Ok I can make that work I'm getting ready for a rough in inspection soon and I need to finish running the 3 circuits to the new addition!! ThanksYou shouldn't run more than two cable assemblies the same hole.
Ouch those are expensive..Make a new hole with a Lee hole puncher or whatever the term is for the tool--makes neat holes.
HTH
Arkaybee
pat32rf said:While we often do install two wire per connector, you aren't really supposed to. Some inspectors are more fussy than others. You are only allowed three #12 or four #14 in a1/2" raceway. By the time you add the ground wire of the roamex, you would be over your allowable fill.....
Pipe ?, raceway ?
I don't think he's using any type of conduit.
Any hoot, I'd double check about doubling up in your cable clamps.
Easier and faster now than doing it twice later.
Willl said:Pipe ?, raceway ?
I don't think he's using any type of conduit.
Any hoot, I'd double check about doubling up in your cable clamps.
Easier and faster now than doing it twice later.
ive been putting 2 sets of 2 wire romex (with ground) wires in a knockout hole for over 28 years without any issues. Though for some time ive been using plastic romex connectors instead of the metal 2 screw connectors to prevent any problems. Now when it comes to 14/3 or 12/3 or the larger sets of romex, its one per hole.
Agree and here is the proof,, http://www.plumbersurplus.com/pdf/3201TB.pdf

Make a new hole with a Lee hole puncher or whatever the term is for the tool--makes neat holes.
HTH
Arkaybee