AC Condensing Units

   / AC Condensing Units #11  
I just found out Lennox also makes the Blue Ridge line.

Ron

Never heard of them (Blue Ridge line). Looked online, can't find them as well. That said, could be a private lable they are making for someone. Trane just came out with their Run Tru (sp) and I have no clue what Trane will do with their "Ox" or "Oxman" newer cheapo line as well.


What is the actual model and serial of the indoor coil that was replaced 2 years ago?
I'm not as familiar with what Lennox industries does, but I do have their NC contractor price catalog for the last 5 years and I don't see a DX coil listed. Is is an actual lennox coil?
What is the model and serial of the outdoor unit?
Why did the contractor only replace the indoor coil 2 years ago?
I know you said you didn't have the coin to replace everything, but was the indoor coil actually leaking?

If the coil is actually only 2 years old, good chance it was manufactured to be rated with at least a 14 SEER outdoor unit. Worst case, doing it yourself, I'd go with a Goodman 14 SEER AC outdoor unit.

The issue with a "dedicated" 16 SEER outdoor unit (split system) is the 2 year old indoor coil may not have the volume area to work properly with the outdoor unit to actually get the SEER rating you think your paying for. At this point, when mix / matching split systems, throw SEER out the window, so... you might as well go cheap as possible.

If you do it yourself, also make certain you have a decent vacuum gauge.

Screen Shot 2019-12-25 at 9.37.13 AM.png

This was on my own home, around 10 at night (250 microns).

Biggest mistake IMO guys make is getting lazy to is pulling a GOOD vacuum, ensuring the system is sealed, and using cheap silver solder for braze joints on the the copper fittings. System the gauge is hooked onto in the pic is an Armstrong heat pump system. In 12 years of operation, never had one part go bad on it. Have another Armstrong split duel fuel system, and in 15 years since it was installed, one bad capacitor on the heat pump and a variable speed motor in the gas furnace (let me tell you, even at a dealer cost, those variable speed motors are outrageously expensive).

My point about the lack of failures at my home is that the brand name doesn't have much to do with how good the unit is (all manufacuturers have issues here and there). What's more important is the quality of install. If YOU take pride in your work and feel confident that you know you'll do a good job, in all honesty, you'll probably put your own HVAC system in better than the average HVAC contractor would. That said, that's why GOOD HVAC contractors sometimes aren't the cheapest.

Forgot to add

Check indoor Metering device on coil (Piston / TXV) and know what if your keeping it or changing it depending on what outdoor unit you get.

Also, do yourself a favor and also check your static pressure along with air flow (per the furnace table guide that should be in the instruction manual with the gas furnace). Service techs always want to break out their gauges to check the systems superheat and subcool before even look at or adjust airflow, which is a huge mistake IMO.
 
   / AC Condensing Units #12  
I've bought HVAC through Grainger and no issues...

Also, the local supply houses will set just about anyone up with a refrigerant card.

All of the above is California based.

In Washington I found A/C costly... not all that many providers in the Olympia area and not many options...

I went with Rheem based on the Dealer... it has not been trouble free and the install cost almost 14k... but the dealer has quickly taken care of any issues with simply a phone call from 800 miles away... which is what I need being long distance.
 
   / AC Condensing Units
  • Thread Starter
#13  
Never heard of them (Blue Ridge line). Looked online, can't find them as well. That said, could be a private lable they are making for someone. Trane just came out with their Run Tru (sp) and I have no clue what Trane will do with their "Ox" or "Oxman" newer cheapo line as well.


What is the actual model and serial of the indoor coil that was replaced 2 years ago?
I'm not as familiar with what Lennox industries does, but I do have their NC contractor price catalog for the last 5 years and I don't see a DX coil listed. Is is an actual lennox coil?
What is the model and serial of the outdoor unit?
Why did the contractor only replace the indoor coil 2 years ago?
I know you said you didn't have the coin to replace everything, but was the indoor coil actually leaking?

If the coil is actually only 2 years old, good chance it was manufactured to be rated with at least a 14 SEER outdoor unit. Worst case, doing it yourself, I'd go with a Goodman 14 SEER AC outdoor unit.

The issue with a "dedicated" 16 SEER outdoor unit (split system) is the 2 year old indoor coil may not have the volume area to work properly with the outdoor unit to actually get the SEER rating you think your paying for. At this point, when mix / matching split systems, throw SEER out the window, so... you might as well go cheap as possible.

If you do it yourself, also make certain you have a decent vacuum gauge.

View attachment 634086

This was on my own home, around 10 at night (250 microns).

Biggest mistake IMO guys make is getting lazy to is pulling a GOOD vacuum, ensuring the system is sealed, and using cheap silver solder for braze joints on the the copper fittings. System the gauge is hooked onto in the pic is an Armstrong heat pump system. In 12 years of operation, never had one part go bad on it. Have another Armstrong split duel fuel system, and in 15 years since it was installed, one bad capacitor on the heat pump and a variable speed motor in the gas furnace (let me tell you, even at a dealer cost, those variable speed motors are outrageously expensive).

