Fawken
Platinum Member
Guess I should chime in: what the other guy (S219) said is correct. IF the loads on the 2 independent 120Volt lines (240volts between them) are equal and they are sharing a Neutral then the current coming thru the Neutral will be a net 0 current. THIS is why having GFI Breakers on a shared neutral is not going to work (the GFIC outlet) is looking at the current going OUT (hot) and that same current coming BACK thru the white/neutral wire. It will trip when the load imbalance (current out) goes back to the panel thru the other HOT lead bypassing the Neutral RETURN circuit.
To properly wire this (you CAN still do it) however the white wire and ALL the white wires from all down stream outlets must go back thru the GFIC's "White Wire" that are feed from that GFIC outlet. This way no unbalanced neutral loads are passed back thru the other hot legs. The single white wire and two hots and green can be on different (single pole) breakers mounted side by side like a 240 breaker so they are on opposite legs of the main panel. The run of 4 wires can be from main panel board to the middle at a 4x4 boc with two GFIC breakers feeding different directions for a series of outlets as long as from that point (the GFICs) 5 wires are run keeping the white1 and white2 independent of each other just as the hots are kept independent.
Mark
Like I said, I'll do a real world test this weekend. In order for a circuit to function a pathway to ground or neutral must be complete. Question: If you cut the neutral in the scenario you describe will you see a spark/s? (let's say for this example each circuit is powering a 20A air compressor and using exactly the same current)