RonMar
Elite Member
Cool concept, but when I looked into it a while back, it was nearly as expensive as putting in a dedicated transfer switch...
From what I have read about the Gulf Stream system it dosn't feed back it has a built in transfer between your shore power and the Gulf Stream generator.. If you walk into your trailer and turn a light on and it's not plugged into shore power the genny will start.. am I right on this ?? and if you walk in and turn on the same light and your plugged in the genny dosn't start,, " No Back Feeding involved"
There is nothing wrong with feeding a house with a generator that is sized for the house and has the proper transfer switch installed..
We need to get the terminology right.
It is FEEDING the house and BACKFEEDING the power grid. Feeding the house is what you want to do while backfeeding the grid is what you don't want to do. Transfer switch or "island" operation takes care of it.
I too have 400amp service at a central farm distribution point. It was easier and cheaper to have my utility put in a special hook-up. Transconnect unit. Similar to the generlink, a special collar moves the meter out about 4 inches. It then has a special pigtail which connects another box. The other box has all the automatic transfer and disconnect circuitry. I have a full power plug (dual modular anderson 350amp gray with 2/0 pins) The same which is on the pto generator. This really works well for me. I have feeds going out from here to the shop, run-in shed, barn, and large house. Each with there own panels.:thumbsup:
Why does the label say 200A rather than 400A? According to the specs:I looked all over the place and the 400amp transfer switch is made of gold. A lot really depends on your utility. I am in Northern Virginia, and have Rappahannock Electric Coop. Here is there pricing page of switches REC Electrical Services Prices I talked with them and was able to bump up into the next size switch. I also paid a little more than the $1,400 which is the 25kw.
![]()
If you look at the break down of what it would cost with;
400amp transfer switch
wiring
electrician labor
utility to pull meter and put back
permit
it really adds up. I am sure it would be more than the $1,400. And since the utility did it, they have a permanent permit![]()
Will this allow me to connect a 15KW PTO generator to my 400A service that has two 200A exterior disconnects feeding one interior panel each?pspproducts said:
- 200amp and 400amp service versions
- (1) 200amp or (2) 200amp service disconnect breakers to meet local code requirements
- Available in 100amp and 200amp generator size
In the posts I quoted above, daybreak1998 stated that he has a 400A service but provided a photo of what appears to be a 200A Transconnect switch.
Question 1: Why?
Question 2: When I buy a Transconnect switch for my 400A service, should I not expect to see "400 peak utility amps" printed on the label to indicate that it is the 400A version?