The breaker panel should be sized to how much power you are actually pulling through it, not how many breakers you have in it.
Also, the breakers alternate which one is on which leg of the 220 coming in, so I labeled your picture to reflect that.

That appears to be a 20 space 200 amp panel, they make 40 space 200 amp panels, so the number of breakers shouldn't be an issue.
As for putting too much load, get a cheap clamp on ammeter (such as Digital Clamp-On Multimeter ) and check each leg where the power is coming in to see how well balanced it is.
By my calculation, you have 260 amps of breakers on the "1" leg and 285 amps of breakers on the "2" leg.
Aaron Z
Also, the breakers alternate which one is on which leg of the 220 coming in, so I labeled your picture to reflect that.

That appears to be a 20 space 200 amp panel, they make 40 space 200 amp panels, so the number of breakers shouldn't be an issue.
As for putting too much load, get a cheap clamp on ammeter (such as Digital Clamp-On Multimeter ) and check each leg where the power is coming in to see how well balanced it is.
By my calculation, you have 260 amps of breakers on the "1" leg and 285 amps of breakers on the "2" leg.
Aaron Z