This is getting a little OT, but this is incorrect for this panel type. The two bars tied together across the bottom are both neutrals. There is a third bar in the upper right for the grounds. That one is bonded to the panel, while the other two are isolated from it.
My original photo is still the same photo posted in my opening of this thread-notice that there is no TBN "EDIT" indicated at the bottom of the original post.What is going on? The photo in post # 1 is not the same as the original photo, the input feeds led were black and there was a bare heavy gauge ground led, now the led are colored. In an other post it talks about the utility feed to the building being Red, Black, Blue, Ground and Neutral. That is very unusual to have 3 phase power to a home.
I'm looking at the Gereral Electric "DEH - 40537 Installation Instructions For 100-225 Ampere Single Phase 12-42 Circuit" that came with the panel and there is an illustrated drawing calling out that the two white verticle strips on each side of the circuit breakers and tied together with a crossbar at the bottom of each strip are both labeled as "Neutral". The third white strip which is located on the extrebe right and paralleling the right vertical edge of the bow is labaled as "Equipment Ground". I don't see where the ground bar is tied to the two neutral bars (which are tied together).After almost 40 years in the trade, of which 30+ are as a licenced master electrician, right off i notice two NEC violations in the OP's image posted.
Even though this is single phase, and as such generallly overlooked by inspectors, NEC requirements for color coding are black-red-blue when viewed from left to right, top to bottom or front to back. The only time NEC allows a change in phasing colors is in the case of three phase, where two wires need to be exchanged on terminals to reverse a motor rotation.
The second is definately a danger issue as it can potentially create back feed to the main panel in case of a fault.
For a sub panel, neutral and ground bar's may NOT be tied together. (A main panel its permissible and in most cases requiered.)
In this case the tie bar at the bottom of the panel needs to be removed, ALL white neutral conductors must be tied under the neutral bar on photo right, while all ground wires must be connected to the isolated ground bar photo left. This is called floating the neutral.Grounded conductor can be either solid or stranded wire, bare or insulated with green or green/w yellow stripe insulation, and must be a minimum #8 in size, though most juristictions i've worked in now require a minimum #6. Any conductor smaller than a #6 cannot be taped green, it must have an insulating coating of the proper color, or be stripped to expose bare wire. The main grounding conductor needs to be attached to a minimum 1/2 x 8' copper or copperclad ground rod or 5/8 x 8 galvinized rod. IF there is water suppled to the building, a cold water ground is also necessary as is bonding any building steel, in the case of a steel building.
That being said, in the case of a 240v welder, two power conductors and a ground are all thats needed generally to safely power and protect the equipment. The ground or equipment ground protects from shock hazard while the two current carrying conductors, (in a 240 volt application) will carry the load imbalance back to the panel for each other.
In the case of a 120v outlet, the white or neutral conductor is what carries said load imbalance back to the panel completing the circuit.
My original photo is still the same photo posted in my opening of this thread-notice that there is no TBN "EDIT" indicated at the bottom of the original post.
My original photo is still the same photo posted in my opening of this thread-notice that there is no TBN "EDIT" indicated at the bottom of the original post.
I'm looking at the General Electric "DEH - 40537 Installation Instructions For 100-225 Ampere Single Phase 12-42 Circuit" that came with the panel and there is an illustrated drawing calling out that the two white vertical strips on each side of the circuit breakers and tied together with a crossbar at the bottom of each strip are both labeled as "Neutral". The third white strip which is located on the extreme right and paralleling the right vertical edge of the bow is labeled as "Equipment Ground". I don't see where the ground bar is tied to the two neutral bars (which are tied together).
No offense to you outright or implied, your 40 vs. my 0, I'm just trying to learn by listening asking questions.
Even though this is single phase, and as such generallly overlooked by inspectors, NEC requirements for color coding are black-red-blue when viewed from left to right, top to bottom or front to back.
While you're at it, can you give me a code reference for this one too?Grounded conductor can be either solid or stranded wire, bare or insulated with green or green/w yellow stripe insulation, and must be a minimum #8 in size, though most juristictions i've worked in now require a minimum #6.