So wstf2 did we answer your question? I think things got a little muddy with all the answers but electricity is something you want to get right the first time.
Can you give me an NEC code reference for this color code, Black-Red-Blue?
While you're at it, can you give me a code reference for this one too?
The NEC I read every day says the grounded conductor must be white or natural grey/gray.
My error, i was thinking of one while referencing another. to correct myself, "grounded" conductors are to be white or gray, while "grounding" conductors shall be bare, green or green with a yellow stripe.
NEC code references for phasing colors can be found in the chapter wireing methods and materials while grounding requirements will be in the grounding section. (I don't have my code book in front of me to reference specific chapter, section and verse)
Note too, for high voltage, phasing array would be brown, orange, yellow which is standard color coding for 277/480
Tomorrow morning, I'm ripping out the #6 four wire feed (it's only about two feet long) and replacing with #6 three wire, happens to be black, white and bare copper. I just want to be done with the four wire/clipped white neutral. If and when we sell the place, I want it to be right for the new owner.So wstf2 did we answer your question? I think things got a little muddy with all the answers but electricity is something you want to get right the first time.
If you are that concerned about the neutral to the plug being in the panel, just clip it off as short as you can.Tomorrow morning, I'm ripping out the #6 four wire feed (it's only about two feet long) and replacing with #6 three wire, happens to be black, white and bare copper. I just want to be done with the four wire/clipped white neutral. If and when we sell the place, I want it to be right for the new owner.
The way I learned it was that you only need 2 hots to run a welder?.the ground wire is a safty factor and the neutral is not needed. I think the plug and recepticle are specific to welders.
Don't want to hijack the thread but I do have a question.
Since there are some electricians here I have a bonding question. I live on 5 acres and have been running wire to different buildings. I have a 200 amp service panel that is bonded (ground to neutral). From there I ran 1/0 w/#2 ground to a sub panel 115 feet away, then through a 4 foot high bank and out the other side about 10 feet (installed another sub panel) away from the first sub panel (again 1/0). From this sub panel I have 2 feeds. One is 75 feet of #2 and the other is 200 feet of 1/0 to my metal building. So I have 1 main panel and 4 sub panels. Three of the sub panels are not bonded. An electrician said to treat the metal building as a new structure and to bond it and use a grounding rod. The ground wire to the metal building is #6 copper and is connected to the main panel ground. Everything is 240/120 volt, 2 hot, 1 neutral, 1 ground.
My question is does the metal building " panel bonding and ground rod " seem ok since it is actually a sub panel .........only 325 feet away?
Thanks
Mike