My point about the lack of failures at my home is that the brand name doesn't have much to do with how good the unit is (all manufacuturers have issues here and there). What's more important is the quality of install. If YOU take pride in your work and feel confident that you know you'll do a good job, in all honesty, you'll probably put your own HVAC system in better than the average HVAC contractor would. That said, that's why GOOD HVAC contractors sometimes aren't the cheapest.

Forgot to add

Check indoor Metering device on coil (Piston / TXV) and know what if your keeping it or changing it depending on what outdoor unit you get.

Also, do yourself a favor and also check your static pressure along with air flow (per the furnace table guide that should be in the instruction manual with the gas furnace). Service techs always want to break out their gauges to check the systems superheat and subcool before even look at or adjust airflow, which is a huge mistake IMO.

SIGARMS, Thanks for the response, good information. I guess I was not that clear. I had an old, burned out firebox, furnace replaced with a Lennox by the only contractor in the area. No AC with it. Went with the contractor as we were in the throes of moving in. Normally I would have done it myself. The new furnace is a SL280DF. The DX coil that came with the furnace is a Lennox CR33 30/36B. It is the mate for a Lennox XP20-036-230 16 SEER 3 ton heat pump. Originally we thought heat pump but have decided to stay with the gas furnace for heat. I will probably have to mod the coil for a TXV with a new 2 ton AC condensing unit. I figurenthe 3 ton coil will help maintain the 16 SEER syetem. The 3 ton was to get enough heating capacity. I have checked with the two HVAC supply houses here in the area. In addition to the EPA cert they want to see a HVAC contractor's license.

The lower end brands made by the big names are especially for the DIY market, but all caveat that a licensed HVAC contractor has to be engaged to check and start up to get warranty coverage. That will be a hurdle to cover also or forget it. I will save enough to take the risk. The Lennox dealer wanted $9K to furnish and install the heat pump. I will get a quote from them now to provide just an AC condensing unit. I was not all the pleased with the workmanship on the furnace either, and they are the most expensive in the area. I also realize the home market for HVAC is not the quality you see in commercial/industrial market which was my trade background.

Talking about the vacuum pump process; I would not rely on the drier to pick up any residual moisture so will leave the pump on at least overnight. I will have to buy the 25# CYLINDER OF R410 which is no problem with my EPA cert. $100 worth I will need very little of. Should be able to sell it after completion for most of the cost.

Thanks again, Ron
 
   / AC Condensing Units
  • Thread Starter
#14  
I've bought HVAC through Grainger and no issues...

Also, the local supply houses will set just about anyone up with a refrigerant card.

All of the above is California based.

In Washington I found A/C costly... not all that many providers in the Olympia area and not many options...

I went with Rheem based on the Dealer... it has not been trouble free and the install cost almost 14k... but the dealer has quickly taken care of any issues with simply a phone call from 800 miles away... which is what I need being long distance.

HVAC is one area up here where the suppliers are not friendly to the DIY crowd.

Do you have an EPA cert? I still have mine from when I worked at the trade.

What kind of problems did you have with the Rheem unit? Do their suppliers sell to DIYs?

Ron
 
   / AC Condensing Units #15  
Talking about the vacuum pump process; I would not rely on the drier to pick up any residual moisture so will leave the pump on at least overnight. I will have to buy the 25# CYLINDER OF R410 which is no problem with my EPA cert. $100 worth I will need very little of. Should be able to sell it after completion for most of the cost.

Thanks again, Ron

SAVE that R410A if you buy a 25lb jug of it. The year 2023 manufuacturers are discontinuing product that uses R410A. The juice will still be around, but it will go like R22 on pricing.

I do have to ask, why in God's earth did you go with a coil to be matched with an XP20 outdoor unit? That's a full mod compressor 20 SEER unit.

AHRI is really slow tonight, didn't get to look at any ratings, but it seems the CR coil is downflow (never mind, I'm an idiot, the SL280DF is downflow LOL), and being it was intended to go with a 20 SEER HP, you should be fine with volume area on any 3 ton outdoor unit. Just make sure you have some reducer couplings. That 3 ton lennox coil looks to be 3/8 liquid 7/8 suction and I believe a lot of the 3 ton outdoor units are 3/8x/34. I can assure you, having to run an hour round trip for $1 fitting can get pretty aggravating, particularly if you don't dare ask your wife to run for you:D
 
Last edited:
   / AC Condensing Units #16  
HVAC is one area up here where the suppliers are not friendly to the DIY crowd.

The reality is when you sell to the general public, you really have NO CLUE what kind of clown you can end up dealing with. I can assure you, there are "professionals" who have licenses who are clowns, so what do you think you can get dealing with the general public and you have no clue what you're going to get? LOL In general, and in all sincereity, the potential headache isn't worth it. HVAC systems aren't "plug and play".

That said, if you'd pull a proper vacuum and ensure the system is sealed, you're already doing it better than 30% of the licensed professionals out there IMO.
 
