Block heater trips breaker

   / Block heater trips breaker #11  
   / Block heater trips breaker
  • Thread Starter
#12  
It doesn't look easy to get into the heater to replace the cord. Yes the breaker is GFI. Maybe just time to buy a new heater?
 
   / Block heater trips breaker #13  
I had the same issue on a newer 20 amp circuit. Even drove to my neighbors new shop. same thing. We pulled my heater out of the hose and the element was just hanging there. Installed a new heater and all is well.
 
   / Block heater trips breaker #14  
It doesn't look easy to get into the heater to replace the cord. Yes the breaker is GFI. Maybe just time to buy a new heater?

It sounds like the heater or the cord is your problem. You should be able to replace either individually. The cord can crack or split causing a trip, or the resistance wire can burn through to the outer tube also causing a trip.
 
   / Block heater trips breaker #16  
I would start by plugging it into another circuit. Preferably one with a gfi. If it pops the breaker then the circuit is overloaded. If it pops the gfi then there is a short in the heater and/or it痴 power cable.

Now that sounds Genius. Never thought to troubleshoot that way.
 
   / Block heater trips breaker #17  
Loose connections on outlets and circuit breakers can cause breakers to trip. Arc fault protection. All it takes is someone not tighten a connection. Since he replaced outlet and breaker, not the problem. Most likely problem is that the heater warms up, expands and and shorts out. It will test good with a meter and will only fail when it heats up. Replace the heater.
 
   / Block heater trips breaker #18  
I would start by plugging it into another circuit. Preferably one with a gfi. If it pops the breaker then the circuit is overloaded. If it pops the gfi then there is a short in the heater and/or it痴 power cable.

Actually, if it pops the GFCI then there is a ground fault. A short will pop the breaker.
 
   / Block heater trips breaker #19  
A small short that is insufficient to pop the breaker will trip the GFI. That could be a short to neutral or a fault to ground because the gfi monitors the load across hot to neutral and trips if there is a variance. These are super sensitive and will trip before a breaker will.

So yes, I agree you are correct, but the real world dynamics of how they work allow you to investigate as I stated.
 
   / Block heater trips breaker #20  
Actually, if it pops the GFCI then there is a ground fault. A short will pop the breaker.

What happens when it pops a groundfault breaker? Is it a short or ground?
 

Tractor & Equipment Auctions

Schulte FX107 84in Rotary Cutter Attachment (A46683)
Schulte FX107 84in...
2014 FREIGHTLINER CASCADIA SLEEPER (A45677)
2014 FREIGHTLINER...
Mini Excavator Hydraulic Breaker Attachment (A45336)
Mini Excavator...
2014 FORD FLEX (A46684)
2014 FORD FLEX...
Spudnik 910 Dirt Eliminator (A47369)
Spudnik 910 Dirt...
2006 Wabash 53' Refrigerator Trailer (A43476)
2006 Wabash 53'...
 
Top