something.