Last edited:
   / AC Condensing Units
  • Thread Starter
#17  
SAVE that R410A if you buy a 25lb jug of it. The year 2023 manufuacturers are discontinuing product that uses R410A. The juice will still be around, but it will go like R22 on pricing.

I do have to ask, why in God's earth did you go with a coil to be matched with an XP20 outdoor unit? That's a full mod compressor 20 SEER unit.

AHRI is really slow tonight, didn't get to look at any ratings, but it seems the CR coil is downflow (never mind, I'm an idiot, the SL280DF is downflow LOL), and being it was intended to go with a 20 SEER HP, you should be fine with volume area on any 3 ton outdoor unit. Just make sure you have some reducer couplings. That 3 ton lennox coil looks to be 3/8 liquid 7/8 suction and I believe a lot of the 3 ton outdoor units are 3/8x/34. I can assure you, having to run an hour round trip for $1 fitting can get pretty aggravating, particularly if you don't dare ask your wife to run for you:D

At the time of quotes the variable speed compressor seemed a good match for the heat pump application for this climate here. Wide changes in heating loads. Short cycling has always been a bugaboo of mine having worked service here in the NW. Amazing how many systems you service that are grossly over sized and the complaints short cycling generates. Hard to sell the customer on a smaller compressor when they just opened their pocketbook for a new system. Hermetic compressors really do like liquid in the crankcase. I understand the new rotaries are more tolerant, still good to keep the oil were it belongs.

When I was getting quotes we were in a hurry moving into a new (to us) house with a defunct furnace and it still being winter weather. Surprised the seller did not CO his family. i tried to get him to pay for the furnace, his reaction "it works, take it or leave it". We wanted the house as it was a sellers market and not much on the market.

You are right on the line sizes. Going with the 2 ton as I would rather have a unit that runs longer. We are not fans of keeping summer temps at 70, 76 is just fine.

Ron
 
Last edited:
   / AC Condensing Units
  • Thread Starter
#18  
The reality is when you sell to the general public, you really have NO CLUE what kind of clown you can end up dealing with. I can assure you, there are "professionals" who have licenses who are clowns, so what do you think you can get dealing with the general public and you have no clue what you're going to get? LOL In general, and in all sincereity, the potential headache isn't worth it. HVAC systems aren't "plug and play".

That said, if you'd pull a proper vacuum and ensure the system is sealed, you're already doing it better than 30% of the licensed professionals out there IMO.

I agree with your analysis. The DIY fan club over reaches their capabilities on highly technical systems. Think back at the posts here on TBN, we have a lot wannabe refrigeration techs that don't have a clue how the systems work. Just their terminology gives them away.

I assume from your posts that your are in the business. Sometimes I look back with nostalgia but then I have had an exciting career by getting into general construction project management. The mandatory college movement finally moved me out so I went into my own consulting firm for 10 years before hanging it all up for good. Not many of us old timers left that could overhaul an ammonia compressor and hand fit the babbit bearings. Talk flooded evaporators today with low side receivers you get blind stares.

Ron
 
   / AC Condensing Units #19  
I agree with your analysis. The DIY fan club over reaches their capabilities on highly technical systems. Think back at the posts here on TBN, we have a lot wannabe refrigeration techs that don't have a clue how the systems work. Just their terminology gives them away.

I assume from your posts that your are in the business. Sometimes I look back with nostalgia but then I have had an exciting career by getting into general construction project management. The mandatory college movement finally moved me out so I went into my own consulting firm for 10 years before hanging it all up for good. Not many of us old timers left that could overhaul an ammonia compressor and hand fit the babbit bearings. Talk flooded evaporators today with low side receivers you get blind stares.

Ron
It depends on where you work, we still have a few evaporators that have surge drums at work, most of our units use pumped liquid (overfed) to flood the units instead.
As for Babbitt bearings, the closest we have come to that was re-pouring the lead seat in a valve. The only compressors that might have Babbitt bearings haven't needed them in recent history.

Aaron Z
 
   / AC Condensing Units #20  
As far as buying off the net without warranty. I wouldn't worry about it much, as long as you can buy parts from a wholesaler in your area and perform the work.

If you get the system dry (deep vacuum), purge with nitrogen when brazing the line set, Keeping critical areas cool while brazing, you shouldn't have any major issues.

Heck, I have installed units one week and the condenser fan motor go out the next week. These were GE motors.
It wasn't an install issue, just a mechanical failure of the motor. Mechanical things fail. it's just the way it is
 

Tractor & Equipment Auctions

2005 FREIGHTLINER COLUMBIA 120 (A47001)
2005 FREIGHTLINER...
2018 INTERNATIONAL RH613 DAY CAB (A45046)
2018 INTERNATIONAL...
300 Gal Stainless Steel Fuel Tank (A47809)
300 Gal Stainless...
2022 Club Car Golf Cart (A47809)
2022 Club Car Golf...
LGMG AS4046E 40 SCISSOR LIFT (A47001)
LGMG AS4046E 40...
TPM 16 Mini Excavator (A47809)
TPM 16 Mini...
 
Top